I'm trying to get a count from a pulse on an AB PLC onto the Panel View 550. can anyone give me heads up on what to expect/how to do this.

thanks
edwin
 
How about that... there aren't a lot of guys with our name !

Very likely your count exists in an Integer Register, with an address like "N7:10".

In the PanelBuilder32 software, you will find an object called a Numeric Display. You can define the object's location, the text size, the number of digits, as well a PLC address (like N7:10) from which the PanelView will request the value in the PLC.

Do you already have your pulse counter set up, or do you need help implementing a counter in the PLC too ?
 