dear,

i was looking at a document where it is showing one digital field device connected to a terminal strip and then using a jumper from field side, on the other side the two terminal strips are connected to two digital input signals.
is this acceptable? what are the drawbacks? is it better to use a splitter?

please see picture attached.

thanks!

charbel

dual input modules.jpg
 
To me, it is technically practical to do that. However you will need to check the sensor spec to make sure that it can supply the load of both inputs.

Practically, I don't know why you would bring the same sensor into 2 separate PLC inputs. What are you trying to gain?
 
dear,

on the field side, digital type switches would be connected (dry contacts) and the two digital input modules for same field device will be connected each to a PLC so that we will be having dual redundant PLC's.

thanks!

Charbel
 
one digital field device going to two remote i/O

please see attached, safe PLC and remote I/O's are being used from Siemens.

thanks for let me know if this connection from field device to remote I/O's is acceptable and will not cause any short from one I/O module to the other or any other problem.

thanks!

charbel

Redundant PLC.jpg
 

Similar Topics

Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
Replies
14
Views
431
I have a PLC type PM856 from ABB with some I/O modules and I get an error from the Digital Inputs model type DI801. The unit status shows error...
Replies
0
Views
261
I am monitoring two BMXDDO3202K digital outputs for their behaviour, they are each for opening and closing, and so the on time affects how far the...
Replies
1
Views
278
On the laser displacement sensor now connected to my PLC, the manual says 4mA=643 and 20mA=64,877. However, I checked with a Fluke, injecting...
Replies
5
Views
886
I'm new to S7/TIA. There's no devices connected to the PLC yet. I've got a laser measurement sensor (Micro-Epsilon optoNCDT 1220). From the...
Replies
18
Views
2,936
Back
Top Bottom