Kinetix 300

I have a Kinetix 300 drive that I want to use to disable a servo (without a break) when the safety circuit is broken. It's for a feeder ring that I would like to allow to be spun freely when a door is open... I can't intercept the "Drive enable" signal to the drive because then it faults, also I tried putting a relay before the Safe-Torque Off controls and that gave a major fault to the drive that I couldn't reset. I also don't have the ability to put a relay after the drive and before the motor..

Any suggestions or input would be appreciated.

https://literature.rockwellautomatio...m001_-en-p.pdf

Last edited by codedRed; February 12th, 2019 at 07:16 AM. Reason: link to manual
  Reply With Quote
Old February 12th, 2019, 07:55 AM   #2
collinsd70
Member
United Kingdom

collinsd70 is offline
 
Join Date: Feb 2014
Location: Swindon
Posts: 91
Quote:
Originally Posted by codedRed View Post
I have a Kinetix 300 drive that I want to use to disable a servo (without a break) when the safety circuit is broken. It's for a feeder ring that I would like to allow to be spun freely when a door is open... I can't intercept the "Drive enable" signal to the drive because then it faults, also I tried putting a relay before the Safe-Torque Off controls and that gave a major fault to the drive that I couldn't reset. I also don't have the ability to put a relay after the drive and before the motor..

Any suggestions or input would be appreciated.

https://literature.rockwellautomatio...m001_-en-p.pdf
It sounds to me like you need to rewire your Hardware Enable signal; this is normally the 24v release from you safety circuit, however without going into too much detail you WILL need some form of safey circuit to monitor this device if it is to be operated during the guard door being opened (something like a speed monitor), I dont know about US Legislation but a machine I worked on recently allowed a max safe speed of 100RPM.

Once you have your Hardware Enable/ STO and your 400V mains; you should be good to go.

From memory; when I commisioned a Kinetix 350 system- there was a lot of confusion surrounding the STO wiring in the manual.

You should be able to examine your drive status bit to see of your STO is truly working xx.DriveEnableStatus.


Regards

Daniel

Last edited by collinsd70; February 12th, 2019 at 07:58 AM.
  Reply With Quote
Old February 12th, 2019, 11:15 AM   #3
RonJohn
Lifetime Supporting Member
United States

RonJohn is offline
 
RonJohn's Avatar
 
Join Date: Jul 2013
Location: NE Ohio
Posts: 447
Is this servo drive hardwire controlled or Ethernet/IP through a PLC?
What fault do you get when you try to disable the Kinetex 300?

If I understand correctly, you want to stop the drive then disable it as straight up disabling causes a fault. There are safety relays which include time delay contacts. You may be able to tie in the immediate contacts to your stop input and the time delay contact to your enable/STO input to do what you want to do.

Last edited by RonJohn; February 12th, 2019 at 11:16 AM. Reason: clarification
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Allen Bradley Kinetix 300 open collector outputs lurby LIVE PLC Questions And Answers 5 September 12th, 2018 11:29 AM
Kinetix 300 Enable/disable by Motionview Onboard unsaint32 LIVE PLC Questions And Answers 4 December 18th, 2017 10:55 PM
How to use the GSV to get the torque of Kinetix 300 Xu MingJiu LIVE PLC Questions And Answers 7 August 14th, 2017 01:11 PM
Kinetix 300 drive enable signal unsaint32 LIVE PLC Questions And Answers 3 May 12th, 2014 07:57 PM
Kinetix 300 versus Ultra 3000 Switek LIVE PLC Questions And Answers 0 July 19th, 2011 05:28 AM


All times are GMT -5. The time now is 10:19 AM.


.