S7 200 and S7 300 PLC Communicate on MPI Network

faisal rasool

Member
Join Date
Oct 2015
Location
pakistan
Posts
60
Hi Everyone,
I want to know how we write the data to s7 200 plc from S7 300 plc on MPI Network
Cpu 315-2dp
Cpu 224XP
i use SFC 67 and SFC 68 for Write and read data.But my Question is that how we can do output high of s7 200 when i use S7 300 plc Programme.thanks
 
S7-200 is only capable of working as a slave (DP-Station) for the S7-300, for this purpose you need to add an EM 277 module to the S7-200,

You also need to integrate the EM 277 GSD file into Simatic manager, then the two CPU's can exchange data between them.

Hagos
 
Hi Mike,
Thanks For reply.I have already been checked this information.In this example thinking is explain about s7 200 setting.How we set MPI Address of S7 200 plc and what instruction use in MicroWin Software.If you have any information please share it.thanks
 

Similar Topics

Dear Experts, One of my client using S7-300 Plc In that Cp343 Module also using for scada and hmi connection ...
Replies
10
Views
6,744
Dear All As I mentioned in the subject I want to know what is required on the PCS 7 both hardware and software aspects also for S7 300/S7 1200...
Replies
0
Views
2,905
We want to data collect from plcs and making archive.3 pieces S7-300 (Only exist mpi port)and 1 piece S7-1200 (exist ethernet port).We are looking...
Replies
4
Views
2,068
PLC supplied from power and ET 200 supplied from difficult. Do you anything that danger for system?
Replies
3
Views
2,295
Hi all, my client has an existing 300 system with 3 by 316/314 PLC's connected on an MPI system with "global data" shared between each. They have...
Replies
8
Views
5,647
Back
Top Bottom