Banging noise from transformer

Any experience with any sounds other than a hum from a transformer? Im not overly familiar with the setup, but from what I saw it was either a 100 or 200hp motor 230v. 480v fed into a soft start, through a step down transformer to 230v and then to motor. When motor attempts to start, we get a loud bang from the transformer and breaker trips. With load disconnected, still get a bang from transformer. I've heard the setup used to not have a softstart, but a regular starter, and the reason the soft start was put in was because of similar issue as today. Is the unit outputting full power rather than gradual? No fault lights or any other signs of problems coming from the soft starter. What could possibly make that kind of noise from within the transformer? Is that common/uncommon to have the transformer after the motor starter rather than before?
  Reply With Quote
Old November 4th, 2017, 03:31 PM   #2
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,057
It may be related.

I used to work in an automotive stamping plant that had a line of automated spot welders, each was single phase on a single 3 phase conduit across the back. They were all interlocked so that only 1 welder on each phase could weld at once.

What happened along the longer sections of EMT conduit when a welder did weld was the wires inside magnetized quickly and banged together and into the conduit wall - with a loud bang each time.

Maybe something inside the transformer is loose and gets magnetized & pulled.
  Reply With Quote
Old November 4th, 2017, 08:00 PM   #3
DrOrpheus
Member
United States

DrOrpheus is offline
 
Join Date: Aug 2016
Location: Washington
Posts: 32
I sort of thought the same thing at first, it is located up against an outer wall of sheet metal.
  Reply With Quote
Old November 4th, 2017, 09:29 PM   #4
mendonsy
Member
United States

mendonsy is online now
 
mendonsy's Avatar
 
Join Date: Feb 2009
Location: Western NY
Posts: 744
I saw a somewhat similar case many years ago.
An electrician took the cover off of a 100 kva transformer to change the taps. He left the cover bolts and his wrench lying in the bottom of the transformer because he wanted to test the voltage before closing it up. When he turned the power to the transformer on the loose pieces all jumped up against the iron core for a few seconds then fell back to the bottom of the case.
  Reply With Quote
Old November 4th, 2017, 10:31 PM   #5
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 257
I have not experienced this sound from a transformer, but like Aabeck stated, I have seen wires/cable jump in conduit.

Although, it too was in a welding app.

We have many 200+HP motors operating and get stopped and started just about everyday. No conduit banging to speak of, except the sound of the starter pulling in.

We also have 20,000A rectifiers that also have a soft start that is done over large resistors in parallel to main line. No banging or strange noises.

You may very well have something loose that is being magnetized for a moment. I would check that before traveling to the Twilight Zone of electrical physics.
  Reply With Quote
Old November 4th, 2017, 11:52 PM   #6
DrOrpheus
Member
United States

DrOrpheus is offline
 
Join Date: Aug 2016
Location: Washington
Posts: 32
Other details I didn't mention. The motor was not running,but was supposed to be. I checked voltage phase to phase on the output of the starter. Had 480v, I clamped each wire and got 1.5A. It was when we switched from auto to manual to start the motor is when we heard the initial bang. I havent been involved since.
  Reply With Quote
Old March 26th, 2018, 11:03 PM   #7
DrOrpheus
Member
United States

DrOrpheus is offline
 
Join Date: Aug 2016
Location: Washington
Posts: 32
Aaaaaaaand it's back. So back in November when this initially happened,I contacted ABB for help. The dude sent me a sheet on how to test the thyristors inside the unit. So I did what it said, I disconnected all the wires attached to the outside, took the cover off, disconnected all the wires inside, did some ohm checks, all seemed to check out ok. Put the thing back together, and it worked perfectly like it should. Ran fine for 5 months, now it's acting up again.

Same issue occured, fan tripped and it's now down. Same set up however, it was time to swap the fan motor so the old one can be serviced/rewound. Got a new motor in it, transformer has been fully tested by outside shop with a clean bill of health, not shorts,etc. Also got a brand new identical ABB softstarter in it. I copied the settings from old unit and entered it into the new one. First test, smooth start up, all is well, as were subsequent manual starts. Put it in for production run and it craps out.

Things I've observed. With motor disconnected and only the transformer on the load side, it makes some gnarly noises, the voltage output on softstart is erratic. Not a smooth 20 sec progression like it's set. Transformer (no load attached) was pulling erratic current, spiking as high as 60A and back to 0 and everything in between. With motor attached, (100hp 230V) I watched the amps spike to 420A as soon as it started and worked it's way down, then slowly up to tripping point of breaker attached inline with motor. I was convinced it was something to do with the xformer, even though all the experts told me otherwise.We pulled wires off of the transformer, hooked up a portable 480V fan to the softstarter, fired it up, ramped up nice and smooth, amps were like 1.5A, voltage ramped up like it was supposed to. I was certain at that point it was the transformer. Took out the portable fan, came back the next day to check some more stuff. Nothing hooked to softstarter, no control calling for action, the output is sitting at 480V. Display screen shows 0% output, removing the fuse for 120VAC control power to the softstarter so it powers down, and it's still outputting 480. Pulling disconnect, and powering back on, still 480V. Pretty sure we have a shorted thyristor now. No longer do I think it's the transformer down stream. Now I need to look upstream, any suggestions? I've checked control voltage to unit which was odd that my meter hesitates when checking high voltage and does a beep first. It did it on the 120V, showed something like 500 volts then immediately down to 88, then 122. PLC commands the softstart as well as a HOA switch on panel. There's a purple and an orange wire on the softstart I assume one provides steady voltage and the orange connects to the start and stop terminals to control. Traced the purple and orange to an ice cube relay that I assume comes from PLC to make the connection. During earlier tests, removing that relay didn't break the 480 output either. I read around a little and it sounds like a no voltage scenario wouldn't necessarily stop the SCRs from conducting, it would actually take a voltage signal to make it stop. I don't know much about this, but unfortunately nobody else does either and we are dead in the water here, so any recommendation on places to check for faults. The softstarter appears like everythings cool, no fault code or protection light. I checked voltage between the orange and purple and didn't get any voltage. But, that was after the stuck on condition. Could there be a problem on the internal power source? Just need to find the root cause of that. Sorry for lengthy post, just wanted to fill in all the details I could remember.
  Reply With Quote
Old March 26th, 2018, 11:24 PM   #8
mhammer214
Member
United States

mhammer214 is online now
 
Join Date: Jul 2013
Location: Colorado
Posts: 32
Without a load on the softstarter you will have 480 volt on the output terminals because the thyristors always have a small leakage current. The internal resistance of a voltmeter is too high to pull that voltage down.
  Reply With Quote
Old March 27th, 2018, 10:47 AM   #9
DrOrpheus
Member
United States

DrOrpheus is offline
 
Join Date: Aug 2016
Location: Washington
Posts: 32
I did not know that. I assume there would be no output if there wasn't a signal to close. Thanks, so that is nothing to worry about? They symptoms of our actual problem is that it is not consistently ramping up smooth and appears to be doing a hard close...sometimes.
  Reply With Quote
Old March 27th, 2018, 11:35 AM   #10
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,252
not familiar with soft starts, so this is my opinion.
transformers should be in front of the soft start units.
they require constant power, not power supplied from a soft start.
transformers are deigned with a laminent / stacking factor in mind to keep the magnetic fields constant.
with a constant power source, you are within the design specifications and the transformer is happy. I do not know what the soft start does, but it does not keep a constant power source to the transformer primary.
if I am wrong, someone please correct me.

regards,
james
  Reply With Quote
Old March 27th, 2018, 12:40 PM   #11
T Gibbs
Member
United States

T Gibbs is offline
 
Join Date: Jun 2012
Location: Morristown, TN
Posts: 385
Quote:
Originally Posted by James Mcquade View Post
not familiar with soft starts, so this is my opinion.
transformers should be in front of the soft start units.
they require constant power, not power supplied from a soft start.
transformers are deigned with a laminent / stacking factor in mind to keep the magnetic fields constant.
with a constant power source, you are within the design specifications and the transformer is happy. I do not know what the soft start does, but it does not keep a constant power source to the transformer primary.
if I am wrong, someone please correct me.

regards,
james
I was thinking the same thing. I've never seen a transformer after a soft start.
  Reply With Quote
Old March 27th, 2018, 12:48 PM   #12
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 786
Transformer is a big inductor with an iron core connecting it to another inductor.

For an inductor, the V = L * dI/dt

a soft start tries to give you a cut off sign wave like this
https://goo.gl/images/1R2i9f

What is the dI/dt at the start of each red section? ~ infinity? yup.

So what could be happening in your transformer? bad things maybe.
  Reply With Quote
Old March 27th, 2018, 01:28 PM   #13
DrOrpheus
Member
United States

DrOrpheus is offline
 
Join Date: Aug 2016
Location: Washington
Posts: 32
This installation has been trouble free for at least a decade, up until recently. I've read around that it is not totally uncommon to have this setup, not saying your wrong, however we've had two instances of the transformer being tested with nothing wrong with it, the output of the soft starter does seem to be erratic in terms of voltage and current.
  Reply With Quote
Old March 27th, 2018, 01:36 PM   #14
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,474
I have used Soft Starters (and VFDs with sine wave filter) to supply transformer primary with motor on secondary side.
Some tips...
Soft Starter must have all 3 legs controlled by SCRs. Some soft starters have a "wild Leg" that is always "hot" and the soft starter only controls 2 phases. "Wild Leg" scrs do not work well with transformers.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old March 27th, 2018, 02:11 PM   #15
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,583
Quote:
Originally Posted by NetNathan View Post
I have used Soft Starters (and VFDs with sine wave filter) to supply transformer primary with motor on secondary side.
Some tips...
Soft Starter must have all 3 legs controlled by SCRs. Some soft starters have a "wild Leg" that is always "hot" and the soft starter only controls 2 phases. "Wild Leg" scrs do not work well with transformers.
Ding ding ding, WINNER! Absolutely correct. Putting a transformer on the load side of a soft starter is not a problem, other than it adds impedance to the circuit so any current limiting effect in the soft starter is going to have even LESS current getting to the motor, but that only counts in measurements and settings, requiring slight compensation.

But, and this is a BIG but, you CANNOT use the "2-phase" versions of cheap soft starters, "2-phase" meaning they only have SCRs on 2 of the 3 phases, the 3rd pole is just a piece of bus bar. The output voltage then is inherently unbalanced. In a motor application, this causes additional heating because of negative sequence currents created by the rotor. But in a transformer, it results in a high DC component in the fields. That might have been the source of your banging sounds.

These types of soft starters are marginally acceptable to motor loads as well; I would never use them on anything other than centrifugal pumps and fans that can accelerate in less than 10 seconds, and then only on loads that were not critical to my operation. Also if this type of soft starter shorts even one SCR, the motor gets power applied to it continuously, even when off, and it burns it up unless someone trips the circuit breaker. the only reason they sell them is because they are a little cheaper, so long as nobody looks at long term operating costs.

What is the model number of the ABB soft starter? The PSR and PSE are both the 2-phase type and should have NEVER been used on a transformer primary application. The only one they still sell that has 6 SCRs is the PST series.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Noise Problem - NI cRIO, Control Techniques Unidrive SP ParetosFew LIVE PLC Questions And Answers 10 February 17th, 2017 04:42 AM
Transformer problem . Maintenance Man LIVE PLC Questions And Answers 8 March 10th, 2011 02:34 PM
Transformer Chandrashekar LIVE PLC Questions And Answers 3 July 5th, 2009 09:46 PM
USB noise with a headset surferb LIVE PLC Questions And Answers 5 May 10th, 2008 09:21 AM
What's wrong with the step down transformer? ckchew666 LIVE PLC Questions And Answers 46 September 6th, 2005 12:50 PM


All times are GMT -5. The time now is 10:40 AM.


.