PowerFlex 753 OL Current Protection?

Hey fellas,

Been getting absolutely hammered this week with tons of cool and exciting new weird problems so here's another one that I believe I know the answer but would love some other ideas.

The customer has 2 Powerflex 753 VFD's individually controlling 2 motors that operate their own tri plex plunger pumps. (PID controls speed reference for 1, if 1 cant reach setpoint after x amount of time a seperate PID controls both) but we haven't got to the fun of tuning that yet.

We start the first ~325 HP motor and tested it full speed with no problems.
we start the second one (~250HP) by itself and ran it full speed with no problems.

When we start both motors and set them to 44hz the bigger motor's powerflex drops down to 33hz on an OL current fault/alarm.

The only thing I can think of that could cause this is a spike in pressure which forces the drive to work harder? Its getting ~900psi on the discharge line but I almost want to say that the motor is undersized for the application. all the name plate information is correct in the drive, power is all good, I really cant find another explanation for this. Just want to collect a few more ideas before I respond to the customer that they need a new shiny expensive motor.

Thanks for the help fellas,
  Reply With Quote
Old March 8th, 2018, 12:16 AM   #2
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 404
Yeah, the only thing I can think is exactly what you're suggesting- the load becomes too high for the motors when both pumps are on at the same time.

Only other thing could be if the feeder isn't sized right, the voltage could be sagging when both are on at the same time, raising the amp draw.
  Reply With Quote
Old March 8th, 2018, 12:37 AM   #3
Ih8Siemens
Lifetime Supporting Member
United States

Ih8Siemens is offline
 
Join Date: Dec 2017
Location: NoDak
Posts: 49
Quote:
Originally Posted by rupej View Post
Yeah, the only thing I can think is exactly what you're suggesting- the load becomes too high for the motors when both pumps are on at the same time.

Only other thing could be if the feeder isn't sized right, the voltage could be sagging when both are on at the same time, raising the amp draw.
I didn't even think of that....I will have the electricians on site check it out tomorrow.
  Reply With Quote
Old March 8th, 2018, 09:39 PM   #4
Ih8Siemens
Lifetime Supporting Member
United States

Ih8Siemens is offline
 
Join Date: Dec 2017
Location: NoDak
Posts: 49
Quote:
Originally Posted by rupej View Post
Yeah, the only thing I can think is exactly what you're suggesting- the load becomes too high for the motors when both pumps are on at the same time.

Only other thing could be if the feeder isn't sized right, the voltage could be sagging when both are on at the same time, raising the amp draw.
***Update***
The motor was in fact under sized.... Someone is taking an *** chewing.
  Reply With Quote
Old March 9th, 2018, 08:25 AM   #5
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,182
Something else to consider.
when 2 motors are connected to a vfd, the vfd must be sized to to accommodate both motors plus extra .

james
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PowerFlex 753 Short UV n.costasilva LIVE PLC Questions And Answers 5 August 29th, 2017 07:42 PM
(Very) Basic Powerflex 753 question SamW LIVE PLC Questions And Answers 4 June 6th, 2016 11:06 AM
Datalink Datatype Powerflex 753 ahuberee LIVE PLC Questions And Answers 1 April 22nd, 2016 09:41 AM
PowerFlex 753 won't power up. tjntjntjn LIVE PLC Questions And Answers 3 April 20th, 2016 06:28 PM
Powerflex 753, clearing fault from HIM LMDAVE LIVE PLC Questions And Answers 5 December 16th, 2015 12:51 PM


All times are GMT -5. The time now is 07:16 PM.


.