Analog input values S7

Im a little rusty regarding S7 and analog value processing atm so I hope I could get some answers.


What is normally the fault when getting overflow on analog value from a sensor ?

On underrange/underflow its broken wire etc. but on overflow what will the cause most likely be?
  Reply With Quote
Old March 2nd, 2018, 08:26 AM   #2
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,224
If you are talking mA loop then an overflow is too much current. Current depends on Voltage and Resistance, so if the voltage driving the loop is too high for the sensor to control, or if the resistance of the loop falls too low, maybe because of a short circuit. Also for mA systems ground loops can cause both failures, it is where the 0V on the sensor and PLC aren't at the same potential.
  Reply With Quote
Old March 2nd, 2018, 09:28 AM   #3
boneless
Lifetime Supporting Member + Moderator
United States

boneless is offline
 
Join Date: Feb 2008
Location: OKC
Posts: 1,414
Some instruments also use overflow to indicate an error.
  Reply With Quote
Old March 4th, 2018, 06:19 AM   #4
Mars
Member
Denmark

Mars is offline
 
Join Date: Oct 2014
Location: Copenhagen
Posts: 17
Quote:
Originally Posted by BryanG View Post
If you are talking mA loop then an overflow is too much current. Current depends on Voltage and Resistance, so if the voltage driving the loop is too high for the sensor to control, or if the resistance of the loop falls too low, maybe because of a short circuit. Also for mA systems ground loops can cause both failures, it is where the 0V on the sensor and PLC aren't at the same potential.
But ground loops is only relevant if the instruments are powered by the 4-20 mA ? And not by external power supply?
  Reply With Quote
Old March 4th, 2018, 11:47 AM   #5
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,224
Quote:
But ground loops is only relevant if the instruments are powered by the 4-20 mA ? And not by external power supply?
Either one can get ground loops. The instruments with an external power supply by their design have a separate 0V, and unless the 4-20ma output is isolated from that 0V, or the PLC input is isolated from the PLC 0V, you will likely have problems unless the 0V can be tied together.

You can also get ground loops in a 4-20mA loop when a loop powered sensor isn't isolated. Fast sensing thermocouple sensors are often electrically bonded to the case and so need isolated converters to avoid issues. I had problems with a guided radar level sensors, it was fine when one was powered up, but if a second was used on a tank that had the same earth as the first they both gave the reading of the fullest tank.

There is an argument that you can avoid ground loops by not grounding anything, for me it is like saying you shouldn't earth any metalwork on a machine to avoid electric shocks.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How to take average analog input data when values are not so stable. ahsan1820 LIVE PLC Questions And Answers 0 June 10th, 2013 05:18 AM
AB Control Logix Analog Input Configuration noface LIVE PLC Questions And Answers 6 April 30th, 2013 08:11 AM
S7 1200 Processing of analog input (mA) npalavras LIVE PLC Questions And Answers 5 April 27th, 2013 03:49 PM
ML1100 analog input help kbradray LIVE PLC Questions And Answers 6 December 11th, 2007 05:13 PM
analog input SIMATIC S7-200, EM235 sarac LIVE PLC Questions And Answers 1 October 26th, 2006 03:32 AM


All times are GMT -5. The time now is 02:21 AM.


.