You are not registered yet. Please click here to register!
plc storereviewsdownloads
This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc.
Try our online PLC Simulator- FREE.  Click here now to try it.
---------->>>>>Get FREE PLC Programming Tips
New Here? Please read this important info!!!
Go Back   PLCS.net - Interactive Q & A > PLCS.net - Interactive Q & A > LIVE PLC Questions And Answers
PLC training tools sale
Reply
Thread Tools Display Modes
Old March 8th, 2018, 09:49 AM   #1
AustralIan
Member
United Kingdom
AustralIan is offline
Multidrop RJ45 RS485 connectors
What do you guys use for connecting several Modbus RS485 devices with a single RJ45 port in the one panel? and terminating resistors?
Old March 8th, 2018, 12:04 PM   #2
kolyur
Lifetime Supporting Member + Moderator
United States
kolyur is offline
kolyur's Avatar
I've used these in the past:
http://www.redlion.net/accessory/rj4...llel-connector
If you download the datasheet they have a similar product that has a RJ45 breakout terminal block, looks like a nice way to add a terminating resistor.
__________________
John
Old March 8th, 2018, 12:32 PM   #3
geniusintraining
United States
geniusintraining is offline
geniusintraining's Avatar
I use a lot of Winford products.... great quality, prices are better than anyone else in the market, great supply of different **** that we need and they normally ship the same day or the next
https://www.winford.com/products/brk8p8csj4b.php
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
Old March 8th, 2018, 02:44 PM   #4
swimmy67
Member
United States
swimmy67 is offline
swimmy67's Avatar
I have used these type of connectors. They work good for RS485 Modbus RTU.
https://www.amazon.com/C2G-Single-37...70_&dpSrc=srch
Old March 8th, 2018, 03:15 PM   #5
BITS N BYTES
United States
BITS N BYTES is offline
+1 for Winford Engineering. Great resource, good quality and reasonably priced.
Old March 8th, 2018, 05:31 PM   #6
danw
Member
United States
danw is offline
danw's Avatar
I would have concerns about either module creating a standing wave which reflects energy back that creates false bits because I see either as more of a star topology where each RJ connector is the beginning of 'stub' exiting from a common point.
Yes, the connectors are physically separated by mm or inches of tracing, but daisy chaining puts devices in parallel. each of which is at some distance from each other, there is a clear end on each end, unlike a star that does not have two ends.
One of the 'rules' of RS-485 is to limit stub or star wiring.
It might be that reflections are not a problem at internal-to-the-panel distances. But it goes against conventional wisdom in 485 networking.
Old March 8th, 2018, 06:01 PM   #7
lfe
Member
France
lfe is offline
+1 danw
What makes RS-485 more resistant to noise is to work by current, circulating an appreciable intensity through the cable, and this is only fulfilled with a daisy chain connection and the resistors at the ends.
__________________
Suppanel HMI
Old March 8th, 2018, 08:20 PM   #8
Geoff White
Member
Australia
Geoff White is offline
I'm totally going to try the red lion product on DSI multidrop if I am ever forced to use it again. The Powerflex 523/525 rj45 connectors are utter garbage to try and terminate as a daisy chain.
Reply
Jump to Live PLC Question and Answer Forum
Bookmarks
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Similar Topics
Thread Thread Starter Forum Replies Last Post
Network panel with punch in connectors (RJ45) JOLTRON LIVE PLC Questions And Answers 8 September 11th, 2015 07:54 AM
cable RS485 siemen ngoclan LIVE PLC Questions And Answers 3 September 18th, 2014 12:54 PM
RJ45 to RS485 pinout Lilith LIVE PLC Questions And Answers 6 April 27th, 2011 09:30 AM
RS485 / RS422 Connection Bridge johnyu LIVE PLC Questions And Answers 4 March 12th, 2007 07:44 AM
Allen Bradley IMC S/234 Connectors ajax LIVE PLC Questions And Answers 4 November 13th, 2006 01:40 PM