1771 A2b Bad Slot

Greetings Friends,

I have a 1771-A2B with one slot not recognizing inputs nor will it turn on any output. It started acting up intermittently on a couple inputs, now nothing.

It is Slot C4- D4 only using C of course. I have taken the chassis apart completely to examine the board and I can see no physical damage.

I also have read out all of the connection points from the socket to the back of the board and the solder traces. I also squeezed (Tightened) and cleaned the socket pins to make sure the card was getting a good connection. I am coming up empty.

I re-soldered the holes that are pass through near pin 12.

Although the card sees an input, the PLC does not in the input image table-

I put a "-1" in the output image table to set all output bits and nothing turns on for that slot. I tested this with several input and output cards and every other slot works.

I know they are somewhat inexpensive on Ebay but I would like to find out where the failure point is.

Any Ideas?

Thank you for your time.... Sincerely!
-
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------

Last edited by CaspianSage; January 30th, 2018 at 09:22 AM.
  Reply With Quote
Old January 30th, 2018, 09:31 AM   #2
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 1,960
It's been a few years since I touch these, but I recall that most of the issues were related to the failed chassis DIP switch that caused PLC or adapter to read slots incorrectly.
  Reply With Quote
Old January 30th, 2018, 11:33 AM   #3
CaspianSage
Member
United States

CaspianSage is offline
 
CaspianSage's Avatar
 
Join Date: Jan 2017
Location: Where I Am
Posts: 104
Quote:
Originally Posted by Contr_Conn View Post
It's been a few years since I touch these, but I recall that most of the issues were related to the failed chassis DIP switch that caused PLC or adapter to read slots incorrectly.

I was wondering about that possibility, kind of shrugged that off as unlikely but now that you mention it that makes sense. I will check that out. Maybe dirty contacts in the switch......

Thanks!
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------
  Reply With Quote
Old January 30th, 2018, 12:35 PM   #4
CaspianSage
Member
United States

CaspianSage is offline
 
CaspianSage's Avatar
 
Join Date: Jan 2017
Location: Where I Am
Posts: 104
..... Well the dip switch seems to check out ok. Not much to this board so really puzzling.
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------
  Reply With Quote
Old January 30th, 2018, 01:17 PM   #5
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 1,960
Are you sure that this is not controller or adapter?
  Reply With Quote
Old January 30th, 2018, 08:13 PM   #6
CaspianSage
Member
United States

CaspianSage is offline
 
CaspianSage's Avatar
 
Join Date: Jan 2017
Location: Where I Am
Posts: 104
Quote:
Originally Posted by Contr_Conn View Post
Are you sure that this is not controller or adapter?

I am not sure what you are asking... If you mean am I mistaken as to what I have, well interesting question.

I am using a PLC 5/20, I don't think an adapter has an I/O image table.

I first started seeing the problem with an actively running program not registering inputs.
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------
  Reply With Quote
Old January 30th, 2018, 08:54 PM   #7
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 1,960
How do you know that 5/20 is OK?
Did you try it in a different chassis?
  Reply With Quote
Old January 31st, 2018, 09:59 AM   #8
CaspianSage
Member
United States

CaspianSage is offline
 
CaspianSage's Avatar
 
Join Date: Jan 2017
Location: Where I Am
Posts: 104
Quote:
Originally Posted by Contr_Conn View Post
How do you know that 5/20 is OK?
Did you try it in a different chassis?
Yes, First thing did, I have 3 PLC5s and tested with all of them. I changed the chassis out in the working system so I could use slot 4. Test Benching with 2 of the other plc5s in the defective chassis- Its just the one slot that is a problem. No problem with any of the 3 processors in the other chassis.

I want to use this chassis for remote i/o. I can probably get by with out that slot but I don't want to use it in case other slots fail.

Thank you!
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------
  Reply With Quote
Old January 31st, 2018, 10:51 AM   #9
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 1,960
Quote:
I want to use this chassis for remote i/o
Just keep in mind that chassis DIP switch setting for RIO adapter in not the same as for the processor.
  Reply With Quote
Old January 31st, 2018, 10:55 AM   #10
CaspianSage
Member
United States

CaspianSage is offline
 
CaspianSage's Avatar
 
Join Date: Jan 2017
Location: Where I Am
Posts: 104
Solved -Loose Pins in Processor Socket

Went back through all the socket connections for the PLC Slot, first slot in the chassis.

Some still looked looser than they ought to be.

I used a small screw driver and pushed them back together, first left to right then right to left, making the gap between them as small as I could with just enough room to slide the processor into the slot.

All works now but unfortunately I got one set the pins in one slot to tight and when I put the processor back in, it pushed them down into the connector, still makes contact but now I need to fix that or get another socket..

Anyway Problem solved. Loose pins in processor socket.

Thank you!
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------
  Reply With Quote
Old February 1st, 2018, 10:44 AM   #11
CaspianSage
Member
United States

CaspianSage is offline
 
CaspianSage's Avatar
 
Join Date: Jan 2017
Location: Where I Am
Posts: 104
Thank You!

Quote:
Originally Posted by Contr_Conn View Post
Just keep in mind that chassis DIP switch setting for RIO adapter in not the same as for the processor.
Exactly, I have the settings for RIO - The chassis is repaired now and working fine.

Thank you for your input here,

Although when you mentioned the processor possibly having an issue I knew it was ok, but your post prompted me to check the pins for the processor again and that is where the problem was.

I really appreciate you staying with this topic through resolution of the problem. So a big thanks!

This is one of the best forums on the net I use.
__________________
Caspian

---------------------------------------
1+1 = 3 and I never was good at math.
----------------------------------------
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Wago IO Process Image Data... Paully's5.0 LIVE PLC Questions And Answers 3 September 8th, 2016 06:25 AM
PLC5 'Slot Addressing' rlmts LIVE PLC Questions And Answers 19 February 19th, 2016 09:37 AM
How The Choose The Asb Module As A 1/2 Slot, 1 Slot, 2 Slot In Ab Redundancy siva_maddala LIVE PLC Questions And Answers 4 January 19th, 2007 02:41 AM
PLC 5/15 processor...Please Help omars LIVE PLC Questions And Answers 28 March 14th, 2006 08:30 PM
Part rejection down line Bob O LIVE PLC Questions And Answers 51 October 28th, 2004 08:20 AM


All times are GMT -5. The time now is 04:14 AM.


.