Need help - can't go online and upload project from 1756-L63 controller

Hello!
I need your assistance with the following issue.
I need to upload project from 1756-L63 (v19.11) B Series controller for further diagnosis. I do it via 1756-EN2T ethernet communication module. I can see via RSWho RSLinx all PLC configuration and can browse all modules in PLC chassis. But when I try to go online with 156-L63 module or to upload its project into RSLogix5000 I receive error message that RSLinx communication failed and can't go online with controller (error 701-80042535). I found an article in RA Knowledbase on this RSLinx error (#40473) and did all described actions (delete the Harmony files, reboot RSLinx, create new driver, reboot PLC with power cycle and reboot whole PC, disconnect battery and CF card, wait few minutes and then re-connect battery without insertion back a CF card). And after the last action (re-connection battery and power up controller without CF card inserted) I at last could connect to controller and go online with it. But when I tried to upload project I received a message that PLC doesn't contain any project to upload. That's correct I thought, because CF is not inserted and controller lost its project from the memory after battery re-connection. Then I install CF card back in the controller, disconnect battery and power up PLC to make a trick with memory corruption action to copy project from CF card into controller memory. Controller went in RUN without any problems. But when I tried to go online with controller I received an error RSLinx communication failed (701-80042535) again.
I repeat all above described actions and found out that the the only case when I can go online with controller is when its memory is clear without any project. When I copy project from CF card to controllers memory I back again could't go online with it.
I also checked does controller secured or not with Logix CPU security tool. And it doesn't. I saw status UNSECURED in the tool's window. And there was also no any password has been set for controller.
May be anyone of you can advice me how can I fix this strange issue?

You can find the screenshots of error messages and online controller properties windows in the attachment.

Looking forward to your feedback. Any help will be appreciated a lot.

Best regards, Oleksandr.
Attached Images
File Type: jpg Empty controller upload message.jpg (37.1 KB, 7 views)
File Type: jpg Go online error message.jpg (37.6 KB, 8 views)
File Type: jpg Controller online properties - 1.jpg (41.9 KB, 11 views)
File Type: jpg Controller online properties - 2.jpg (44.6 KB, 8 views)
File Type: jpg Controller online properties - 3.jpg (43.7 KB, 8 views)
  Reply With Quote
Old February 7th, 2018, 05:20 AM   #2
dowthebow
Member
Ireland

dowthebow is offline
 
Join Date: Aug 2014
Location: Kildare
Posts: 27
There is currently an issue with a windows security update, affects similar to your problems.
Description of the fix here -
http://forums.mrplc.com/index.php?/t...comment-160412
  Reply With Quote
Old February 7th, 2018, 05:29 AM   #3
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 622
From your online properties pic: You have a non-recoverable major fault. The PLC has died and the project won't be there anymore.
  Reply With Quote
Old February 7th, 2018, 07:22 AM   #4
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,372
Quote:
Originally Posted by janner_10 View Post
From your online properties pic: You have a non-recoverable major fault. The PLC has died and the project won't be there anymore.
janner is quite correct, there is no project in the controller to upload, as can be seen in the picture "online properties - 2". The controller name is "<no name>".

For Major, Non-Recoverable Faults, the controller will dump the current program. This is a protection measure, as the controller can't be relied on to run anything. I suspect the Controller has died, but it might be possible to flash it again - could be worth a try.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens Step7 - File > SaveAs on ONLINE Project mcjschmidt LIVE PLC Questions And Answers 4 October 17th, 2016 06:42 AM
Does Denying Future Access Allow Online Edits Secpcb LIVE PLC Questions And Answers 17 June 20th, 2016 06:22 AM
Error 701-8004250A.Failed to go online with controller. Unable to Open connection asim_rana LIVE PLC Questions And Answers 5 March 5th, 2016 05:43 PM
Recommendation for a good class on ControlLogix5000? rustydud LIVE PLC Questions And Answers 1 February 8th, 2013 04:23 PM
can't upload from or get online to controllogix 5555 Btherealist_644 LIVE PLC Questions And Answers 5 January 29th, 2013 08:49 PM


All times are GMT -5. The time now is 02:04 AM.


.