FactoryTalk View SE Alarm Filter

I am looking to get some of the filters that have been setup for the Alarm/Event windows to be automatically selected when the window is opened.
I basically have a pop-up window available for every piece of machinery on the assembly line that has a trending chart and alarm history for that particular machine. The trending chart and every other element on the page shows the correct data because the pens uses a parameter (#1) to only show relevant historical data. Unfortunately the alarm log seems to default to show every piece of machinery set up - not the specific one that should be shown. I have broken up each machine's faults to use a specific group and have filters made up to show good data, however it is not auto selected when the window is loaded.

Is there any way that this filter can be auto applied via some macro or ??
Thanks..
  Reply With Quote
Old November 30th, 2017, 04:16 PM   #2
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,693
There should be a way, and it probably uses VBA.

I've got an application where I have multiple clients all looking at the same alarm display, but when it opens, it automatically selects the filter that shows only alarms related to the area the client is in. The operator can select to view all, but by default, it only shows their area.

It was a while ago that I did this, so I can't remember exactly how. But seeing as I would have had to determine which filter to apply based on the PC name, I must have used VBA somewhere in there.

Have a look into VBA code and I'll see if I can't dig out the code I used later on.
  Reply With Quote
Old November 30th, 2017, 09:54 PM   #3
thumperbs
Member
United States

thumperbs is offline
 
Join Date: Dec 2014
Location: Midwest United States
Posts: 27
I no longer work for the employer so I cannot fish out an example for you but I believe I accomplished what you are looking for once by prescribing unique alarm severity values for different areas. I then used VBA to filter by those values based on the area I cared about.
  Reply With Quote
Old November 30th, 2017, 10:09 PM   #4
jholm90
Member
Canada

jholm90 is offline
 
Join Date: Mar 2012
Location: Ontario
Posts: 8
Thank you very much for your assistance - it led me on the path to success

For the documentation side here's what happened:

My alarm and event log viewer name is "Log Viewer". All of my events are sorted into groups that I'd like on the particular page.

I am able to pull the 'GroupNameHere' from a tag/parameter in the project file based on the window opening. I found that I couldn't put this code to activate while the pop-up window/alarms display was loading so I implemented a delay of 1 second and it activates the filter as desired.

The VBA code to be called for the alarm filter is:
Code:
LogViewer.WhereClause= "GroupPath = 'GroupNameHere'"
The time delay code of 1 second is: (Borrowed from the help file...)
Code:
    Dim PauseTime, Start, Finish, TotalTime
        PauseTime = 1    ' Set duration.
        Start = Timer    ' Set start time.
        Do While Timer < Start + PauseTime
            DoEvents    ' Yield to other processes.
        Loop
        Finish = Timer    ' Set end time.
Some of the other methods to filter the alarms may require opening the SQL Management Studio to get the precise column names as they don't all line up exactly with the names inside FactoryTalk Studio
  Reply With Quote
Old December 3rd, 2017, 08:29 PM   #5
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,693
Glad you got it working! Thanks for posting back with the solution.
  Reply With Quote
Old April 3rd, 2018, 10:49 PM   #6
Gabriel B. C.
Member
Brazil

Gabriel B. C. is offline
 
Join Date: Oct 2017
Location: Porto Alegre
Posts: 9
Filtro de Alarmes no sumário pelo tag desejado!

Estou precisando de ajuda para fazer um filtro no meu sumário de alarmes, gostaria de digitar o nome do alarme em um campo, apertar um botão e com isto filtrar no sumário somente o tag desejado. Sera que tem como me auxiliar neste processo?

Last edited by Gabriel B. C.; April 3rd, 2018 at 10:54 PM. Reason: Quando coloco para postar as palavras estão se alterando sozinhas
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
VNC Server FactoryTalk View SE elmatador LIVE PLC Questions And Answers 4 November 3rd, 2018 04:43 AM
FactoryTalk View SE and ODBC swphillips LIVE PLC Questions And Answers 18 September 10th, 2018 02:18 AM
FactoryTalk view SE questions Kalagaraz LIVE PLC Questions And Answers 9 June 1st, 2017 12:47 PM
FactoryTalk View Alarm History Problem pampoon LIVE PLC Questions And Answers 2 April 26th, 2017 05:45 PM
Updating FactoryTalk View SE Local Station zacslade LIVE PLC Questions And Answers 7 July 5th, 2016 03:10 PM


All times are GMT -5. The time now is 10:07 PM.


.