Errors when setup DeviceNet network

Hi all,

I am in the first time setup the deviceNet network.
My system is redundant controllers use CompactLogix and deviceNet network.
Bus 1769: L32E controller, power PA2 and 1769-SND.
Flex IO: 1769-IB32, IB8, IE12, OB32P and MVI94-MCM.

I had configure offline for deviceNet network used Rsnetworx for deviceNet as:
- Scanner node address 00
- Flex IO node address 02

After configuration offline, I powered up deviceNet, switch scanner to idle mode and download the configuration for deviceNet.
The errors came up. Just scanner can be downloaded, other flex IO cards got errors as my attached pictures.

Anyone met this issues before and what wrong in my configuration? Pls help to advise me? We had to conduct FAT next week.

Thanks alot,
anhkhoi
Attached Images
File Type: jpg 1.jpg (47.6 KB, 43 views)
File Type: jpg 2.jpg (47.3 KB, 32 views)
File Type: jpg 3.jpg (63.2 KB, 28 views)
  Reply With Quote
Old June 27th, 2010, 01:53 AM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,112
1794-ADN adapters cannot accept a configuration change that modifies the I/O connection if an I/O connection is already established.

Object State Conflict errors are very common with this adapter during commissioning for this reason.

To fix this issue:

1. Remove the 1794-ADN from the scanlist, or disable the scanlist entry (uncheck the "Active" box), then cycle power to the DeviceNet and the 1794-ADN.

2. Download your 1794-ADN configuration.

3. Activate the I/O connections by creating them in the scanlist or checking the "Active" box.
  Reply With Quote
Old June 27th, 2010, 07:15 PM   #3
anhkhoi
Member
Viet Nam

anhkhoi is offline
 
Join Date: Aug 2009
Location: Ho Chi Minh
Posts: 26
Thanks alot, Ken.

All errors were now cleared and deviceNet is working now.
Regarding to the backup solution on deviceNet, I found (in Rockwell Automation Publication 1769-UM009D-EN-P documents) that 2 canners module 1769-SDN must be gotten firmware 3.x or later.
Firmware of 2 scanner 1769-SDN are 2.2. I tried use the ControlFlash utility to upgrade firmware (as some manual suggested) but this tool just use when firmware is 3.x or higher.

"TIP: You must use a DeviceNet network connection to update the 1769-SDN
scanner module firmware to revision 3.10 After the firmware is
updated to revision 3.10, subsequent updates to the 1769-SDN scanner
module firmware can be initiated via a controller backplane
connection."

Could you advise me how to update firmware for 1769-SDN from 2.2 to 3.x?

Thank in advance.
anhkhoi
  Reply With Quote
Old June 27th, 2010, 11:25 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,112
Most Logix-family modules can be upgraded by accessing them over the backplane or over the network port.

I am not very familiar with the 1769-SDN, but it sounds like v2.x can only be upgraded over the network port.

My guess is that "You must use a DeviceNet network connection" means you must connect to the DeviceNet using a 1770-KFD, 1784-PCD, or 1784-U2DN in order to access the module via the network port.

You might also be able to bridge from one module, onto the network, to the other module to perform the 2.x -> 3.x upgrade, or use a 1756-DNB and a ControlLogix to bridge onto the network to perform this upgrade via the DeviceNet port of 1769-SDN module.
  Reply With Quote
Old June 28th, 2010, 12:25 AM   #5
anhkhoi
Member
Viet Nam

anhkhoi is offline
 
Join Date: Aug 2009
Location: Ho Chi Minh
Posts: 26
Hi Ken,

Our local RA also never work with deviceNet before and do not know how to advise...
I will try to borrow some tools as your suggestion to update 1769-SDN firmware.

Thank you very much,
ankhoi
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
rockwell Devicenet Error 91 - VSD interference matt_sd LIVE PLC Questions And Answers 7 July 2nd, 2014 07:40 AM
DEVICENET, what am I missing rsdoran LIVE PLC Questions And Answers 10 October 14th, 2011 05:19 PM
SVX9000 Drives on Devicenet B Fix LIVE PLC Questions And Answers 2 June 25th, 2009 03:25 PM
RIO Network setup Help" jayala LIVE PLC Questions And Answers 7 August 3rd, 2008 09:55 AM
DeviceNet (Ken Roach) Thomas Franklin LIVE PLC Questions And Answers 6 February 14th, 2006 10:11 AM


All times are GMT -5. The time now is 04:42 AM.


.