plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 7th, 2017, 12:52 PM   #1
Levi G
Canada
Levi G is offline
Lenze ESV22N02YXB571XX1A10 Drive and Modbus RS-485
Hi I am trying to communicate with this Lenze drive I have kicking around.
My PLC is a Productivity 1000.
This drive has a built in Modbus module with a RJ-45 connector. This is not the plug-in Modbus module. I can not seem to get a hold of the pin-out for this RJ-45 connector. Lenze tech support says this drive was custom made for Captive Aire and they don't know the pin-out. Has anyone had any success communicating with this drive before? If so could you provide me with the pin-out of the RJ-45 connection. I have the manual and it says it is for Modbus RS-485 Daisy chaining.
Attached is the picture of the Modbus comms
Old December 7th, 2017, 04:14 PM   #2
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
If it is a standard Modbus Connection then the following PDF will show you the Pinout:
http://www.modbus.org/docs/Modbus_ov...al_line_V1.pdf
Pin 4 - +
Pin 5 - -
Pin 8 - Gnd
Regards,
__________________
Garry
http://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old December 7th, 2017, 05:36 PM   #3
danw
United States
danw is offline
danw's Avatar
Is it likely that Modbus RTU over RS-485 is the only signal on the RJ-45? Probably. If that's the case, then it is a known fact that swapping the driver lines will not damage the driver lines. Comm won't work if the lines are swapped, but there's no damage. So you can break out those lines and give it a try.
You might be able to confirm the signal GND by testing for continuity to the frame ground. It might or might not be the same point.
If those pins 4 and 5 do not modulate when Modbus is polling, then use a voltmeter to check for which pins modulate/oscillate when Modbus is polling. It is very likely too be 2 wire half duplex and only 2 wires out of the 8.
Old December 7th, 2017, 05:50 PM   #4
Levi G
Canada
Levi G is offline
I will give this a try later today and report back
What is the "T" Terminal for on the P1000 when using RS-485? (see attached)
I have never worked with Modbus before so I really appreciate the help
Old December 7th, 2017, 07:04 PM   #5
danw
United States
danw is offline
danw's Avatar
I've seen dozens of RS-485 connections before:
Here's a handful of them:
None have a termination terminal.
I have no idea what its purpose is. Termination resistors are installed directly across the (+) and (-) driver lines.
Old December 7th, 2017, 08:42 PM   #6
Levi G
Canada
Levi G is offline
Ok, I tried glcshortt's suggestion and it's working like a champ.
Thanks for the help guys.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
M340 NOE100 IO Scanning Modbus Comms to AB PowerFlex 753 Drive scader LIVE PLC Questions And Answers 2 February 8th, 2017 07:12 PM
ABB ACS550 Drive ModBus Control vijay s LIVE PLC Questions And Answers 22 January 30th, 2016 08:01 AM
Replacing Freq Drive brand on ModBus Rob S. LIVE PLC Questions And Answers 4 May 8th, 2015 09:01 AM
ABB drive control via modbus communication with FXCPU plc prakashchy85 LIVE PLC Questions And Answers 3 April 5th, 2015 10:06 PM
Omron 3G3RV drive Modbus djpalaz LIVE PLC Questions And Answers 1 March 1st, 2007 10:36 AM
