PowerFlex 525 Parameter Definition
Pete_S
Mar 2015
Portland Maine
76
Hi All,
I have a PowerFlex 525 drive with Ethernet I/P capability. Device in theory had known static IP on it, 10.10.114.22. I didn't see it in Linx or with an ARP-A, and I cant use BOOT-P, so I connected via USB to upload current configuration. I pasted contents of my .pf5 file below, but IP seems to be defined, 10.10.114.22. I found manual for the drive and attempted to find parameter definition table so I could verify parameter definition, and device manual says that I need the manual for the communication module to get the parameter table. I didn't see any model number on the module that disconnects from the "drive" other than 25B which lead me to this manual that stated I needed communication module manual.
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/520-um001_-en-e.pdf
it seems like the communication module is not modular, and I didnt see another model number on it, but clearly I am missing something.
Any advice would be greatly appreciated!
~~~~~~~~~~~~.pf5 contents~~~~~~~~~~
<?xml version="1.0" encoding="utf-8"?>
<Node>
<Drive Brand="1" Family="9" Config="130" MajorRev="4" MinorRev="1">
<Parameters>
<Parameter Instance="128">1</Parameter>
<Parameter Instance="129">10</Parameter>
<Parameter Instance="130">10</Parameter>
<Parameter Instance="131">114</Parameter>
<Parameter Instance="132">22</Parameter>
<Parameter Instance="133">255</Parameter>
<Parameter Instance="134">255</Parameter>
</Parameters>
<CustomGroups>
<CustomGroup Instance="1">
<Name>Custom Group</Name>
</CustomGroup>
</CustomGroups>
</Drive>
</Node>
I did see that, and I was looking at the network section which directs user to the manual for particular module, hence my initial comment that I was looking for a different manual. šŸ™ƒ
520com-um001 PowerFlex 525 Embedded EtherNet/IP Adapter
In the pdf version of the User Manual, there is a direct link to this manual on the first page of Appendix H, the Appendix entitled; "Ethernet I/P"
So I have pushed the following configuration to the device:
<Node>
<Parameters>
<Parameter Instance="134">0</Parameter>
<Parameter Instance="135">0</Parameter>
<Parameter Instance="136">0</Parameter>
</Parameters>
<CustomGroups>
</CustomGroup>
</CustomGroups>
</Drive>
</Node>
According to the manual this should use IP of 10.10.114.22 with a subnet mask of 255.0.0.0. I power cycled the device after download of configuration file as the manual instructs. I am still not able to ping the device with this IP address.
hello i am trying to set the max frequency for the drive via rslogix 5000, but do not see that patameter in the rslogix 5000 drive paramerts? the...
274
Hello there. I'm using PowerFlex 525, 0.5 HP, 230V, firmware 5.1 and RS Logix 5000 v.20 software. Is there a way to set in Logix 5000 a...
2,893
143: when changing this parameter the default value is to fault out when it happens but there are other options. They are stop, zero data, hold...
2,817
I am controlling a Powerflex 525 drive with a Micrologix 1100 through explicit messaging. Just the basic start, stop, and speed control. Reading...
2,381
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
53
