RL DataStation setup help

First Modbus project, rookie question I hope.

Modbus device -> DSPLE -> Control Logix L72 via Ethernet I/P

Need to read 5 Modbus registers. Four are 16 bit, one is 32 bit.

I have a block set up in the DSP with a size of 5 and mapped the appropriate Modbus registers.

My question is for the input instance of the Generic Ethernet module, what do I set the 32 bit size to?

I'm confused as to how the DSP moves the 16 bit words to the 32 bit tags. Will it only use two tags for the four 16 bit words, or will it use four tags and fill in the first 16 bits of the each tag? The 32 Modbus register I'm assuming will move to a single tag in the control logix.

Thanks!
  Reply With Quote
Old December 6th, 2017, 06:02 PM   #2
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,305
Can you post your Crimson Code? Zip it first.

You will need 6 Gateway blocks reading 6 registers in the Modbus device. Modbus uses 16 bit registers max. So for floating point or long integers (32 bit) you have to read 2 16 bit registers and combine them in a Data Station Tag.

I am not sure how to answer your questions about a Generic Ethernet Module. Can you explain what module you are talking about? You shouldnt need anything more than a standard Ethernet Module to talk to the DSPLE and get your data.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old December 6th, 2017, 08:28 PM   #3
cncsparky
Member
United States

cncsparky is offline
 
Join Date: Dec 2014
Location: Ks
Posts: 65
The DSP is added to the 5000 project as a generic ethernet module. Data type is DINT, set an input and output instance, and a size. Does the 6 gateway blocks in the DSP = 6 DINTs in the logix project? Or would it be 3 DINTs?
  Reply With Quote
Old December 6th, 2017, 08:43 PM   #4
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,305
I wouldn't add it as a generic module. I am not even sure if you can do that. Just give the DSP a IP that is in your control network. Then you set up the DSP to read the Modbus Registers you need and place that data into your PLC Tags. It is really pretty simple nothing special needs to be set up.

Here is a Youtube video that does a pretty good job explaining protocol conversion in the DSP https://www.youtube.com/watch?v=uLk5AdbPW2A

As for your question each Gateway Block will have only 16 bits of data (INT). So for each DINT you will need to read 2 consecutive registers. Same for a Real data type. So in your case with 4 INT's and 1 DINT you would need 6 Modbus Registers.

You can have the DSP write the INT data from the Modbus device to a DINT in the PLC if you want. I dont think it will affect anything. It will just write to the lower 16 bits of the 32 bit register.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old December 7th, 2017, 09:07 AM   #5
cncsparky
Member
United States

cncsparky is offline
 
Join Date: Dec 2014
Location: Ks
Posts: 65
Thanks. I think this answers my questions. One Modbus register = one logix tag. The input instance for my Ethernet module will have a size of 6, same as number of Modbus registers.

Quote:
Originally Posted by Bullzi View Post
As for your question each Gateway Block will have only 16 bits of data (INT). So for each DINT you will need to read 2 consecutive registers. Same for a Real data type. So in your case with 4 INT's and 1 DINT you would need 6 Modbus Registers.

You can have the DSP write the INT data from the Modbus device to a DINT in the PLC if you want. I dont think it will affect anything. It will just write to the lower 16 bits of the 32 bit register.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Com Setup SLC 5/01 and RL G307K2 cmarinello LIVE PLC Questions And Answers 3 November 24th, 2014 10:04 PM
Stratix 5700 NAT Setup Help aidamcg LIVE PLC Questions And Answers 2 October 29th, 2014 03:45 PM
MAVE SLOGS 5000 Setup Help lukesnhoj LIVE PLC Questions And Answers 4 October 3rd, 2014 07:32 PM
Ideal S7-300 + OPC + HMI communication setup Clemenzo LIVE PLC Questions And Answers 7 January 13th, 2014 03:53 PM
Value of changing from NPN sensor setup to PNP sensor setup David.Reed.Schmidt LIVE PLC Questions And Answers 10 November 18th, 2013 06:20 AM


All times are GMT -5. The time now is 03:21 AM.


.