Red Lion to GE 90-30

Hi Everyone,
Got a new project coming up and one of the older pieces of equipment has a GE 90-30 311 PLC. I would like to connect that to the Red Lion G09 HMI.

I have been doing some research and it looks like the 15 pin connection is RS-485 Communication. Is that correct? If so then connecting it to the G09 485 port should be pretty straight forward. I know RL makes a cable for the communications so I am trying to get a quote for that now.

Next question: I have done some work with GE Versamax and the RX3i processors but never worked with the 90-30. Will my PME 9.5 work to upload the program from the processor? This unit is about 20 years old as far as I can tell. Just wondering if I will have to convert it from some older file source. Let me know your thoughts on that.

Thanks for any advice you can give.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old January 31st, 2018, 03:10 PM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,496
I think you'll have better luck if can convert the Logicmaster or VersaPro project file to PME first.
I just tried an experiment. I cleared the PLC memory using Logicmaster version 9.05. Then I created a new project with the hardware configuration and one rung of ladder logic, a NO contact addressed to %I001 driving a coil instruction addressed to %Q0033. The hardware configuration has a CPU363, two 16-point input modules and two 16-point output modules. I downloaded the logic and hardware configuration to the PLC with Logicmaster, got Logic Equal and PLC running.
I then went online with PME version 7.0. I was able to upload the hardware configuration and the memory values but not the ladder logic. When I tried to upload the ladder logic I got Error 8095 and Error 8509. The help files for those errors were unhelpful in either resolving or understanding the errors.
After uploading the hardware configuration PME still said configuration not equal although the list of modules matched what was present. After downloading the hardware configuration with PME the message reverted to configuration equal.
  Reply With Quote
Old January 31st, 2018, 04:17 PM   #3
Bullzi
Lifetime Supporting Member
United States

Bullzi is online now
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,276
I am waiting for the original program but once I get it how do I convert it? Is there a convert utility in PME? I dont have Logicmaster or VersaPro.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old January 31st, 2018, 04:31 PM   #4
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,496
Yes, you start a new project in PME and then you can import both logic and hardware configuration from a Logicmaster or VersaPro project.
  Reply With Quote
Old January 31st, 2018, 07:31 PM   #5
Bullzi
Lifetime Supporting Member
United States

Bullzi is online now
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,276
Thanks Steve!!

Am I correct in thinking the DB15 Connection on the CPU is RS-485?
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old January 31st, 2018, 08:12 PM   #6
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,496
Also correct. The name of the serial protocol is either SNP or SNPX. The latter is a stripped-down version optimized for HMI communications. The full SNP protocol supports program transfers which of course isn't needed for HMIs. If your CPU311 is really old, it won't support SNPX. Support for SNPX began at firmware version 4.40 in 1994. That corresponds to CPU311L.
Pin assignment for the RS485 port can be found in the manual GFK-0356.
  Reply With Quote
Old February 1st, 2018, 12:43 PM   #7
Bullzi
Lifetime Supporting Member
United States

Bullzi is online now
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,276
I just got a picture of the panel. The PN of the PLC is IC693CPU311W. So will that unit have SNPX ?
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old February 1st, 2018, 12:53 PM   #8
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,496
Yes, CPU311W is newer than CPU311L.
  Reply With Quote
Old February 1st, 2018, 03:49 PM   #9
Bullzi
Lifetime Supporting Member
United States

Bullzi is online now
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,276
I figured but wanted to make sure. Thanks for all the help.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
GE Fanuc Series 90 30 Johnny T LIVE PLC Questions And Answers 31 April 22nd, 2018 03:06 PM
Simulating Unity and Red Lion Crimson 3.0 jordan45 LIVE PLC Questions And Answers 1 January 8th, 2018 12:36 PM
Quickpanel JR migration to Red Lion Kadet Question Plutonius LIVE PLC Questions And Answers 4 May 15th, 2017 11:33 AM
Finally a Red Lion G3 but with Siemens MarkNightingale LIVE PLC Questions And Answers 2 June 29th, 2012 03:33 PM
Red Lion programming issues and answers Rik LIVE PLC Questions And Answers 4 November 4th, 2009 10:14 AM


All times are GMT -5. The time now is 10:12 PM.


.