Old October 6th, 2017, 12:56 PM   #46
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 362
Based on what I see, this is what your setup should be... Anyone more knowledgeable please chime in if I'm mistaken.

+24DC is going to your EStop, which appears to be a NC on your print based on the symbol. The other side of the EStop is going to R1 on your safety relay, and R2 is going to 0VDC. This is the circuit that closes the coil of the relay. When the EStop is NOT PRESSED (if it is indeed a NC like the print says), then your coil on the safety relay should be closed.

13>14
23>24
33>34

The top side of your relay SHOULD be your line (power in), either from your PLC outputs or from some alternate power supply. The bottom side SHOULD be your load (power out) going to you motor starter and whatever else you are controlling.

So if you want your output channel 0 to enable your motor, you need to run a wire from output channel 0 to terminal 13 on the relay, then run a wire from terminal 14 to the motor starter contact. You also need to run a common to your motor in order for that circuit to be complete. If that is all done correctly, you should have an energized coil on your relay and a working motor starter. If it is set up that way and you aren't getting your motor to turn on, you need to ring everything out with a meter to figure out where you are losing continuity. Do it in this order, your positive pole on the target and your negative on the common R2 screw of the relay:

1. Check that you are getting +24vDC from your power supply.
2. Check that you are getting +24vDC on the INCOMING side of your ESTOP when it is depressed (energized).
3. Check that you are getting +24vDC on the OUTGOING side of your ESTOP when it is depressed (energized).
4. Check that you are getting +24vDC on your R1 screw on the relay.

If that all checks out, then your coil should be closed. If it isn't you might have a bad relay. If it fails at any point, let us know which point it is.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old October 6th, 2017, 01:04 PM   #47
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 362
Somehow I missed a whole bunch of posts. It seems like this is all correct and the only problem is that your EStop button is functioning as a NO instead of the correct NC. My suggestion would be to go to the stock room and a get a proper EStop and swap it out haha. Sometimes it makes more sense to just scratch an itch than to try and spend three days figuring out what's causing the itch.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old October 10th, 2017, 09:13 AM   #48
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Sorry LoganB, I missed your reply! Thank you though and thanks to everyone for the reply!

We figured out the problem. Power supply connection to output card was loose! it's working now yay!!

I will post video of my working project
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 10th, 2017, 09:18 AM   #49
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 362
Hope you gave that electrical guy a good ribbing for that one
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old October 10th, 2017, 09:20 AM   #50
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Quote:
Originally Posted by LoganB View Post
Hope you gave that electrical guy a good ribbing for that one
hahah it was pretty smooth
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 10th, 2017, 04:22 PM   #51
ScruffyNerfHurtr
Member
United States

ScruffyNerfHurtr is offline
 
Join Date: Feb 2017
Location: PA
Posts: 41
Quote:
Originally Posted by LoganB View Post
Hope you gave that electrical guy a good ribbing for that one
Luckily I do the programming and installation/wiring. So I can take it pretty easy on myself when I slip up. lol
  Reply With Quote
Old October 10th, 2017, 06:34 PM   #52
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 181
Quote:
Originally Posted by ScruffyNerfHurtr View Post
Luckily I do the programming and installation/wiring. So I can take it pretty easy on myself when I slip up. lol
lololol I hear yea!
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SattCon PLC vset LIVE PLC Questions And Answers 17 April 24th, 2017 04:25 PM
AB Led lamp wont turn off when PLC output go's off Kipper LIVE PLC Questions And Answers 15 September 4th, 2015 01:51 PM
PLC Advice - Home Automation Needs onefineday2010 LIVE PLC Questions And Answers 10 July 31st, 2015 09:43 AM
CP1H - Sending data from plc to computer teknok LIVE PLC Questions And Answers 3 March 1st, 2011 01:31 AM
PLC communicatio error adamly LIVE PLC Questions And Answers 0 February 13th, 2008 04:57 AM


All times are GMT -5. The time now is 09:52 AM.


.