Hi, Experts please i wish to do batch totalizing

Hi, please i wish to do batch totalizing ( automatic flow control)
i wish to use Endress+Hauser flow transmitter with Allen Bradley 1400 to do this control for example, if i need 1000 gallon in my batch, i should give an instruction to the PLC once is 1000 the flow should switch off. i wish to do this using the pulse output of the flow transmitter.

please i will appreciate if someone can help me with sample project for this to elaborate me more
thanks.

Last edited by nyameephraim; February 12th, 2019 at 02:45 AM.
  Reply With Quote
Old February 12th, 2019, 05:07 AM   #2
chud
Member
South Africa

chud is offline
 
chud's Avatar
 
Join Date: Oct 2007
Location: KALAHARI
Posts: 906
What plc are you using if any?
  Reply With Quote
Old February 12th, 2019, 05:13 AM   #3
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
Hi, Thanks for the reply

Allen Bradley 1400 PLC
  Reply With Quote
Old February 12th, 2019, 06:47 AM   #4
crawler009
Member
Switzerland

crawler009 is offline
 
crawler009's Avatar
 
Join Date: Feb 2012
Location: Planet Earth
Posts: 209
what do you have right now? Do you at least have rslogix and try'd something by your own?
You cannot expect that someone will have a complete program for you, which you can load into your plc and it will work.
I see that you asked this question several times
http://www.plctalk.net/qanda/showthread.php?t=119315
http://www.plctalk.net/qanda/showthread.php?t=119296
and also on a Rockwell forum.
On plctalk in the download section, there are a lot of examples for Rslogix 500. Check them and see if you can learn
something. Reading help files is also a good source of knowledge, also goolge is your friend.
And if you have specific questions, then i'm sure that someone is willing to help you. But not to do the job for you.

Last edited by crawler009; February 12th, 2019 at 07:06 AM.
  Reply With Quote
Old February 12th, 2019, 07:05 AM   #5
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
OK thanks
  Reply With Quote
Old February 12th, 2019, 09:39 AM   #6
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
but its always easier to understand with example. (what am actually asking is an example) that is what i mean by ( sample project)

Last edited by nyameephraim; February 12th, 2019 at 09:44 AM.
  Reply With Quote
Old February 12th, 2019, 10:17 AM   #7
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,377
First, how fast are your pulses? Do you require a high speed input, or can a standard input be used. This will be a factor in how you write the logic. Will it always be 1000 or will the volume change? Is it okay to overshoot the target, how accurate must it be? How long does it take your control valve to close? Do you need to have a "pre-act" to shut off early. Are you controlling a pump too?
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams

  Reply With Quote
Old February 12th, 2019, 10:53 AM   #8
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
Hello thanks for your contribution.
am using Endress + Hauser flow transmitter, ( yes i require high speed input).
Will it always be 1000 or will the volume change? ( the volume will change more or less than)
it okay to overshoot the target (yes)

i wont use control valve. i will use only pump.

Last edited by nyameephraim; February 12th, 2019 at 11:00 AM.
  Reply With Quote
Old February 12th, 2019, 11:06 AM   #9
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,868
You'll need some device to input the preset volume setpoint for the batch - BCD multi digit switch? HMI?

Presumably you want some indication when the batch is 'stopped', 'filling', 'done'. LED's? panel lights? HMI?

Many flowmeters have frequency output where the pulse frequency varies with flow rate, say, 0-50 GPM = 0-2,000Hz. This is usually a monitored with a 'high speed' digital input on a PLC. This is what I'd use for batching.

Sometimes the flowmeters have a pulse output (relay or solid state) that trips every time a given volume has flowed, say, every 10 gallons a discrete output changes state or cycles. This is usually monitored with a standard discrete input on a PLC.

Some comments on batch control in general:
The assumption is that a flow meter is always full of liquid (no air, not partially full) in order to report the correct flow rate. Vertical down flow is no-no with liquids. Vertical upflow is preferred. If horizontal, put the meter body at a low point so entrained air does not accumulate in the meter body at a high spot in the line.

If your batch control drains the flowmeter, it will take some period of time for the meter to re-initialize when the flow starts.

When the controller turns the valve off, a quick closing valve can damage piping or even a flow meter with water hammer shock. It pays to not slam the valve shut. At a given pressure, its operation will be repeatable, meaning you might have to shut it off at 989 gallons and the remaining 11 gallons flow during the valve shutdown and with whatever drainage there is.

Many batch controls shut down the large valve at, say 95% of setpoint and use a smaller pipe and valve to finish the filling (dribble mode). That might require either a second flow meter or just timing remainding flow.
  Reply With Quote
Old February 12th, 2019, 11:27 AM   #10
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
Hello thanks for you contribution i appreciate.
please i need the ladder logic example of this control system, it gives me better understanding.

You'll need some device to input the preset volume setpoint for the batch? (yes)

Presumably you want some indication when the batch is 'stopped', 'filling', 'done'. HMI (yes)

Last edited by nyameephraim; February 12th, 2019 at 11:32 AM.
  Reply With Quote
Old February 12th, 2019, 11:32 AM   #11
chud
Member
South Africa

chud is offline
 
chud's Avatar
 
Join Date: Oct 2007
Location: KALAHARI
Posts: 906
Quote:
Originally Posted by danw View Post
You'll need some device to input the preset volume setpoint for the batch - BCD multi digit switch? HMI?

Presumably you want some indication when the batch is 'stopped', 'filling', 'done'. LED's? panel lights? HMI?

Many flowmeters have frequency output where the pulse frequency varies with flow rate, say, 0-50 GPM = 0-2,000Hz. This is usually a monitored with a 'high speed' digital input on a PLC. This is what I'd use for batching.

Sometimes the flowmeters have a pulse output (relay or solid state) that trips every time a given volume has flowed, say, every 10 gallons a discrete output changes state or cycles. This is usually monitored with a standard discrete input on a PLC.

Some comments on batch control in general:
The assumption is that a flow meter is always full of liquid (no air, not partially full) in order to report the correct flow rate. Vertical down flow is no-no with liquids. Vertical upflow is preferred. If horizontal, put the meter body at a low point so entrained air does not accumulate in the meter body at a high spot in the line.

If your batch control drains the flowmeter, it will take some period of time for the meter to re-initialize when the flow starts.

When the controller turns the valve off, a quick closing valve can damage piping or even a flow meter with water hammer shock. It pays to not slam the valve shut. At a given pressure, its operation will be repeatable, meaning you might have to shut it off at 989 gallons and the remaining 11 gallons flow during the valve shutdown and with whatever drainage there is.

Many batch controls shut down the large valve at, say 95% of setpoint and use a smaller pipe and valve to finish the filling (dribble mode). That might require either a second flow meter or just timing remainding flow.
You will struggle to get a more comprehensive reply to this.
People are not going to do the work for you
You will have a setpoint entered as said above via a hmi or scada or some other device.
Then once the batch has started you count the pulses from your flow switch to see if the setpoint has been reached.....
If it has you will close the feed valve..
  Reply With Quote
Old February 12th, 2019, 11:42 AM   #12
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
Hello thanks for your reply, Given an example of something i believe is a way of putting somebody on track not doing his work.

note, i have not asked any body to do the work for me.
(i have also given several examples to people in the field of control)
  Reply With Quote
Old February 12th, 2019, 12:22 PM   #13
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,331
Have you given any thought to using a dedicated Batch Controller? There are many on the market in just about every price range. You could use your PLC to communicate via Modbus to the controller and get data and even start a batch. Of course that will depend on the features of the controller.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old February 12th, 2019, 12:32 PM   #14
nyameephraim
Member
United Arab Emirates

nyameephraim is offline
 
Join Date: Apr 2016
Location: dubai
Posts: 26
Hello thanks for the contribution.

As i have stated above that is what i wish to do.

i need some domesticated example,
also i need demonstrated example for (HSC) high speed counters
  Reply With Quote
Old February 12th, 2019, 02:11 PM   #15
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 474
Here ya go, first result on google. Also a ton of videos on youtube.

https://www.google.com/url?sa=t&sour...Elme1CFzujs46T
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSview SE and Visual Basic SCAN.PLC LIVE PLC Questions And Answers 9 May 29th, 2015 03:20 PM
Application assistance needed, autoprinting batch reports a285323 LIVE PLC Questions And Answers 2 February 23rd, 2014 06:50 PM
Learning Curve for RS BizWare Batch sanger LIVE PLC Questions And Answers 1 November 2nd, 2013 05:48 AM
Possibillities new project, MP277 317-2PN/DP Combo LIVE PLC Questions And Answers 19 July 28th, 2008 03:40 AM
chemical batch control-idec FA3S-CP12 chris clayton LIVE PLC Questions And Answers 1 November 11th, 2002 07:22 AM


All times are GMT -5. The time now is 10:43 AM.


.