Hi everybody,
I am working on a project where the G306 HMI is set-up as a Modbus Master where it is collecting data from 7 analog panel meters via RS485 network. I would like to get this data into a Micrologix 1100.

I am using the ethernet port on the Micrologix to communicate with other remote devices and collect data from other meters. Will I be able to setup the ethernet protocol on the redlions panel to send the data to micrologix via ethernet even though I have it communicating with other remote meters.

Any suggestions on what would be the best way to get this data from redlions G306 into the Micrologix?

Any advice is greatly appreciated.

Thanks,

Brij
 
Last edited:
You shouldn't have any trouble with this, just get an Ethernet switch to connect all the devices if you don't have one already.

Use the Allen-Bradley EIP driver in Crimson and your G3-ML1100 communications should work without a hitch.

-John
 
Dave's example is basically the same as the example I mentioned in my PM. The only difference is his example pulls data from the ML and writes it to the MOdbus device. To send data the other way you wouls place the block under the ML. You can do it with a block under the Modbus device, but with a change in direction, however I think it is easier to place the block under the device that the data is going TO. (I find this a bit easier to visualize)

Regards,
 
This is great stuff guys. I really appreciate all the answers. I should be trying it very soon. I will let you guys know how it goes.

Thanks for your time, this has been really helpful!

Brij
 
Alright, I setup the block under the Micrologix and I am able to move the data from the analog meters to micrologix. It works like a charm. Thank you so much guys.

However, I have some Allen Bradley Energy meters that are connected on the same ethernet network as the Redlions. The Energy meters accept modbus RTU addressing. I am wondering if you can read data from these meters via Modbus TCP/IP protocol via Ethernet?

I tried doing this by selecting Modbus TC/IP Master as one the ethernet protocols and I set the IP address of the device in the target device. I am not sure about the TCP port and unit number, so I left it as default. I left all the protocol options at default like the Ping holding register, ICMP ping, etc.

I am trying to read from the Analog Input Registers of the meters. The data in the meter is a 2 word array (30419-20), how do I handle this or setup to read both words and reassemble into valid a floating point value.

Can you do this with the Redlions G306 and If so can you please tell me if I am doing anything wrong or how I should be setting this protocol and how do i setup the data tag to read the data.

Thanks again for all your help.

Brij
 
Brij,

FYI, this is the same text from the PM I just sent.

I do not see why you would not be able to do this.

I would suspect that your AB unit would use TCP Port 502 (this is the 'standard' Modbus TCP port), and I would also suspect that the unit number would be 1.

I have a feeling that your problem is related to the 'Ping Holding Register'. Does 400001 exist in the device, IE will it repsond to a read? You can set this to zero and it will disable the ping.

As far as reading 2 contiguous registers as a floating point number, you will want to create a Real tag. Then map it to 300419 and choose Word as Real for the Data Type. Depending on the format of the number in the AB, you may need to use the Swap Words Transform of the tag to get it to read correctly.

Regards,
 

Similar Topics

Having trouble communicatng via the USB port to the CF card, the datastation is logging OK to the CF card but am having trouble mounting and...
Replies
0
Views
1,546
Happy New Year everyone, I am working on a Prototype project using a AutomationDirect Click Ethernet PLC and a Red Lion G306 HMI. I have the HMI...
Replies
3
Views
1,650
So i have this application where I have to read/write from/to the serial port. Write has worked fine so far, but it is reading that I have issues...
Replies
3
Views
1,856
Hello Everyone, I have been playing with the Automation Direct Productivity 2000 PLC for the past couple days. I have a program in the PLC now...
Replies
1
Views
1,848
Hi, I have a Redlion G306 and its GSM Modem add on which I have successfully managed to send and receive texts from. I'm interested to know...
Replies
0
Views
2,161
Back
Top Bottom