1756-BA2 in SLC 5/04?

jrsnydley

Member
Join Date
Dec 2014
Location
Minnesota
Posts
155
This may be a dumb question but can I use a 1756-BA2 in place of the 1747-BA for a SLC 5/04? The reason I ask is that we stock the 1756-BA2 in our spare parts.
 
No the connection is different from the BA2 to the BA, see the details of the ones we sell below... they are also cheap and small enough to stock the correct one

1747-BA
Type: Lithium
Voltage: 3.0
Capacity: 1200 mAh
Color: Black Heat Shrink
Size: 0.58" diameter x 1.04" long

1756-BA2
Type: Lithium
Voltage: 3.0
Capacity: 1200 mAh
Color: Black Heat Shrink
Size: 0.68" dia. x 1.38" tall

1756-BA1
Type: Lithium
Voltage: 3.0
Capacity: 1800 mAh
Color: Black Heat Shrink
Size: 0.68" dia. x 1.38" tall

The BA1 has the same connection but the size is not the same and will have a hard time fitting in the holder

bas.png
 
Last edited:
Yeah, I thought the connection was the same but I guess not. There can't be any sort of standardization, that would make things too simple.
 

Similar Topics

How has your experience been using non-Allen Bradley 1756-BA2 batteries? Would you use them in all instances, or limited applications? Any other...
Replies
16
Views
5,056
Good Afternoon , We have a ControlLogix 5561 controller. The maintenance group , powered down the machine and lost the program. The battery...
Replies
5
Views
5,086
Is there any difference between these batteries other than the connector style? We have a ControlLogix L61 processor with a dead 1756-BA2 battery...
Replies
3
Views
14,366
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
11
Views
260
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
Replies
6
Views
149
Back
Top Bottom