Old January 31st, 2018, 04:36 AM   #1
joshi14
Member
Germany

joshi14 is offline
 
Join Date: Jan 2018
Location: Berlin
Posts: 2
A little help regarding a pressure switch!!!

i am a beginner plc programmer and have some confusion, a little help would be appreciated . why do we use a normally close contact when we are dealing with low pressure switch and use normally open contact when dealing with high pressure switch? i saw a programmer doing this while writing his program in ladder diagram and i got confused. should not it be that both the switches are normally close in both low and high and opens if the pressure drops down a certain level or increases above certain level?

thanks in advance
  Reply With Quote
Old January 31st, 2018, 10:24 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,522
Don't think of the contacts in the program as normally open and normally closed. Use the terms "examine if 0 (open)" and "examine if 1 (closed)" The contents of the addresses being a 1 or 0 is what the ladder logic instructions are checking. Using the terms normally open and normally closed for ladder logic instructions can lead to confusion even though Automation Direct actually names their instructions this way...

Now with that out of the way, the switch itself could be normally open or normally closed. If you make the decision about which contacts to select for use in your system, think about what you want to happen if the wire from the sensor breaks. Do you want the PLC to "think" that a pressure problem has occurred or do you want it to "think" that everything is okay?

In many cases both sensors act exactly the same way and are wired the same way but the low pressure switch closes under normal operating conditions and the high pressure switch closes under a high pressure condition. In most cases, in ladder logic, you are looking for a "0" (off) input from the low pressure switch to indicate a problem and you are looking for a "1" from a high pressure sensor to indicate a problem.

Clear as mud?

All newbies should watch these videos in order:

https://www.youtube.com/watch?v=T3tn...PxGunBTtPcS3Ez

It's based on Allen Bradley PLCs but the concepts are pretty much universal.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old January 31st, 2018, 10:40 PM   #3
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,309
Quote:
Originally Posted by joshi14 View Post
i am a beginner plc programmer and have some confusion, a little help would be appreciated . why do we use a normally close contact when we are dealing with low pressure switch and use normally open contact when dealing with high pressure switch? i saw a programmer doing this while writing his program in ladder diagram and i got confused. should not it be that both the switches are normally close in both low and high and opens if the pressure drops down a certain level or increases above certain level?

thanks in advance
Ideally, all switches should be NC, and open in a fault condition, but we don't live in a perfect world. Sometimes, you just have to deal with what you have.
__________________
  Reply With Quote
Old February 1st, 2018, 10:47 AM   #4
Mara
Member
Finland

Mara is offline
 
Join Date: Jan 2017
Location: Finland
Posts: 39
Quote:
Originally Posted by Bit_Bucket_07 View Post
Ideally, all switches should be NC, and open in a fault condition, but we don't live in a perfect world. Sometimes, you just have to deal with what you have.
Not always. For example in cases where you have to know position of certain part before other parts can move. Sorry my English but I believe you know what I mean. Of course in most of cases nc is safest but like I said, not always
  Reply With Quote
Old February 1st, 2018, 12:33 PM   #5
Racer5039
Member
United States

Racer5039 is offline
 
Join Date: Oct 2014
Location: midwest
Posts: 69
I would say the correct way for high and low pressure will be low wired to NO this will send power to the input in a normal condition. If a wire is broken, you have a fault. In the case of the high pressure side it should be wired NC. This will give you a high input in normal operation. If you have a high pressure issue or a bad wire, you get a fault. If High was wired NO and you have a wiring problem, the PLC will never see the High presser Issue. Wired NO & NC, Safe on both counts. We need to think about not only the normal state but also the possibility of a wiring problem. You want to fail in a safe state.

Last edited by Racer5039; February 1st, 2018 at 12:36 PM.
  Reply With Quote
Old February 1st, 2018, 05:28 PM   #6
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 214
Normal is a confusing term.

A pushbutton is normal when unpushed
A relay is normal when de-energised
A safety device is normal when un-interrupted

Pressure limit switches both have the same normal state but the pressure is normally high in one and low in the other.
  Reply With Quote
Old February 1st, 2018, 06:46 PM   #7
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,314
Quote:
Originally Posted by joshi14 View Post
i am a beginner plc programmer and have some confusion, a little help would be appreciated . why do we use a normally close contact when we are dealing with low pressure switch and use normally open contact when dealing with high pressure switch? i saw a programmer doing this while writing his program in ladder diagram and i got confused. should not it be that both the switches are normally close in both low and high and opens if the pressure drops down a certain level or increases above certain level?

thanks in advance
Okay...it appears we are using NO contacts on both PRESSURE SWITCHES...

I think interpreting this may depend on if the "contact" you refer to is in plc or switch itself.

For example.... if you have 50 PSIG operating pressure and the low is adjusted at 40 PSIG and the high is adjusted at 60 PSIG.

In reference to 0 PSIG (Atmospheric pressure) the low would be energized because you are above 40 PSIG. And the high is not energized till you get to 60 PSIG.
So...In the PLC LOGIC....
The Low PS would be seen as closed (NC) for okay, because you are above Low Press limit. And switch will open below setpoint for alarm.
Thee high PS is seen as NO for okay, because you are below the high pressure limit. And the switch will close above setpoint for alarm.
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; February 1st, 2018 at 06:48 PM.
  Reply With Quote
Old February 1st, 2018, 07:57 PM   #8
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,309
Quote:
Originally Posted by Geoff White View Post
Normal is a confusing term.

A pushbutton is normal when unpushed
A relay is normal when de-energised
A safety device is normal when un-interrupted

Pressure limit switches both have the same normal state but the pressure is normally high in one and low in the other.
I agree that "normal" can be a confusing bit of terminology sometimes.

For instance, I've seen normally open micro-switches operated by cams in conveyor e-stop enclosures that provide a closed contact when the switch operator is not tripped, or is in the "normal" condition.
__________________
  Reply With Quote
Old February 1st, 2018, 08:10 PM   #9
jaden
Member
United States

jaden is offline
 
Join Date: Sep 2009
Location: Pleasant Dale, Nebraska
Posts: 89
With devices such as pressure or temperature switches, I prefer the terms such as Open on Rise, Close on Fall, etc. Takes out some of the confusion.
  Reply With Quote
Old February 1st, 2018, 08:12 PM   #10
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,309
Quote:
Originally Posted by jaden View Post
with devices such as pressure or temperature switches, i prefer the terms such as open on rise, close on fall, etc. Takes out some of the confusion.
+1
__________________
  Reply With Quote
Old February 2nd, 2018, 12:27 AM   #11
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,314
Quote:
Originally Posted by jaden View Post
With devices such as pressure or temperature switches, I prefer the terms such as Open on Rise, Close on Fall, etc. Takes out some of the confusion.
It seems even simpler to use...Open Above or Closed Below, etc.
My equipment is vacuum/pressure, so that is why I use these terms.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old February 2nd, 2018, 06:41 AM   #12
joshi14
Member
Germany

joshi14 is offline
 
Join Date: Jan 2018
Location: Berlin
Posts: 2
Thanks a lot guys, i think i got it now.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Pressure Switch recommendations Saturn_Europa1 LIVE PLC Questions And Answers 8 January 5th, 2017 07:01 PM
SICK PAC50 (CCD) Pressure switch - Analog Output JohanM LIVE PLC Questions And Answers 0 December 15th, 2015 01:31 AM
level switch vs pressure switch for dry run protection Charbel LIVE PLC Questions And Answers 15 November 11th, 2015 11:56 PM
Pressure Switch Woes JBradley LIVE PLC Questions And Answers 24 November 7th, 2007 12:42 AM
Pressure-Position Orn Jonsson LIVE PLC Questions And Answers 5 July 9th, 2002 03:44 PM


All times are GMT -5. The time now is 06:45 PM.


.