RSLogix 5 IO File Help

If you take a look at the picture attached you can see that both I:000/0-4 and O:000/0-4 are used.

I was under the impression that the "000" in 0:000/0 was at least a logical slot number and therefore that any bit in the input and output files can only be used by either input or output.

The other issue is that with O:000/0-4 the total number of output bits goes to 36 and there are only 32 outputs points on the physical system as seen in the other attachment.

Any help is appreciated!
Attached Images
File Type: jpg Lid Return Logix 5 IO tables.jpg (33.3 KB, 31 views)
File Type: jpg Lid Return Physical IOs.jpg (47.6 KB, 26 views)
  Reply With Quote
Old December 19th, 2017, 11:38 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,870
With a PLC-5, all the I/O data tables always exist regardless of the physical hardware. In certain situations, you can have an input and an output card with the same logical slot numbers.

See this thread for some more information that should be useful.
http://www.plctalk.net/qanda/showthread.php?t=21174
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old December 19th, 2017, 11:45 AM   #3
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 345
And this thread:

PLC5 slot addressing(112814)
  Reply With Quote
Old December 19th, 2017, 12:06 PM   #4
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,407
Quote:
Originally Posted by lillquist View Post
I was under the impression that the "000" in 0:000/0 was at least a logical slot number and therefore that any bit in the input and output files can only be used by either input or output.
Not a "slot" number, but a "group" number. A group may occupy more than one physical slot within a chassis.
__________________
  Reply With Quote
Old December 19th, 2017, 01:35 PM   #5
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 183
Like OkiePC said, the I/O image table in the PLC-5 existed for ALL potential I/O, whether it was there or not.

In the old days of PLC-2, it was common practice to write to unused "Output" addresses for internal coils (what might be a "B3" address in PLC-5 parlance). Because there was no output card, it didn't affect anything. Memory was expensive back in those days.


I've seen a few cases in really old PLC-5 applications where that practice continued. It's possible in your case. I had first suspected you had a case of "Complimentary I/O" (what Okie was referring to "in certain cases"), but looking at the physical rack, that's not the case here.

Instead, you appear to have "Double-slot addressing", where the first TWO 8-bit input cards (red labels) are in the first "slot" register (I:000/0 - 7; I:000/10 - 17 respectively), and the other two 8-bit input cards are in I:001. These are then followed by the first 2 8-bit output modules (orange labels) in O:002, and the last 2 cards are in O:003.

This accounts for everything in your Usage Map.

HTH
  Reply With Quote
Old December 19th, 2017, 02:18 PM   #6
lillquist
Member
United States

lillquist is offline
 
Join Date: Dec 2017
Location: Denver
Posts: 7
Quote:
Originally Posted by Aardwizz View Post
I've seen a few cases in really old PLC-5 applications where that practice continued. It's possible in your case.
HTH
This is what I'm thinking, mostly because these 5 bits take me over the physical output limit. It seems like these 5 extra bits have to be used as internal memory.
Another reason is that this overlap of input and outputs is a common theme among other programs at this site so maybe the original programmer was used to doing things a certain way.

Thanks for all the help!!
  Reply With Quote
Old December 19th, 2017, 02:55 PM   #7
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,438
suggestion:

take a look at the "Switches" tab of the processor's status feature and tell us what it says for the "Addressing Mode" setting ... that will help the forum nail down what configuration you're dealing with ...

IMPORTANT:

use the "Switches" tab - and do NOT give us the "Rack Addressing" entry from the "IO Configuration" feature ... that's just "documentation" and it might not be set correctly ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old December 19th, 2017, 03:26 PM   #8
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 183
Quote:
Originally Posted by lillquist View Post
Another reason is that this overlap of input and outputs is a common theme among other programs at this site so maybe the original programmer was used to doing things a certain way.
Maybe. "Complimentary I/O" was also a popular technique back in the day, where Input & Output cards were alternated in the rack, and then with the proper dip switch setting, they would then be tied to the same O: and I: word references.

Your rack COULD have had that -- if the engineer had put two DIs then 2 DOs then 2 DIs and finally 2 DOs (since you have 8-bit cards), then with both "Double Slot" addressing and "Complementary I/O", everything would have been in I:000-I:001 and O:000-O:001.

Confusing? It took some getting used to. Now it's just legacy.
  Reply With Quote
Old December 19th, 2017, 04:42 PM   #9
lillquist
Member
United States

lillquist is offline
 
Join Date: Dec 2017
Location: Denver
Posts: 7
The processor is in 2 Slot addressing mode.
  Reply With Quote
Old December 19th, 2017, 05:57 PM   #10
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,179
My guess is that this was originally a PLC-2 system, which is consistent with the 8-point I/O modules, the 2-slot Addressing and the 1771-PA or 1771-P1 power supply.

In fact, I'm not sure how they got that power supply to work with a PLC-5/11; the official migration guides I've read suggest that they're compatible with RIO adapters but not PLC-5 CPUs. Maybe they did something creative with the power cable.

Aardwizz's comments about PLC-2 programmers being accustomed to using unavailable output memory as internal bits is consistent with the age of the system and lillquist's comments about other parts of the system reflecting early-1980's conventions.

lillquist: remember that PLC-2 and PLC-5 physical I/O bits are numbered in Octal; the bits 00 through 17 are just sixteen bits.

I try to get in the habit of calling out bit numbers audibly, like "One Two" instead of "Twelve".
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSLogix Micro Starter Lite - How can I add a 1746-IB16 card into the IO config? Ecnal LIVE PLC Questions And Answers 5 July 22nd, 2016 10:40 AM
Read a text file in RSLogix 5000 prats33 LIVE PLC Questions And Answers 16 December 14th, 2013 10:53 AM
Software for MicroLogix1200 SirCharles1 LIVE PLC Questions And Answers 7 July 17th, 2013 01:36 AM
Can I save my data from PLC to a file automatically on RSlogix 500? wormite LIVE PLC Questions And Answers 5 June 17th, 2010 11:27 PM
Rockwell Allen Bradley Programming Software, RSLogix 5, RSLogix 500, RS Linx, RSLogix vvcd LIVE PLC Questions And Answers 21 September 24th, 2009 10:04 PM


All times are GMT -5. The time now is 11:28 PM.


.