Member
|
2-wire ac NC proximity sensor
These are not used very often I know. I do not have a PLC on this piece of equipemnt that I am attempting to install a monitoring/alarm circuit in. My intent is to use this prox to monitor for weld wire presence and to switch the load to a timer relay when no wire is detected. When the relay times out at 11 seconds it will latch a relay that sounds/lights an alarm condition that requires a key reset to unlatch. I installed the prox using a micro qd with #3 suppling load(120VAC) and #2 to the timer relay. Sometimes the prox doesn't light at all and other times after cycling power I have gotten a flash on/off from the red LED indicating a short circuit. Also, the micro qd cable I have the red/white to load and the red/black to the relay
How far off the track am I?
__________________
John In the land of plenty, conservation is a foreign word. |
|
|
|
#2 |
|
Lifetime Supporting Member + Moderator
|
Is your "micro qd" some type of smart relay or electronic relay?
You have to be careful about what type and size of load you use with a prox switch. Not all prox switches will successfully switch all different loads (relays). DC relays can be difficult, as are some electronic relays. Last edited by Lancie1; June 13th, 2011 at 02:50 PM. |
|
|
|
#3 |
|
Member
|
micro qd is a type of "quick disconnet" that has 3 terminals and 2 keyways to assure proper mating
__________________
John In the land of plenty, conservation is a foreign word. |
|
|
|
#4 |
|
Member
|
Thank you for the replies, both parts are AB.
The prox is a 871TM-B4C12-R3,switches up to 200ma. The timing relay is a 700-HRP42TA17. I grabbed the timer I had on the shelf and did not qualify it fully, it appears that it requires quite a load to energize it. As for the load to the prox, I put a 250ma AGC fuse inline before the prox.
__________________
John In the land of plenty, conservation is a foreign word. |
|
|
|
#5 |
|
Member
![]() Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,150
|
The prox needs a minimum load of 5 mA. There isn't a load spec on the timer datasheet. I suspect it might be small. Looked at similar Fuji timers from AD. They are only 10 VA. You should use a relay that draws at least 5 mA in between.
|
|
|
|
#6 |
|
Lifetime Supporting Member
|
If it's a two wire AC prox, then you should be able to wire it either way with the same results. I have seen some that also include a 3rd connection for ground.
If the prox is directly feeding the coil of a relay, then its indicator should always function unless it is damaged. Perhaps the prox was shorted or the load of the relay coil is too much for it? Can you post a link to the part(s) you're using?
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." |
|
|
|
#7 | |
|
Member
![]() Join Date: Oct 2005
Location: Chicago
Posts: 1,366
|
Quote:
I agree with Paul. Chances are that the load of the relay is too much for the prox. The prox is primarily used as a signal/feedback device and it is not capable of load switching. Check the prox specs. |
|
|
|
|
#8 |
|
Member
![]() Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,150
|
A 2 wire prox needs a good size load to power it's internal electronics. Check specs. I believe it's minimum 20 mA or so. Give it a load like an incandescent lamp.
|
|
|
|
#9 |
|
Lifetime Supporting Member
|
Is it an electronic Timer? It may have too high of a resistance (minimum current to power the prox) Try putting a coil relay in between, or us a resistor to draw a few mA.
__________________
Brian |
|
|
|
#10 |
|
Member
|
I threw in a omron MY2 between the prox and timing relay. I was trying to minimalize the amount of components in the circuit by landing directly on the timer. Of course, no I can just use a NO prox. I guess what I learn here is that is a certain item is rarely used, its probably that there is a better, more mainstream way of doing it.
thanks again
__________________
John In the land of plenty, conservation is a foreign word. |
|
|
|
#11 |
|
Member
|
I would put a 10K ohm 2W resistor across the coil of the timer. AC switches need a minimum load to stay "on", this is common when using solid state timers to turn on a load.
tommy23t |
|
|
|
#12 |
|
Member
![]() Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,150
|
That's a common value, good for most applications. The problem is it will run a little hot.
For this application, 22K will give us a little over 5 mA, enough to meet the prox spec. Watts drops down to .6 Watts. |
|
|
|
#13 |
|
Member
|
I was able to test this today with no problems making the latch. The prox energizes the coil on a omron MY2 relay which closes a circuit to the timer. I'm probably missing something, but isn't there plenty of amperage to power that coil?
__________________
John In the land of plenty, conservation is a foreign word. |
|
|
|
#14 |
|
Member
![]() Join Date: Jul 2005
Location: Lucas, TX
Posts: 1,150
|
Coil draws 9.2 mA at 120V. Well within your range of 5-250 mA for the prox.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 4 wire proximity sensor to plc input | jeii | LIVE PLC Questions And Answers | 9 | March 14th, 2011 02:22 AM |
| AC proximity sensor | rguimond | LIVE PLC Questions And Answers | 2 | February 13th, 2011 08:37 PM |
| Inductive proximity sensor interfacing | xilog | LIVE PLC Questions And Answers | 16 | March 22nd, 2010 10:06 PM |
| How to connect AC sensor and motor to PLC | Zhen | LIVE PLC Questions And Answers | 5 | April 10th, 2009 06:47 AM |
| proximity sensor on sugar mill | labingtone | LIVE PLC Questions And Answers | 6 | January 17th, 2003 08:14 PM |