Why do "Switch in STOP" tags exist?

This has always eaten away at me ever since I started programming PLC's.

Simply, why do "Switch in STOP" tags exist? If the PLC is in stop, then it's not running any logic, as such it's silly to reference the tag. Of course, you could use it as a NC contact, but that contact will always be closed if the PLC is running, so why bother in the first place?

As someone who programs for retail-type applications, I would love to be able to make use of it so I can have a red indicator lamp turn on if someone is messing about and switches the PLC to stop.
  Reply With Quote
Old November 4th, 2017, 02:16 AM   #2
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 905
Tags can still be read by a SCADA system or other controller, so can be useful for alarming or HMI purposes.

If you want to drive a red lamp if the PLC is not executing code then wire the lamp to a relays normally closed contact. Drive the relay from your PLC with a "always on" bit. If the PLC fails or stops, the relay turns off and the lamp turns on.
  Reply With Quote
Old November 4th, 2017, 07:11 AM   #3
kwade
Member
United States

kwade is offline
 
Join Date: May 2013
Location: sc
Posts: 310
As Saffa says... since the STOP stops your programming, not the PLC FW or comms, anything that can read from the PLC can read the Stop switch state - take action based on that state.
  Reply With Quote
Old November 5th, 2017, 03:40 PM   #4
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,648
I saw an application once where the PanelView Plus was configured to display an alarm if the MicroLogix PLC was not in run mode.

The only thing was, they hadn't directly addressed the S bits themselves. They'd written ladder logic in the PLC something like:
Code:
|   PLC_RunMode            B3:0/0
|------|/|------------------(  )--|
...and then tied the HMI alarm to the B3:0/0 bit. I laughed so hard the project manager thought that the 13-hour days had finally caught up with me and sent me mad.

But, as others have suggested, if you DON'T do something as dumb as the above, and instead address the S bits directly, you can have a HMI display the status of the PLC even if it's not in run mode.

Remember, the PLC is still doing things when it's not in run mode. It still services communication requests, still updates status bits, the only thing it doesn't do is execute the user code.
  Reply With Quote
Old November 5th, 2017, 05:11 PM   #5
Brandon_K
Member
United States

Brandon_K is offline
 
Join Date: Mar 2016
Location: Pittsburgh, PA
Posts: 139
Thanks guys. I never gave thought to the usability in a HMI or SCADA.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Can't delete RSLOGIX and FACTORYTALK tags AFPC LIVE PLC Questions And Answers 6 September 27th, 2017 01:24 AM
RSLogix 5000 moving program tags to control tags NetNathan LIVE PLC Questions And Answers 5 February 15th, 2014 05:36 AM
RSLogix 5000 v16 - RSViewStudio online tags, some missing. Jimbo72 LIVE PLC Questions And Answers 2 September 17th, 2013 06:55 AM
Generate HMI / SCADA tags from S7 project! nebula_1979 LIVE PLC Questions And Answers 1 November 18th, 2009 08:32 AM
RSview-online tags missing-device shortcut not usable- Need Help! brettdawnj LIVE PLC Questions And Answers 6 October 1st, 2007 06:04 PM


All times are GMT -5. The time now is 12:38 AM.


.