Old February 12th, 2019, 09:46 AM   #1
DamianInRochester
Lifetime Supporting Member
United States

DamianInRochester is offline
 
DamianInRochester's Avatar
 
Join Date: Jan 2011
Location: Rochester NY
Posts: 1,275
Mismatch of safety destination address (F_Dest_Add)

TIA v15.1
CPU 1512SP F-1 PN

Took a program that was working fine on one system and downloaded it into an identical system.

I've got a fault on the Safety Output module
6ES7136-6DB00-0CA0



Mismatch of safety destination address (F_Dest_Add)
I can't get it to clear and I'm having difficulty finding the root cause.

When swapping the module with another of the same, the issue follows the system and not the module.
  Reply With Quote
Old February 12th, 2019, 10:25 AM   #2
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,148
Quote:
Originally Posted by DamianInRochester View Post
TIA v15.1
CPU 1512SP F-1 PN

Took a program that was working fine on one system and downloaded it into an identical system.

I've got a fault on the Safety Output module
6ES7136-6DB00-0CA0

Mismatch of safety destination address (F_Dest_Add)
I can't get it to clear and I'm having difficulty finding the root cause.

When swapping the module with another of the same, the issue follows the system and not the module.



Every Profisafe device has a unique address that has to be downloaded directly to it. If you ever used the old ET200S IO, that was the dip switches on the side. Here, the address is downloaded directly to the safety card. There are a couple HOWEVERs, though:


1) the address is actually stored on a chip that snaps into the base unit (you'll see a couple pins coming out of the module key in the back)
2) for these devices, what ACTUALLY needs to be unique (across the whole network, not just the project) is the combination of the SOURCE address in the PLC and the DESTINATION address in the IO.


My guess is that you need to re-assign the F-destination address to the IO module.
  Reply With Quote
Old February 12th, 2019, 11:56 AM   #3
DamianInRochester
Lifetime Supporting Member
United States

DamianInRochester is offline
 
DamianInRochester's Avatar
 
Join Date: Jan 2011
Location: Rochester NY
Posts: 1,275
How can you download the correct address to the chip if download to device is grayed out? How do you actually get it to update the address in the chip that snaps into the base module?
  Reply With Quote
Old February 12th, 2019, 12:06 PM   #4
JRW
Member
United States

JRW is offline
 
JRW's Avatar
 
Join Date: Jun 2002
Location: Upstate South Cackalacky
Posts: 1,770
Go online
Right click the safety module
Then click assign f address
That should get you in the ballpark
  Reply With Quote
Old February 12th, 2019, 12:42 PM   #5
DamianInRochester
Lifetime Supporting Member
United States

DamianInRochester is offline
 
DamianInRochester's Avatar
 
Join Date: Jan 2011
Location: Rochester NY
Posts: 1,275
Thanks both of you.

Where I was getting hung up was where to do the right clicking. I kept right clicking on the device in the project tree instead of the module in the rack. That was the bit I was missing.

Everything is working fine now.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1756 enbt Prayder LIVE PLC Questions And Answers 35 May 11th, 2016 03:28 PM
Safety PLC for dummies Wilso LIVE PLC Questions And Answers 10 October 18th, 2013 07:48 PM
Powerflex ip address disappears unsaint32 LIVE PLC Questions And Answers 9 October 13th, 2013 07:50 PM
E-Stop Circuit Wiring jshiepe LIVE PLC Questions And Answers 35 July 26th, 2004 09:46 AM
Building an S7 Array Move Questions DesertDog LIVE PLC Questions And Answers 19 June 17th, 2004 09:51 AM


All times are GMT -5. The time now is 03:34 AM.


.