Hi,
Have seen a couple of occurrences of this error during search:
failed to go online with controller.
Unable to open connection -- all connections may be in use


From knowledgebase, it mentions that the 100% utilization is related to continuous task config.
If I change the task to periodic, will that assist in alleviating this issue.?
I am aware that the ethernet CPU is very loaded often & have plans in place to rectify, but interim is we need to keep it going.

Is there a way to reset port remotely, so at least IO Servers can reconnect succesfully & perhaps RS5k..?


Thanks
lc
  Reply With Quote
Old January 5th, 2018, 07:45 AM   #2
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: barranquilla
Posts: 2,532
Please check ethernet connections timing, probably they are too fast. Try to slow them down.
__________________
My two cents.
  Reply With Quote
Old January 5th, 2018, 09:07 AM   #3
Paully's5.0
Lifetime Supporting Member
United States

Paully's5.0 is offline
 
Join Date: Jan 2006
Location: WI
Posts: 1,991
This refers to CIP connections. The L35E I believe is limited to 32. CIP connections will be anything that communicates to the controller via remote IO, HMI/SCADA, PLC-PLC messages.

When it comes to remote IO, you have to be mindful of how many analog IO cards are in the remote rack. They consume 1 CIP connection each. My experience is that L35e using remote IO and lots of analog cards you'll hit your CIP limit pretty quickly.

More details of what the L35e is communicating to would be handy. Also, you can log onto the L35e webpage for diagnostics to see how many CIP connections are being used at any given time. Check the RPI to those IO adaptors as well.

Last edited by Paully's5.0; January 5th, 2018 at 09:09 AM.
  Reply With Quote
Old January 6th, 2018, 12:32 AM   #4
lostcontrol
Member
New Zealand

lostcontrol is offline
 
lostcontrol's Avatar
 
Join Date: May 2009
Location: NeverSayNever
Posts: 761
Thanks for replies
Quote:
Originally Posted by widelto View Post
Please check ethernet connections timing, probably they are too fast. Try to slow them down.
There is 6x VSD's & 1x Point IO rack, as well as some Produce/Consume connections to 2x other PLC's.
The VSD's are 250ms, Point IO is 100.

Quote:
Originally Posted by Paully's5.0 View Post
This refers to CIP connections. The L35E I believe is limited to 32. CIP connections will be anything that communicates to the controller via remote IO, HMI/SCADA, PLC-PLC messages.

When it comes to remote IO, you have to be mindful of how many analog IO cards are in the remote rack. They consume 1 CIP connection each. My experience is that L35e using remote IO and lots of analog cards you'll hit your CIP limit pretty quickly.
This is interesting about the analogs. There are 2x cards in the point rack.

Quote:
More details of what the L35e is communicating to would be handy. Also, you can log onto the L35e webpage for diagnostics to see how many CIP connections are being used at any given time. Check the RPI to those IO adaptors as well.
As above, as well as 2x Magelis HMI's, the SCADA IO Server & a large screen for general status ( so another IO Server..)
From the webpage, I noticed that there were 2x IO servers enabled. Disabling them both allowed access.
The other telling thing was that the large screen still had 4x connections. I'm putting this down to restarts of the application & it not releasing the connection properly.

Quote:
Originally Posted by grahamf View Post
You could try adjusting the System Overhead Time Slice setting to allocate more CPU time to the backend tasks such as comms. etc. I stumbled over a great article here that does a good job explaining.

https://*************/system-overhead-time-slice/
Cheers, slice is already at 50%..
Ethernet (?) CPU is consistently high ( > 70%)
Would changing this continuous task to periodic improve things?

The key things that were identified from the web server was the 2x IO Serves (they should of been redundant), as well as the large screen not disconnecting correctly.

But all things aside, getting online to the PLC should always be possible.
Is there a way to monitor the connection status & possibly release..?
I'm thinking a GSV/SSV possibly, but it might be limited to the port rather than a single connection?
  Reply With Quote
Old January 6th, 2018, 11:27 AM   #5
Paully's5.0
Lifetime Supporting Member
United States

Paully's5.0 is offline
 
Join Date: Jan 2006
Location: WI
Posts: 1,991
Quote:
Originally Posted by lostcontrol View Post
But all things aside, getting online to the PLC should always be possible.
Not if all the CIP connections are used so it may not be possible.

You really need to understand what is using CIP connections and how many. For example your VSDs. IIRC, powerflex com cards used to use 4 CIP connections, I believe newer firmware condensed it down to 1 but for arguments sake say it's 4 since you haven't mentioned specifics.

Your VSDs alone would be consuming 24/32 connections.

Your point IO rack will consume 1 if "rack optimized" for discrete IO plus the 2 analog cards. So you are now consuming 27/32.

Your HMI/SCADA and produced/consumed tags could easily consume the remaining 5 and you're out-of-luck connecting Logix5000 to the PLC.

You need to do your homework on this one, check your firmware versions and CIP connections. Look at your HMI software and IO server configurations. If they are not properly releasing CIP connections you may have to patch/update that software. Check your produced/consumed tags, it might be better to pack comms into a MSG instruction.

L35Es are nice little units however 2 CIP connection limit is a major bottleneck.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1769 AENTR comm's on power cycle John Morris LIVE PLC Questions And Answers 16 August 3rd, 2017 05:33 PM
CompactLogix 1769 l35e ethernet hanging up? kf5pv LIVE PLC Questions And Answers 19 February 19th, 2014 10:56 AM
1769 L35E to Kinetix 300 via? junkerjorg LIVE PLC Questions And Answers 0 February 27th, 2013 04:21 PM
Using 1769 I/O via Ethernet with ControlLogix controller johny-rock LIVE PLC Questions And Answers 6 February 20th, 2012 11:25 AM
Lost Ethernet option link from a 1769 L35E captain_fracasse LIVE PLC Questions And Answers 7 October 2nd, 2008 02:23 PM


All times are GMT -5. The time now is 06:49 AM.


.