Contactor chatter

Hi to all. I have been called to take a look at a intdustrial type control panel that gets hot about 98 F at 80 ambient. The panle has a 200 amp main and only draws about 50 amps. Panel has about 30 contactors and a small type of a siemens plc aprox. 5 cards. after a short diagnose i saw that practycly all the cable connections wore loose and i went on with tighting all connections about 4 solid turns on every one.

Problem: after making sure that all connections wore tight i went on and powerd up the panel and the componets motors, valves etc. What i experianced was that 4 of the 30 contactors started chattering execevly. I waent on and replaced the contactors and the four stoped but another 2 or 3 started the chattering again i replaced the contactors and another two started the same problem. Can anyone explain? mesured the coil vboltage at 120 volts ac . what would cause this weird chattering. Thanks to all for your help.
  Reply With Quote
Old September 2nd, 2009, 12:13 AM   #2
leitmotif
Member
United States

leitmotif is offline
 
Join Date: Nov 2004
Location: Seattle Wa. USA
Posts: 3,679
OK lessee if I understand correctly
Initial trouble call was for cabinet overheating.

you found loose wires and tightened all connections.
On energize you had relays A B C D chattering.
You replace them and on retest they are OK
BUT
E and F start
You replace them and on retest they are OK
BUT
G and H start chattering.

Most interesting. I have a hard time with idea you have some contagous disease causing death of relays one after another.

The coils on relays are 120 VAC?
Did you check voltage on the chattering coils themselves?
Are you getting a voltage drop across the control switches and you checked both coil terminals?
What is source of 120 VAC control power? Is it large enough?
I think I would check for a lifted neutral also.

Dan Bentler
  Reply With Quote
Old September 2nd, 2009, 12:26 AM   #3
Kev77
Member
United States

Kev77 is offline
 
Kev77's Avatar
 
Join Date: Mar 2008
Location: Beaverton, Or
Posts: 337
any chance that the panel was cleaned? I had the same type of issue after blowing compressed air in a panel (first and last time doing that!).
  Reply With Quote
Old September 2nd, 2009, 01:11 AM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,351
Here's another thread on the subject.

http://www.plctalk.net/qanda/showthr...highlight=coil
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old September 2nd, 2009, 02:42 AM   #5
jingo
Member
Philippines

jingo is offline
 
jingo's Avatar
 
Join Date: Aug 2008
Location: DAVAO CITY
Posts: 18
possible of carbonized auxilary contacts that causes the chattering, on this contacts one of the supply line is connected before it reaches the coil,it sometimes sparks before the contactor energized....
hope this will help..
  Reply With Quote
Old September 2nd, 2009, 02:57 AM   #6
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 808
From experience there are two separate problems you can get with contactors that have an AC coil: chattering and buzzing.

A low hum to a buzz is quite normal, these things are after all working on an AC supply. Went to a job in a bank where they were complaining about a 'buzz', they had specified AC, lapped up the facing of the magnetics and they were then whisper quiet.

A chatter to a clatter generally has two causes: first is a wrong voltage or frequency on the coil, second is major dirt or magnetic swarf inside the contactor. Went to a job up in Scotland where they were complaining of chattering. Their contractors who had installed the job had cut holes in the top of the enclosure without protecting the contactors, they were full of metal swarf and cuttings.

You often find that as you fix one noise another seems to start, I tend to find that it isn't so much that another starts, more that as you stop one source of noise you can hear slightly quieter ones.

Bryan
  Reply With Quote
Old September 2nd, 2009, 05:12 AM   #7
BobB
Lifetime Supporting Member
Australia

BobB is offline
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 3,615
The main 2 things that I have seen over the years to cause chattering are dirty pole faces and wear and tear.
A break in the shading coil usually causes the contactor to 'stick' in.
__________________
The Old Pfhaart

  Reply With Quote
Old September 2nd, 2009, 05:27 AM   #8
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 3,821
While the above are most likely the causes (summed up nicely by BobB), some other gotchas to look out for:

1) If the neutrals (commons) are daisy-chained, an upstream problem can cause difficult to find downstream faults.

2) If any of the contactors have an internal DC coil, the holding resistor and/or contacts might have a problem.

3) If they rely on aux decks to seal in, the mechanical mounting of the aux deck may have degraded, making them function improperly.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old September 2nd, 2009, 10:38 PM   #9
plcsoftvsd
Member
India

plcsoftvsd is offline
 
plcsoftvsd's Avatar
 
Join Date: Sep 2007
Location: 23 15 13.2 N 77 27 28.75 e
Posts: 132
I would suspect the voltage at the coil terminals (What is the coil rated voltage) .

What is the control voltage? I have seen this happening with loose neutrals. (at the incomer)

Cheers.
__________________
Happiness is a decision...take it.
  Reply With Quote
Old September 2nd, 2009, 10:49 PM   #10
Adam303
Lifetime Supporting Member
United States

Adam303 is offline
 
Adam303's Avatar
 
Join Date: Aug 2009
Location: Chicago
Posts: 584
Yes I did blow the contactors with air.
120 volt coil mesured voltage is 119 volt
i took apat the rest of chattering contacots cleaned the contacts with a wire brush and contact cleaner seemed to help a lot thanks for all your help.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 04:14 PM.


.