Old December 12th, 2017, 12:05 AM   #1
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,175
Pump Control Ideas

Hi Everyone,
Looking for ideas on a new project. Here are the details:
PLC - CompactLogix L33
VFD - PowerFlex 753
Ethernet/IP Control

We are unloading rail cars of Gasoline and Diesel and putting it into storage tanks. I have Pressure Transmitters on the pipe on the inlet to the pump and on the outlet from the pump. Those run into the PLC Analog Card.

The pump requires a minimum NPSHr of 6 ft at lower flows up to 8.5 ft at full flow. I have converted that to psi to give me a range of 1.9 to 2.95 psi.

I have done projects with this VFD but it was more simple control, based on the # of pump request. Never done one where I was looking at a dynamic input like pressure.

What I want to do is to use the PT's, PLC and VFD's to control the pump speed so I can pump as fast as I can without cavitating the pump.

As the rail car pumps down the NPSHa will drop so obviously I will need to slow down the pump. I was just looking for some ideas. I could just do some kind of range thing like:
Inlet Press >3psi run full speed
Inlet Press between 2 & 3 run and 3/4 speed
and so on
But I as thinking that there has to be a better more fluid solution for doing this. Maybe PID?

So if you have any experience in doing something like this I would love to hear how you handled it.
Thanks for the help!!
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old December 12th, 2017, 01:38 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,521
PID would probably work well here using the inlet pressure as the PV and with a setpoint set with a small safety factor above the minimum allowed for smooth pump operation. Once it is well tuned, you could probably trim the setpoint down even closer to that minimum value and get the fastest performance from the system.

You will probably need to filter the analog input from the PT if it is in the moving stream of fluid. It is likely to bounce due to vibrations in that stream. I have only done water and fluids with SG near or above 1.0 so not sure how the fluid dynamics of fuel might pose unique challenges I am not aware of.

I would definitely have shutdown fault logic based on the inlet pressure being below a setting somewhere below the minimum PID SP and above the mechanical safe limit, but tied to a debounce timer to avoid nuisance trips.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old December 12th, 2017, 10:29 AM   #3
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,175
Thanks Oki,
I have all my analog scaling in a timed task that runs every second. Do you think that is long enough of a delay?

I have never used PID in a PLC so this will be a first for me. What would you recomend for starting values of P,I & D?
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old December 12th, 2017, 11:53 AM   #4
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,044
Bullzi,

I don't know your degree or background so I am going to give my opinion.

Since you mentioned Railcar tankers with gasoline and diesel, you must adhere to class 1, div 1 rules in NFPA70. you must also look and NFPA70e - are flash, and nfpa 496 - purging and pressurization of enclosures, nfpa 79
- electrical standard for industrial machinery (may not apply here), and I think there is a requirement for unloading pads (staging area).

I also recommend that a PE (if you are not one or have on in the staff) to review your design and stamp it to avoid any future issues if an incident occurs.

regards,
james
  Reply With Quote
Old December 12th, 2017, 01:48 PM   #5
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 322
I don't know that I would even use a PLC, there are very smart VFD's that have PID's built into their software.

We use VFD's with PID's setup all over the oil industry and they work great.

A standalone VFD just might be cheaper also??
__________________
David M. Camp
Automation Engineer
Marshall Electric / www.mei-tech.com

PLEASE READ: https://www.prlog.org/12642091-marsh...-industry.html

PLEASE READ: https://www.prlog.org/12680572-marij...hold-word.html
  Reply With Quote
Old December 12th, 2017, 03:45 PM   #6
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,175
James - I am not a PE but we have one on the project. I have been working with Petroleum products for almost 30 years so I fully understand your concerns. The VFD and Control panel are outside of the Classified Area.

damica1 - Yea we looked at the ABB drives with the "Pump Smart" Technology and they were over $2,000 more expensive each than the AB PowerFlex. That is saying something when you are more money that AB!!

I like functionality they had but for $8,000 (4 x $2,000) I can write a lot of logic. So I guess I am trying to emulate some of that functionality in my PLC code.

Thanks for the input!!
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old December 12th, 2017, 04:01 PM   #7
VAN
Member
United States

VAN is offline
 
Join Date: Apr 2012
Location: Wa
Posts: 172
Quote:
Originally Posted by Bullzi View Post
So I guess I am trying to emulate some of that functionality in my PLC code.
Does this project have an HMI?
Can you build a quick HMI just as a proof of concept?
Can you inhibit the IO cards and build a simulation routine (this maps IO so that when an input comes on the code turns an output on and you can simulate the system running)?

I always think it's easiest to just simulate a system and figure out what to anticipate.
So, pump turns on the PSI should rise this can be a simple add based off a timer that the pump is on and the output of the pump (or CV) would make the added value rise/fall. This would let you get some base PID parameters in and start a "tuned" PID. Or even prove the system works as you think it should.

I'm a big fan of simulation code.
  Reply With Quote
Old December 12th, 2017, 04:20 PM   #8
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,836
A couple of thoughts.

NPSH is typically absolute pressure (psia) not gauge pressure. Make sure you include approximate barometric pressure into your considerations.

NPSH is based on preventing cavitation, which is the formation of vapor bubbles at the impeller. It will depend on temperature, so make sure you have adequate safety margin for reasonable temperature variations.

Most pump curves show NPSHR for water. Gasoline and Diesel have different vapor pressures, and both will differ from water. Make sure your NPSHR is appropriate for the worst case fluid or somehow differentiate between them.

I wouldn't control the pump with a PID based on the suction side, particularly if this is a flooded suction pump. I would run based on another constraint, such as discharge pressure or flow rate if that matters, or else run flat out until I approach the NPSH limit. Then I would simply increment the speed down until NPSH is OK. I would use a simple deadband control like a home thermostat.
  Reply With Quote
Old December 12th, 2017, 05:01 PM   #9
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 273
I agree with Tom above. PID on inlet pressure is probably not the best approach, particularly if the liquid level in the rail car has a greater effect on the pressure than the pump speed.
  Reply With Quote
Old December 12th, 2017, 05:45 PM   #10
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,044
so more thoughts to consider

use line and load reactors for 480 volts if the motor length id over 50 ft. I would use them for less than 50 ft.
use shielded vfd cable for the motor leads to reduce noise in the cabinet.

regards,
james
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PID Control for pump problem Martindag LIVE PLC Questions And Answers 12 February 8th, 2017 02:09 PM
PowerFlex 525 - Lobe Pump Flow PID Control freju LIVE PLC Questions And Answers 7 February 7th, 2017 09:55 AM
PowerFlex 525 Open Loop Metering Pump Control Help shiftedbits LIVE PLC Questions And Answers 5 February 1st, 2014 02:15 PM
DI Water Centrifugal Pump Flow PID control Camcanpro LIVE PLC Questions And Answers 32 March 29th, 2013 08:47 AM
Metering Pump control with a flow meter VIRUZIE LIVE PLC Questions And Answers 8 September 15th, 2012 07:56 PM


All times are GMT -5. The time now is 09:53 PM.


.