Hi all,
I'm in the middle of a project utilizing a A/B Micro 820 controlling a PF 525 with a PID loop.
In the process of trying to establish comms with the 525. All the start source and ref setting on the 525 are set to Ethernet and the IP is set to 192.168.1.2 whereas the plc is 192.168.1.1 with matching subnets. I cannot even locate the 525 on rslinx tree and there's no enet activity on the switch itself. I'm currently talking to the Micro820 and have a function block set up in the program defining the IP with parameters but still no go. help would be appreciated.
TIA
Old February 9th, 2018, 09:14 AM   #2
PLC Pie Guy
Canada
PLC Pie Guy is offline
PLC Pie Guy's Avatar
1. Set parameter C128 to 1 for parameters, default is 2 for BOOTP.
2. Assign IP Address to drive and Subnet Mask set to (normally 255.255.255.0)
3.Cycle drive power and verify Ethernet address is present.
4. Ping the I.P. If you can't ping it, Micro820 will never see it.
Then we can work at talking to the PLC.
Get comms. able to ping the drive from the PC first!
Old February 9th, 2018, 09:27 AM   #3
toddp65
United States
toddp65 is offline
Boom--mentioning that parameter c128 set off an alarm (in my head). It was on 2--i set it to '1' and I'm talking....thanks for the response
Old February 9th, 2018, 09:30 AM   #4
PLC Pie Guy
Canada
Glad you got it working!
Old February 9th, 2018, 12:47 PM   #5
toddp65
United States
toddp65 is offline
Another issue, somewhat related: the drive needs to communicate two ways-- the first being enet IP for ref and enable and the 2nd a manual mode with speed pot and di for enable.
I know it's parameters 48 and 49 but how do the drive differentiate between the primary and secondary input?
Old February 9th, 2018, 01:16 PM   #6
PLC Pie Guy
Canada
Look at parameters 62 through 68, they will allow you to use the dig ins to select which speed reference you are using.
Old February 9th, 2018, 01:31 PM   #7
toddp65
United States
toddp65 is offline
I see those parameters--under terminal block, correct? They aren't making much sense to me in regards to addressing the issue of using the digi start and speed reference in lieu of the primary ethernet control
Old February 9th, 2018, 01:41 PM   #8
PLC Pie Guy
Canada
Leave start source 1 set to EthI/P = 5 and speed reference 1 to EthI/P = 15.
Set the Start source 2 and speed reference 2, P48 and P49, to dig termblock and drive pot respectively.
Then set P62 or 63 or 65 depending on what terminal your connected with your digital input to = spd + strt 2 (notice all the available choices you have for this digital input coming on.)
Give that a shot! Remember to have your yellow jumper installed between 1 and 11 as well as the safety circuit completed.
Old February 9th, 2018, 01:54 PM   #9
toddp65
United States
toddp65 is offline
okay--great. I'll try those; the safety circuit shouldn't be an issue--it still has the factory jumper installed.
Old February 12th, 2018, 10:09 AM   #10
toddp65
United States
toddp65 is offline
So I have those parameters and setting changed.
However when I short terminal 1 and 2 on the TB for the drive I don't get a response--it's as if it's awaiting the command from the primary ethernet settings. How do you allow it to differentiate between one of the other?
Old February 12th, 2018, 10:18 AM   #11
PLC Pie Guy
Canada
You need to energize whichever terminal you assigned to the secondary start source as configured in P62, or whatever P** corresponds to the secondary digital input that you have wired.
Look at the manual's wiring section. It shows this is great detail. Look at page 37 in the 520-UM001G-EN. This shows how to wire it and even which parameters to look at as well.
Old February 12th, 2018, 11:47 AM   #12
PLC Pie Guy
Canada
Perhaps.. But this statement "I shorted terminal 1 and 2" makes me suspect a little that the wiring (could be) wrong. Is 1 still jumped to 11? Or in some way being made?
What digital input do you have wired to initiate the "start source 2" and the "speed Reference 2"?
Are you using 24VDC from the drive terminal or external,,, is the DIGCOM terminal connected to 0VDC? DIGCOM is terminal #4
What is the value of parameter P46, P48, T062, T063, T065, T066.
Also, does the drive work correctly from the PLC commands. Start stop and speed ok???
I know I'm asking more questions than you now but usually its just some silly little thing that is overlooked with this setup. Its pretty straight forward.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump