You are not registered yet. Please click here to register!


 
 
plc storereviewsdownloads
This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc.
 
Try our online PLC Simulator- FREE.  Click here now to try it.

---------->>>>>Get FREE PLC Programming Tips

New Here? Please read this important info!!!


Go Back   PLCS.net - Interactive Q & A > PLCS.net - Interactive Q & A > LIVE PLC Questions And Answers

PLC training tools sale

Reply
 
Thread Tools Display Modes
Old February 6th, 2018, 07:49 AM   #1
richleva
Member
Canada

richleva is offline
 
Join Date: Sep 2012
Location: ontario
Posts: 69
Fancy Exclamation Scale Analogue

Hello,

I'm confused with Instruction called "SCP" with RSlogix. Never really had to use this one, till now.

I need to control an Acid pump at a water treatment plant, Using an analogue output of a PLC. This PLC only has 0-10V analogue output card. So I was going to install a 500Ohm resister to get my 4-20Ma. So at 2Votls will be my 4mA and 10 Volts will be 20mA

If the pump for example is 0-37 liter/hour

I assume the:
Input min is 0
Input Max is 37

How do I figure the Scaled Min and Scaled Max?
Also remembering that 2 Volts should be 4mA

Thanks everyone
  Reply With Quote
Old February 6th, 2018, 07:56 AM   #2
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,380
What is the model number of the analog output card ?
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old February 6th, 2018, 07:59 AM   #3
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 643
If it were me I would scale the output of the pump to another variable in mA desired. Then use another block to scale the mA to the V.

It will make it easier for the next guy, especially as you can comment the rung, it makes it easy on the eye to what you have done.

So 0 to 37 scales to 4 to 20 then 4 to 20 then scales to say 2000 to 10000, 6554 to 32767 on your OP card (or whatever units it is set for)
  Reply With Quote
Old February 6th, 2018, 08:30 AM   #4
richleva
Member
Canada

richleva is offline
 
Join Date: Sep 2012
Location: ontario
Posts: 69
Quote:
Originally Posted by daba View Post
What is the model number of the analog output card ?
Here is the model number of the PLC, There's no cards attached it comes with 2 analogue outputs 0 -10V
1766-L32BXBA
  Reply With Quote
Old February 6th, 2018, 08:39 AM   #5
richleva
Member
Canada

richleva is offline
 
Join Date: Sep 2012
Location: ontario
Posts: 69
Quote:
Originally Posted by janner_10 View Post
If it were me I would scale the output of the pump to another variable in mA desired. Then use another block to scale the mA to the V.

It will make it easier for the next guy, especially as you can comment the rung, it makes it easy on the eye to what you have done.

So 0 to 37 scales to 4 to 20 then 4 to 20 then scales to say 2000 to 10000, 6554 to 32767 on your OP card (or whatever units it is set for)
Hi Janner,

What do you mean by (6554 to 32767 on your OP card)?
  Reply With Quote
Old February 6th, 2018, 10:12 AM   #6
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 643
Taken from manual:

Number of inputs 2 single-ended
Voltage output range 010 V DC - 1 LSB
Type of data 12 bit unsigned integer
Step response 2.5 ms @ 95%
Load range Voltage output >1 KΩ
Output coding (010V DC) 04095
Output resolution 12 bit
Analog output setting time 3 ms (max.)
Overall Accuracy
-2060 C (-4140 F) 1.0% of full scale
Electrical isolation Non-isolated with internal logic
Cable length 30 m (98 ft) shielded cable

So your 2v to 10v output would be 819 - 4095.

Something like this:

  Reply With Quote
Old February 6th, 2018, 10:23 AM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,120
[quote]
Quote:
Originally Posted by richleva View Post
Hello,
I need to control an Acid pump at a water treatment plant, Using an analogue output of a PLC. This PLC only has 0-10V analogue output card. So I was going to install a 500Ohm resister to get my 4-20Ma. So at 2Votls will be my 4mA and 10 Volts will be 20mA

/QUOTE]
Your acid pump is also a load on the circuit. What is it's value?

You are better off using a converter to convert voltage to current.

See link(s) for an example..

https://www.automationdirect.com/adc...er_Input/FC-33

https://www.google.com/search?rlz=1C...w=1671&bih=830
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; February 6th, 2018 at 10:28 AM.
  Reply With Quote
Old February 6th, 2018, 10:37 AM   #8
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,120
Quote:
Originally Posted by janner_10 View Post
Taken from manual:

Number of inputs 2 single-ended
Voltage output range 010 V DC - 1 LSB
Type of data 12 bit unsigned integer
Step response 2.5 ms @ 95%
Load range Voltage output >1 KΩ
Output coding (010V DC) 04095
Output resolution 12 bit
Analog output setting time 3 ms (max.)
Overall Accuracy
-2060 C (-4140 F) 1.0% of full scale
Electrical isolation Non-isolated with internal logic
Cable length 30 m (98 ft) shielded cable

So your 2v to 10v output would be 819 - 4095.

Something like this:

Only one "SCP" is required. First one with scaled min/max at 819-4095.

FYI: the ML1400 will not allow two "SCP"'s on the same rung. It uses RSLogix500 not RSLogix5000.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 6th, 2018, 11:40 AM   #9
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,120
Quote:
Originally Posted by Mickey View Post
Only one "SCP" is required. First one with scaled min/max at 819-4095.

FYI: the ML1400 will not allow two "SCP"'s on the same rung. It uses RSLogix500 not RSLogix5000.

Should have said on the same rung in series, parallel would be ok.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
GSE 465 Scale issues muusic_man LIVE PLC Questions And Answers 4 October 22nd, 2013 10:13 AM
Mitsubishi Analogue Input & Output programming sttchui LIVE PLC Questions And Answers 0 January 18th, 2011 07:56 PM
Blown analogue input... Siemens cpu Combo LIVE PLC Questions And Answers 2 December 14th, 2010 06:59 PM
315-2 DP to Scale on Profibus runx999 LIVE PLC Questions And Answers 4 January 5th, 2008 05:21 AM
Scale an analogue value Combo LIVE PLC Questions And Answers 11 November 26th, 2006 10:32 AM