plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old June 27th, 2012, 12:04 AM   #1
Karsten
Denmark
Karsten is offline
Softstarter -25C to 50C
Hello,
Having a hard time to find a Softstarter for a 11kW motor to be used in low temperature -25C to 50C.
Any ideas?
Old June 27th, 2012, 12:46 AM   #2
seppoalanen
Finland
seppoalanen is offline
seppoalanen's Avatar
Talking
Put Inverter (VFD) inside the box. Insulate box by Polyurethane, add Rittal's heater inside the box and don't forget the cooler if ambient temp. really is +50.
Finally You have soft starter, soft stopper and variable speed !
On right wall has small heating unit (gray one). On left wall have thermostats for heating, ventilation and interlocking for VFD's supply.
Under -10, electrolytic capacitors can explode, so use Vacon or ABB VFD, others are their "copy".
Old June 27th, 2012, 02:25 AM   #3
JesperMP
Denmark
JesperMP is offline
JesperMP's Avatar
About the low temperature, I agree that you can install a thermostat and heater in the panel.
About the high temperature, 50 degr. C is high but not exceptionally high. In case that the 50 degr. is the exception rather than then norm (*), then a simpler fix than installing a cooler is to derate all equipment inside the panel, i.e. select at least one dimension larger than the nominal size for the load. The mmanufacturers often have recommendations as to how much the equipment must be derated.
I would also consider to avoid any heat-generating equipment inside the panel. Use a direct 400VAC to 24VDC PSU without the typical transformer in between. Choose sofstarters with integral bypass. Use a modern PLC, and not a legacy PLC. Etc...
*: Almost all equipment can operate at 50-60 degr. C. What happens is merely that the equipment age faster than normally. Not so important if the high temperature is an exception to the normal operation.
__________________
Jesper
Old June 28th, 2012, 02:24 PM   #4
Karsten
Denmark
Karsten is offline
Well the problem is the -25C and I can not use heaters. It is a mobile aplication. The Vehicle moves without power to the soft starter. Then it stops, connects to external power and the motor is started. So I can not use heaters.......
Old June 28th, 2012, 02:49 PM   #5
jstolaruk
United States
jstolaruk is online now
Radiator off the vehicles cooling system, just like the vehicle interior.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
Old June 28th, 2012, 03:12 PM   #6
DickDV
United States
DickDV is offline
Basically, if you cannot use heaters then you cannot use electronic softstarters. All manufacturers of softstarters use commercial grade integrated circuits in their control cards and these are only rated for 0 degrees C or 32 degrees F. The same is true for VFD's.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Softstarter ramping Down Jeff23spl LIVE PLC Questions And Answers 20 March 14th, 2012 10:01 AM
Modbus communication between Micrologix 1400 as Master and ABB softstarter as slave pravinshinde LIVE PLC Questions And Answers 6 February 2nd, 2012 09:00 AM
Softstarter "inside delta" connection. Why only for some kind of softstarters ? JesperMP LIVE PLC Questions And Answers 19 August 3rd, 2011 11:24 AM
Protection in front of large Softstarter lalion LIVE PLC Questions And Answers 4 October 3rd, 2008 08:01 AM
Softstarter to be used for safety stop ? JesperMP LIVE PLC Questions And Answers 12 October 27th, 2006 11:49 AM