PLC Interface with Two HMI
Hello ,
I am currently working with MicroLogix 1200 and i need to connect the plc with Two Different HMI (panelview-c600 & pannelview-c1000) but i discovered that the plc is provided with only one HMI communication Port , so i tried to get an Port Splitter -DPS2-1747 but its not available in India at present , so please help me out in an alternative with this problem , urgent solution required. TIA. Last edited by gibson; September 21st, 2012 at 07:29 AM. |
|
|
|
#2 |
|
Member
![]() Join Date: Sep 2006
Location: Ireland
Posts: 36
|
You could use a net eni module to convert 1200 communications port to Ethernet and then connect HMI's with a small hub
|
|
|
|
#3 |
|
Member
![]() Join Date: Sep 2012
Location: mumbai
Posts: 23
|
Thanks For the Reply ,
I am thinking of Using MGate EIP3170 Series DF1 to EtherNet/IP gateways , will this work in solving my problem . |
|
|
|
#4 |
|
Member
|
Try using an 1761-net-eni from rockwell, or a df1/ethernet_ip gateway from anybus or RTA.
__________________
My two cents. |
|
|
|
#5 |
|
Member
![]() Join Date: Apr 2010
Location: Whitby
Posts: 24
|
I would use a net-ENI module on any Micro Logix. EtherNet is wide open, free protocol. This way you get away from all the expensive AB comm options. Use a hub (Phoenix makes a good industrial hub or Weidmuller makes a cheap DIN mount 4 port) and there you go ... fast communication with not too much money added.
|
|
|
|
#6 |
|
Member
![]() Join Date: Nov 2011
Location: Arkansas
Posts: 221
|
honestly, i would look into just replacing the aging Micrologix 1200 with an Micrologix 1100. The 1100 isn't much more than the 1761-net-eni and you get so much more with the 1100.
|
|
|
|
#7 |
|
Lifetime Supporting Member
|
+1 as long as the base I/O and 4 expansion modules fits your needs
__________________
"It's a lot easier to find another job than to find another family. And families tend to be a lot more loyal than corporations." - Steve Bailey THE AUTOMATION STORE - Your source for automation supplies, component repairs, and PLC training classes |
|
|
|
#8 |
|
Member
|
|
|
|
|
#9 |
|
Member
![]() Join Date: Sep 2011
Location: Mla
Posts: 67
|
saw long time ago PLC5/40e with 1 RIO rack connected to phoenix serial to DH485 converter but did not get to see how 2 PVP1000 HMI was connected. any ideas except for ethernet?but I think they went e-net due to speed. thanks
Last edited by mike_dr; September 24th, 2012 at 09:56 PM. |
|
|
|
#10 |
|
Member
![]() Join Date: Sep 2011
Location: Mla
Posts: 67
|
EDIT saw long time ago PLC5/40 with 1 RIO chassis connected to phoenix serial to RS 485 converter but did not get to see how 2 PVP1000 HMI was connected. any ideas except for ethernet?but I think they went e-net due to speed. thanks
![]() In the program it had channel 0 as USER(ASCII),ch 1A configured as DH+, ch 1B as RIO scanner.but correct me if im wrong(which is the case) the 25-pin port,ch0 of the main chassis was connected to the converter then the RIO chassis was also connected via RIO adapter(1771-asb) using blue,clear,shield wire. I think it is possible to also connect the 2 PVP using only the PSM-ME-RS232,485-P converter and without the use of a ethernet hub. |
|
|
|
#11 |
|
Lifetime Supporting Member
|
If both your HMIs support DH485, the Micrologix could be configured for that protocol and the proper modules installed, but I would go ethernet. If you want quick, compact and proven, the Digi One IAP is better than the NET-ENI, and you could get away with two of them since one could bridge an HMI to the ML1000 serially, but it would be cleaner to put each device on Ethernet.
If your HMIs both support Ethernet, then one Digi'll do ya'.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. "You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway." |
|
|
|
#12 |
|
Member
![]() Join Date: Sep 2012
Location: mumbai
Posts: 23
|
Thank's a Lot all of u For your replies.
|
|
|
|
#13 |
|
Member
![]() Join Date: Jun 2009
Location: Keokuk, IA
Posts: 113
|
The DigiOne IAP is a better alternative than the NET-ENI module.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| PLC interfacing with HMI and PC??? | hamzasyyed | LIVE PLC Questions And Answers | 8 | January 30th, 2012 01:44 PM |
| Siemens S7 – 300 PLC and WinCC Flex 2007 HMI | peng | LIVE PLC Questions And Answers | 3 | March 17th, 2011 02:13 AM |
| Can't Upload Modicon TSX 57 PLC and Magelis HMI | Kenny Teixeira | LIVE PLC Questions And Answers | 2 | August 29th, 2008 02:23 AM |
| Excel read/write to HMI or PLC? | Charles1 | LIVE PLC Questions And Answers | 1 | December 13th, 2005 06:28 PM |
| Ethernet PLC and HMI recommendation? | jackk | LIVE PLC Questions And Answers | 7 | November 30th, 2005 11:32 PM |