What do you guys use for connecting several Modbus RS485 devices with a single RJ45 port in the one panel? and terminating resistors?
  Reply With Quote
Old March 8th, 2018, 01:04 PM   #2
kolyur
Lifetime Supporting Member + Moderator
United States

kolyur is offline
 
kolyur's Avatar
 
Join Date: Oct 2004
Location: Wooster, Ohio
Posts: 1,409
I've used these in the past:
http://www.redlion.net/accessory/rj4...llel-connector

If you download the datasheet they have a similar product that has a RJ45 breakout terminal block, looks like a nice way to add a terminating resistor.
__________________
John

Last edited by kolyur; March 8th, 2018 at 01:07 PM.
  Reply With Quote
Old March 8th, 2018, 01:32 PM   #3
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,860
I use a lot of Winford products.... great quality, prices are better than anyone else in the market, great supply of different **** that we need and they normally ship the same day or the next

https://www.winford.com/products/brk8p8csj4b.php
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old March 8th, 2018, 03:44 PM   #4
swimmy67
Member
United States

swimmy67 is offline
 
swimmy67's Avatar
 
Join Date: Apr 2004
Location: Rockford, Illinois area.
Posts: 68
I have used these type of connectors. They work good for RS485 Modbus RTU.

https://www.amazon.com/C2G-Single-37...70_&dpSrc=srch
  Reply With Quote
Old March 8th, 2018, 04:15 PM   #5
BITS N BYTES
Lifetime Supporting Member
United States

BITS N BYTES is offline
 
Join Date: Jun 2005
Location: Miami Beach
Posts: 402
Quote:
Originally Posted by geniusintraining View Post
I use a lot of Winford products.... great quality, prices are better than anyone else in the market, great supply of different **** that we need and they normally ship the same day or the next

https://www.winford.com/products/brk8p8csj4b.php
+1 for Winford Engineering. Great resource, good quality and reasonably priced.
  Reply With Quote
Old March 8th, 2018, 06:31 PM   #6
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,833
I would have concerns about either module creating a standing wave which reflects energy back that creates false bits because I see either as more of a star topology where each RJ connector is the beginning of 'stub' exiting from a common point.



Yes, the connectors are physically separated by mm or inches of tracing, but daisy chaining puts devices in parallel. each of which is at some distance from each other, there is a clear end on each end, unlike a star that does not have two ends.

One of the 'rules' of RS-485 is to limit stub or star wiring.

It might be that reflections are not a problem at internal-to-the-panel distances. But it goes against conventional wisdom in 485 networking.
  Reply With Quote
Old March 8th, 2018, 07:01 PM   #7
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 305
+1 danw

What makes RS-485 more resistant to noise is to work by current, circulating an appreciable intensity through the cable, and this is only fulfilled with a daisy chain connection and the resistors at the ends.
__________________
Suppanel HMI
  Reply With Quote
Old March 8th, 2018, 09:20 PM   #8
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 282
I'm totally going to try the red lion product on DSI multidrop if I am ever forced to use it again. The Powerflex 523/525 rj45 connectors are utter garbage to try and terminate as a daisy chain.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Network panel with punch in connectors (RJ45) JOLTRON LIVE PLC Questions And Answers 8 September 11th, 2015 08:54 AM
cable RS485 siemen ngoclan LIVE PLC Questions And Answers 3 September 18th, 2014 01:54 PM
RJ45 to RS485 pinout Lilith LIVE PLC Questions And Answers 6 April 27th, 2011 10:30 AM
RS485 / RS422 Connection Bridge johnyu LIVE PLC Questions And Answers 4 March 12th, 2007 08:44 AM
Allen Bradley IMC S/234 Connectors ajax LIVE PLC Questions And Answers 4 November 13th, 2006 02:40 PM


All times are GMT -5. The time now is 01:31 AM.


.