I have connected an op3 to my pc using rj12, I have pro tool lite installed. when I open a new project in pro tool I have options for connecting with PLC but not with pc and in op3 I get a message address as 2 not possible when I try to log in transfer mode.I did not connect any PLC to the op. first of all i want to make a project in pro tool and transfer it to the op.In pro tool >new> download>preferences the connection com1 and serial and then download I tried this way but the message is no connection to the op .Thanks
|
|
|
|
#2 | |
|
Lifetime Supporting Member
|
Quote:
You change to transfer mode as follows: Change to "System" image Select the mode required with SHIFT+CURSOR Enter the password "100" Select the mode required and press ENTER If a custom configuration is already loaded that does not include the standard function "Change mode", you must make a general reset by pressing the key combination"ESC+ CURSOR right + CURSOR down" and then the standard English configuration is loaded. The power on the OP must be switched off before pressing the 3-key combination. The 3-key combination must be pressed and held when the power is switched on again on the OP. |
|
|
|
|
#3 |
|
Member
![]() Join Date: Feb 2012
Location: Hyderabad
Posts: 31
|
The Op3 display shows ready for transfer when I press enter"$104 restart after transfer abort " message is displayed and then "$ 551 as address AS 2 not possible"
|
|
|
|
#4 |
|
Member
|
It's a long time ago but normally:
address 2 = default adress plc address 1 = default adress OP |
|
|
|
#5 |
|
Member
![]() Join Date: Feb 2012
Location: Hyderabad
Posts: 31
|
still unable to make a connection to op
|
|
|
|
#6 |
|
Member
|
This morning something popped up in my mind:
I think it can be that you use the wrong com-port. If I find yet a manual I will let you know if there is something else that you can try. |
|
|
|
#7 |
|
Member
![]() Join Date: Feb 2012
Location: Hyderabad
Posts: 31
|
Thanks Ivo
If I can overcome the 4017 protocol error then half of the problem will end. I did not find what this error is about. |
|
|
|
#8 |
|
Member
|
|
|
|
|
#9 |
|
Member
|
Do you use the correct cable:
http://www.control.com/thread/1026153043 i saw that you use com1-serial, so that should be OK. 'no connection to the OP' suggest that your OP is not in transfer-mode. I would again suggest 'Moggie's' 3-key-move but I'll try to make it more detailed: - power off - ESC + arrow-right + arrow-down - power on AND hold the 3-keys pressed. Here I most times went wrong (see next line). - only after the text 'flash test' appears on the OP you can let go of the 3-keys. I this text does not appear you can repeat everything again!. - after start-up: press enter, go to 'F4-system', F2-OP-mode, you should see the text 'Operat. mode online'. - press shift+arrow-down, use password '100' - you should see "Operat. mode MPI down". Press ENTER, you should see "ready for transfer". |
|
|
|
#10 | |
|
Member
|
Quote:
http://www.control.com/thread/1026160562 Error message $551 AS address 2 not possible is meaning that MPI, or PTP, or DP, or in every case connection plc-op is faulty. This depends basically by 3 factors: a)connection cable (A and B reversed is common error) b)terminating resistors at each end of bus must be on. c)the cpu connected doesn't have address 2 |
|
|
![]() |