Old November 23rd, 2022, 10:45 PM   #151
MaxK
Member
Czech_Republic

MaxK is offline
 
Join Date: Jul 2022
Location: FrozenHell
Posts: 46
#116 #125
Are you sure that is what destination unknown is using?

Guess we should ask Destination Unknown about it


Quote:
Originally Posted by Peter Nachtwey View Post
Use software/modeling. My estimated positions are better than the feed back positions on a sample to sample basis.

https://www.youtube.com/watch?v=7Gmrc-dj_uc&t=14s
Could you please point out the differences between the system shown in the block-diagram (below) and the system in your video?
Attached Images
File Type: png observerBD.png (10.1 KB, 67 views)
  Reply With Quote
Old November 24th, 2022, 01:34 AM   #152
Peter Nachtwey
Member
United States

Peter Nachtwey is online now
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: The land of the woke and the home of the broke
Posts: 8,030
Quote:
Originally Posted by MaxK View Post
#116 #125
Are you sure that is what destination unknown is using?

Guess we should ask Destination Unknown about it

Could you please point out the differences between the system shown in the block-diagram (below) and the system in your video?
Excellent! That looks good. I saved your picture because it looks good.
You have made a big leap forward.

The system you and I are modeling is a linearized model of a hydraulic cylinder with a load. This video shows how well the algorithms work even though the system is designed poorly. The system in the video was purposely designed to be impossible to tune well using just a normal PID. The damping factor is about 0.15 and the natural frequency is about 6.5 Hz. This means our old RMC100 and Rockwell's HYD02 and M02AS are not capable of controlling this system.
https://deltamotion.com/peter/Videos/NF-FOA.mp4

Notice that K2 is the second derivative gain. Most people don't like using the first derivative gain because it is noisy. However, none of this is possible without a good model derived by a good "auto tuning" program, the observer, and the extra K2 and Kj.

Now you seem to understand, each system is different. There is no one size fits all. A PID alone is often not the best solution.

You need to look at more of my Peter Ponders PID videos.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old November 24th, 2022, 08:15 AM   #153
MaxK
Member
Czech_Republic

MaxK is offline
 
Join Date: Jul 2022
Location: FrozenHell
Posts: 46
Quote:
Originally Posted by Peter Nachtwey View Post
Excellent! That looks good.
If my block-diagram is correct then there is some problem.
I attached MathCAD calculations for block-diagram with coefficients from video and get another-shape curves
Attached Files
File Type: zip Observer1.zip (9.7 KB, 2 views)
  Reply With Quote
Old November 25th, 2022, 08:52 AM   #154
destination unknown
Member
Ireland

destination unknown is offline
 
Join Date: Jun 2010
Location: Ireland
Posts: 94
Quote:
Originally Posted by Peter Nachtwey View Post
@destination unknown. Without a better explanation you graphs are meaningless.
With Process Variable Tracking Enabled there is jump in CV initially whereas with Process Variable Tracking Disabled the CV starts at zero initially.


Note:
In essence this is "Bump" transfer versus "Bumpless" transfer as in these plots itís a change of setpoint and then a transition to Auto-Mode.
With Process Variable Tracking enabled the PID matches the SP to the PV internally which keeps the error at zero, and when you change to Auto the PID acts as if it was a normal SP change.
Whereas with Process Variable Tracking disabled the PID puts the product of -Kp*E into the I-term to keep the CV at zero initially i.e. bumpless transfer



PVT_NoPVT.png


PID controllers work with Dimensionless P Gain, which is actually (% of CV)/(% of PV).
So gains have to be recalculated when the scaling is changed to get the same response.

Code:
Example with a PV scale of 0-100:

 Kp = 1.5,  SP = 75,  PV = 15 so the Error = 60% of the range as 100*60/(100-0)=60%

P-Term -> 1.5*60=90
Code:
Example with a PV scale of 0-400:

Kp = 1.5,  SP = 75,  PV = 15 so the Error = 15% of the range as 100*60/(400-0)=15%

P-Term -> 1.5*15=22.5
0-100_v_0-400.png


Code:
Example with a PV scale of 0-400 and rescaled Kp 1.5->6:

Kp = 6,  SP = 75,  PV = 15 so the Error = 15% of the range as 100*60/(400-0)=15%

P-Term -> 6*15=90
0_400 GainsRescaled.PNG



Quote:
Originally Posted by Peter Nachtwey View Post
The dependent and independent responses should be the same. I am assuming the small difference is rounding errors.
This is the case.
__________________
same same, but different...

Github: https://github.com/Destination2Unknown
YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ
  Reply With Quote
Old November 25th, 2022, 08:54 AM   #155
destination unknown
Member
Ireland

destination unknown is offline
 
Join Date: Jun 2010
Location: Ireland
Posts: 94
Quote:
Originally Posted by MaxK View Post
#116 #125
Are you sure that is what destination unknown is using?

Guess we should ask Destination Unknown about it
What's the question?
__________________
same same, but different...

Github: https://github.com/Destination2Unknown
YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ
  Reply With Quote
Old November 25th, 2022, 01:23 PM   #156
Peter Nachtwey
Member
United States

Peter Nachtwey is online now
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: The land of the woke and the home of the broke
Posts: 8,030
Quote:
Originally Posted by MaxK View Post
If my block-diagram is correct then there is some problem.
I attached MathCAD calculations for block-diagram with coefficients from video and get another-shape curves
The first equation for CO(s) doesn't look right and you skipped too many steps to follow.


Also, I don't usually combine the whole transfer function into one big function because the control output is limited in reality and Laplace transforms ignore this reality.
Learn to make proper trajectories.





My book about this is at work and I am now at home. It is turkey time ( thanks giving ) in the US.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old November 25th, 2022, 01:41 PM   #157
Peter Nachtwey
Member
United States

Peter Nachtwey is online now
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: The land of the woke and the home of the broke
Posts: 8,030
Quote:
Originally Posted by destination unknown View Post
With Process Variable Tracking Enabled there is jump in CV initially whereas with Process Variable Tracking Disabled the CV starts at zero initially.
Is process tracking your term for feed forwards?

Note:
In essence this is "Bump" transfer versus "Bumpless" transfer as in these plots it’s a change of setpoint and then a transition to Auto-Mode.
[/quote]
The old bump vs bumpless argument. Bumpless transfer doesn't apply to temperature systems. Temperature systems don't "bump". Motion systems do.

We still don't know what you are using as the open loop transfer function.

Quote:
With Process Variable Tracking enabled the PID matches the SP to the PV internally which keeps the error at zero, and when you change to Auto the PID acts as if it was a normal SP change.
Whereas with Process Variable Tracking disabled the PID puts the product of -Kp*E into the I-term to keep the CV at zero initially i.e. bumpless transfer
This is all necessary because you don't have a proper target generator. In motion control the target starts from where the actual is otherwise there will be a bump. That is not good when moving a 50 ton coil of steel.

Quote:
PID controllers work with Dimensionless P Gain, which is actually (% of CV)/(% of PV).
The P gain is not dimensionless. (% of PV) is wrong. What is the of %PV. What it should be (SP-PV). So if controlling a temperature system the P gain is (%CV/temperature_error)
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old November 25th, 2022, 02:28 PM   #158
destination unknown
Member
Ireland

destination unknown is offline
 
Join Date: Jun 2010
Location: Ireland
Posts: 94
Quote:
Originally Posted by Peter Nachtwey View Post
Is process tracking your term for feed forwards?

Note:
In essence this is "Bump" transfer versus "Bumpless" transfer as in these plots itís a change of setpoint and then a transition to Auto-Mode.

The old bump vs bumpless argument. Bumpless transfer doesn't apply to temperature systems. Temperature systems don't "bump". Motion systems do.

We still don't know what you are using as the open loop transfer function.

This is all necessary because you don't have a proper target generator. In motion control the target starts from where the actual is otherwise there will be a bump. That is not good when moving a 50 ton coil of steel.


The P gain is not dimensionless. (% of PV) is wrong. What is the of %PV. What it should be (SP-PV). So if controlling a temperature system the P gain is (%CV/temperature_error)
Process Variable Tracking is just where the SP is set to match the PV when in Manual Mode.

I should have said some PID controllers have a dimensionless P gain.
Logix for example: http://www.plctalk.net/qanda/showthread.php?t=63400


And some tuning methods calculate the gain in %/EU as apposed %/%:
https://controlguru.com/controller-g...rcial-systems/
__________________
same same, but different...

Github: https://github.com/Destination2Unknown
YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ
  Reply With Quote
Old November 25th, 2022, 10:55 PM   #159
Peter Nachtwey
Member
United States

Peter Nachtwey is online now
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: The land of the woke and the home of the broke
Posts: 8,030
Quote:
Originally Posted by destination unknown View Post
Process Variable Tracking is just where the SP is set to match the PV when in Manual Mode.
So there is a name for doing the obvious. Good. No one told me what you call this. I was just told years ago that this is what you should do. Someone came up with a name.

Quote:
I should have said some PID controllers have a dimensionless P gain.
Logix for example: http://www.plctalk.net/qanda/showthread.php?t=63400
This is such a joke and a flaw in the RoKcwell PID system. This is one reason why so many people have problems setting up their Rockwell PIDs. When is the error a percent? A percent if what?

Our gains, Delta Motion RMCs, have units.

Yes, the controlguru is trying to explain that the true gain depends on the scaling of error in SP_count-PV_counts on the input and counts/% control output. In the end is is as I said. Error units/% control output. It looks like the gains have units of counts_in to counts_out but the counts in and counts out don't represent the same thing and they must be scaled. All that just confuses people.

The open loop gain on a temperature system should have units of degree/control output%. The closed loop gain should be the inverse.

For instance, if the open loop gain is 2 degree/% then I know I can output 100% to increase the temperature to 200 degrees above ambient and 100%. I can scale for any temperature in between.

So if the open loop gain has units of degree/%CV then how can the close loop gain, K have gain anything other than %/degree?

The only answer is all the mickey mouse stuff that Rockwell put you through scaling inputs and outputs.

Most Rockwell customers are totally clueless because they are not calculating gains. They just use trial and error.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old November 28th, 2022, 12:03 AM   #160
MaxK
Member
Czech_Republic

MaxK is offline
 
Join Date: Jul 2022
Location: FrozenHell
Posts: 46
Quote:
Originally Posted by Peter Nachtwey View Post
The first equation for CO(s) doesn't look right and you skipped too many steps to follow.


Also, I don't usually combine the whole transfer function into one big function because the control output is limited in reality and Laplace transforms ignore this reality.
Learn to make proper trajectories.





My book about this is at work and I am now at home. It is turkey time ( thanks giving ) in the US.
It is seems like Simulink must to Learn to make proper trajectories too
Attached Images
File Type: png simulink_obs.png (66.0 KB, 37 views)
  Reply With Quote
Old November 28th, 2022, 01:08 AM   #161
Peter Nachtwey
Member
United States

Peter Nachtwey is online now
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: The land of the woke and the home of the broke
Posts: 8,030
Do I need to do if for you?
It takes using the Dirac function of you want to keep EVERYTHING in the s-domain.

Eventually you will need to graduate to state space or better yet, differential equations. Serious control people use differential equations because then they can start simulating non-linear systems.

All this is easy for me since I have over 30 years of files and work to refer to.

Take the time to figure out how to make good usable ramps. You will have them for the rest of your life.


Making a good target generator for motion control is FAR MORE difficult than doing system identification and computing the controller gains.


Here is a complete 3rd order motion profile.
https://deltamotion.com/peter/wxMaxima/Seg1234567.html
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon

Last edited by Peter Nachtwey; November 28th, 2022 at 01:40 AM.
  Reply With Quote
Old November 28th, 2022, 09:54 AM   #162
destination unknown
Member
Ireland

destination unknown is offline
 
Join Date: Jun 2010
Location: Ireland
Posts: 94
Quote:
Originally Posted by Peter Nachtwey View Post
So there is a name for doing the obvious. Good. No one told me what you call this. I was just told years ago that this is what you should do. Someone came up with a name.

This is such a joke and a flaw in the RoKcwell PID system. This is one reason why so many people have problems setting up their Rockwell PIDs. When is the error a percent? A percent if what?

Our gains, Delta Motion RMCs, have units.

Yes, the controlguru is trying to explain that the true gain depends on the scaling of error in SP_count-PV_counts on the input and counts/% control output. In the end is is as I said. Error units/% control output. It looks like the gains have units of counts_in to counts_out but the counts in and counts out don't represent the same thing and they must be scaled. All that just confuses people.

The open loop gain on a temperature system should have units of degree/control output%. The closed loop gain should be the inverse.

For instance, if the open loop gain is 2 degree/% then I know I can output 100% to increase the temperature to 200 degrees above ambient and 100%. I can scale for any temperature in between.

So if the open loop gain has units of degree/%CV then how can the close loop gain, K have gain anything other than %/degree?

The only answer is all the mickey mouse stuff that Rockwell put you through scaling inputs and outputs.

Most Rockwell customers are totally clueless because they are not calculating gains. They just use trial and error.

Logix PID -> 0-100:

0-100.png

Logix PID -> 0-400:

0-400.png


Logix PIDE:

PIDE.png


This is the Siemens Approach:

S.jpg
__________________
same same, but different...

Github: https://github.com/Destination2Unknown
YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ
  Reply With Quote
Old November 29th, 2022, 10:57 AM   #163
destination unknown
Member
Ireland

destination unknown is offline
 
Join Date: Jun 2010
Location: Ireland
Posts: 94
Siemens 0-100
Siemens 0-100.PNG


Siemens 0-400
Siemens 0-400.PNG
__________________
same same, but different...

Github: https://github.com/Destination2Unknown
YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Slow Acting Long Time Interval PID Tuning GrizzlyC LIVE PLC Questions And Answers 141 March 30th, 2021 07:04 AM
PID tuning methods OysterMan LIVE PLC Questions And Answers 4 March 21st, 2021 11:59 AM
Micrologix 1400 Timed Proportioned Output PID Tuning Paul Begley LIVE PLC Questions And Answers 3 January 13th, 2014 05:26 PM
PID Tuning and Process Modeling kdcui LIVE PLC Questions And Answers 14 October 15th, 2009 02:27 PM
PLC PID Auto Tuning Problem monet LIVE PLC Questions And Answers 6 May 26th, 2009 10:50 AM


All times are GMT -4. The time now is 02:23 AM.


.