Hi,



i need to communicate around 32 vfd's (mitsubishi E700 Series) with master plc(mitsubishi). All vfd's are at different location around 300 meter apart from each other and distance from control room of the nearest vfd is around 800 meter. What is the possible Architecture to communicate at this distance.
 
There are allot of other questions to ask. Redundancy?
The basic specifications for Mitsubishi are 100m without repeaters for Ethernet.
http://dl.mitsubishielectric.com/dl/fa/document/manual/plc/sh080446eng/sh080446engh.pdf

I would go Ethernet. It has a distance of 100m but if you are using optical fiber you can go 2000m. This is without repeaters on the lines.
See this on Ethernet Modbus TCP communication distances:
http://www.electrical-installation.org/enwiki/Communication_protocols_and_architectures_in_iPMCC

Repeaters / Converters
http://www.veracityglobal.com/products/ethernet-and-poe-devices/outreach-lite.aspx
https://www.perle.com/products/10-100-1000-ethernet-extender.shtml

The above should give you some information to consider.
Regards,
 

Similar Topics

Hello Experts, I have begun working on a new project and am specifying all the components. I am planning to use the AB compact logix platform and...
Replies
10
Views
5,080
Hi guys! I have been spending quite a bit of time yesterday and today trying to get a definitive answer to this question regarding protection an...
Replies
10
Views
3,785
Hey guys , I am involved in a equipment installation process wherein the customer wants me to run multiple motors with a single VFD. I...
Replies
3
Views
2,028
Good morning, A Yaskawa A1000 series VFD is controlling a chain at the ref. frequency 1 (let's say 70 Hz) as its default. In winter months, a...
Replies
2
Views
1,299
Is it OK to have multiple Frame size VFD's inside the same enclosure that will be dedicated to VFD's only or is there any code/regulations against...
Replies
4
Views
1,734
Back
Top Bottom