Hello friends. I have a PLC in the field that intermittently faults out. Its a compact logix L24ER-BB1B. The status "OK" light blinks red, according to the customer. He toggled the switch from program mode to remote, to reset the fault, and the machine resumed operation. According to the customer, this has happened 2 or 3 times in a month.

Help!

Does toggling the switch erase the controller fault list in the properties window?

Has anybody ever dealt with something like this?

If there was a negative number in a counter or timer, (which I don't think happened) Toggling the reset wouldn't fix the problem, and it would fault out again instantly?


Regards,

JF
 
Does this site have a lot of brown-outs, supply transients or do they have a habit of cycling power to fix things often?
 
The Micrologix and SL line will do that with a math overflow fault just going to program and back to run will reset it until the next time.
I don't know if the Logix processors still have that problem
 
I had a couple that did that do to programming error. The SCP instruction I was using had indirect addresses and I was causing a divide by 0 error When I accessed the routine they were located in.
 
The ControlLogix/CompactLogix OS considers overflow and divide by zero to be minor faults, which will not stop the user program.

An out-of-bounds array index will definitely fault the controller, and that's the sort of thing that's very typically reset during an initialization routine.

I agree that OP needs to go online and look at the fault logs. I admit I don't remember if they are cleared by a keyswitch cycle or power cycle.
 

Similar Topics

Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
242
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
242
Does anybody have a reccomendation for a camera with at least 200 frames per seconds recording speed for tracking an intermittent fault? Might be...
Replies
8
Views
3,463
System has been in place for 4+ years with no problem...There are 2 (nearly identical machines) that each have 6 Powerflex VFDs (5)( PF700 & 1...
Replies
5
Views
2,914
Hi, Anyone using a Redlion to communicate to a Beckhoff PLC? CX9020 or similar. Set up comms and all was working for about a month then comms...
Replies
1
Views
2,211
Back
Top Bottom