Quote:
Originally Posted by Combo View Post
I am sure Combo means delta connection.

I just happen to know that in some languages, what we call "wye" and "delta", is literally called "star" and "triangle". Combo is just not fluent in English techno slang, that's all.


That's indeed what I mean, delta.

I have 2 motors, both:

delta/star
220V/380V xA/xA 2.2kW

What I wanna do is, connect the motors in Delta; and the connect tot the frequency drives. I know that I shood connect in Star normally. Shat am I gonna do:

When u connect in delta, then u will haven 400 Volts on each winding (max); It Wil take more current, and the Torque wil be great untill 87Hz. Yes 87Hz, comes from sqrt 3 x 50Hz
OK, this is actually a valid concept for when you need to run a motor ABOVE the rated frequency and still need rated torque. Here is how this works.

First off, torque output from an AC induction motor is dependent upon maintaining a constant ratio of voltage and frequency, a V/Hz ratio. So a 400V 50Hz motor requires 8.0V/Hz (400/50), a 230V 50Hz motor requires 4.6V/Hz. So as long as you maintain that V/Hz ratio, the motor is capable of producing rated torque. The problem arises when you want to go OVER the base speed, in this case 50Hz, but your voltage is fixed, i.e. 400V. You cannot maintain the proper V/Hz relationship because you run out of V to increase with the Hz. So if for example you wanted to run the motor at 87Hz, 400/87 = 4.6V/Hz which is .575 of the design ratio, so that motor will now only be capable of delivering 57.5% of rated torque at that speed. But here is the workaround:

  1. You have a motor rated for 230V Delta, 400V Star.
  2. You have a 400V supply.
  3. You have a VFD rated for 400V.
  4. You strap (connect) the motor in DELTA (triangle) as if it is to get 230V.
  5. You then program your VFD to tell it that the motor is 230V 50Hz, which will create a 4.6 V/Hz ratio that the motor requires to get full rated torque.
  6. You then allow the maximum speed to be 87Hz instead of 50Hz, at which time the VFD will output 400V and we already know from the above that 400/87 = 4.6, so the motor is now capable of delivering full rated torque at a speed higher than the base speed.
This is done all the time by the way, totally legitimate. The only thing you MUST check is that the motor is physically capable of the higher speed. If it is a 2 pole motor for example, the base speed may be 2900 RPM, so operating it at 87Hz means it will be spinning at 5000 RPM and the bearings may not be rated for that additional speed. ONLY the motor manufacturer can answer that question, no two motors are built the same, so just because one motor is OK at that speed doesn't mean another one is.
  Reply With Quote
Old October 31st, 2017, 12:39 PM   #47
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,476
Quote:
Originally Posted by Steve Bailey View Post
Zombie thread alert. This one has been dead for twelve years.
Oh ****... suckered in again...

I wish they would close threads that are 6 months old.
  Reply With Quote
Old October 31st, 2017, 12:44 PM   #48
travispedley
Member
United States

travispedley is offline
 
Join Date: May 2012
Location: Sanford, NC
Posts: 84
Maybe a zombie thread, but still an EXCELLENT explanation.
  Reply With Quote
Old October 31st, 2017, 04:58 PM   #49
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,476
Quote:
Originally Posted by travispedley View Post
Maybe a zombie thread, but still an EXCELLENT explanation.
Thank you. At least it wasn't a waste of electrons then...
  Reply With Quote
Old November 1st, 2017, 03:39 AM   #50
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,220
Zombie thread ! Maybe because of halloween ?
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old November 1st, 2017, 10:45 AM   #51
Maxkling
Member
United States

Maxkling is offline
 
Join Date: Mar 2011
Location: Atlanta
Posts: 159
Quote:
Originally Posted by jraef View Post
OK, this is actually a valid concept for when you need to run a motor ABOVE the rated frequency and still need rated torque. Here is how this works.

First off, torque output from an AC induction motor is dependent upon maintaining a constant ratio of voltage and frequency, a V/Hz ratio. So a 400V 50Hz motor requires 8.0V/Hz (400/50), a 230V 50Hz motor requires 4.6V/Hz. So as long as you maintain that V/Hz ratio, the motor is capable of producing rated torque. The problem arises when you want to go OVER the base speed, in this case 50Hz, but your voltage is fixed, i.e. 400V. You cannot maintain the proper V/Hz relationship because you run out of V to increase with the Hz. So if for example you wanted to run the motor at 87Hz, 400/87 = 4.6V/Hz which is .575 of the design ratio, so that motor will now only be capable of delivering 57.5% of rated torque at that speed. But here is the workaround:

  1. You have a motor rated for 230V Delta, 400V Star.
  2. You have a 400V supply.
  3. You have a VFD rated for 400V.
  4. You strap (connect) the motor in DELTA (triangle) as if it is to get 230V.
  5. You then program your VFD to tell it that the motor is 230V 50Hz, which will create a 4.6 V/Hz ratio that the motor requires to get full rated torque.
  6. You then allow the maximum speed to be 87Hz instead of 50Hz, at which time the VFD will output 400V and we already know from the above that 400/87 = 4.6, so the motor is now capable of delivering full rated torque at a speed higher than the base speed.
This is done all the time by the way, totally legitimate. The only thing you MUST check is that the motor is physically capable of the higher speed. If it is a 2 pole motor for example, the base speed may be 2900 RPM, so operating it at 87Hz means it will be spinning at 5000 RPM and the bearings may not be rated for that additional speed. ONLY the motor manufacturer can answer that question, no two motors are built the same, so just because one motor is OK at that speed doesn't mean another one is.
This response was completely worth the zombie thread.
  Reply With Quote
Old November 1st, 2017, 11:33 AM   #52
JimmyBio
Member
United Kingdom

JimmyBio is offline
 
Join Date: Oct 2017
Location: Stoke
Posts: 2
Hmm. I thought the calibration table contained in the powerstack data of the VFD decreases the torque above the rated data, regardless of frequency e.g if vfd set to 50Hz, decrease after 50Hz, 60 Hx decreases 10Hz higher. I best tell my employer this is not the case - and scrap my test results as they must be wrong. I didn't know it was really that simple and the results I've been getting show a roll off of torque at 60Hz for a vfd set to 50Hz. So what happens to all the voltage spikes above rated torque? does the V/Hz equation factor these in? or the extra flux as the winding fields start to overlap? zombie thread so... bye.
  Reply With Quote
Old November 1st, 2017, 02:01 PM   #53
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 231
When I have done it, I set the Base Frequency at 120hz/460v, but connect the motor for 230v, and set FLA to 230v value... works like a charm!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Pumps Alan Case LIVE PLC Questions And Answers 14 June 9th, 2003 04:30 PM


All times are GMT -5. The time now is 04:02 AM.


.