Old November 24th, 2021, 03:20 AM   #1
DigiWaste
Member
Norway

DigiWaste is offline
 
Join Date: Apr 2021
Location: City of Bergen
Posts: 5
S7-1500 communication with SCADA system

I'm working with a client who are in the process of installing a smart waste solution in a new building. This solution will be using s7-1500 PLC and ET200SP as remote I/O units. The communication between PLC and I/O units will be using modbus master/slave (CM PtP, RS485). This system needs to communicate with a top system (central operation) based on Schneider teknology running with modbus. My question: what is the best way to setup this communication between ths PLC and the top system?
  Reply With Quote
Old November 24th, 2021, 04:17 AM   #2
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 15,044
It is a new system in a new building ?
The choice of Modbus RTU puzzles me.
Even if there is an existing SCADA that uses Modbus RTU, then it should be evaluated if a more recent fieldbus standard would be a better choice.

Quote:
This solution will be using s7-1500 PLC and ET200SP as remote I/O units. The communication between PLC and I/O units will be using modbus master/slave (CM PtP, RS485).
So the S7-1500 PLC will communicate as master with the ET200SP as slaves via Modbus RTU (??). That is a weird decision if any. The natural choice would be Profinet for an all-Siemens system. If it must be a serial RS485 protocol (like Modbus RTU), then Profibus would be the natural choice.
It is as far as I know not possible to setup ET200SP as Modbus RTU slaves. There is an Interface Module for Modbus TCP though.
You can install an CM PtP which will can communicate via Modbus RTU. But it will be the Profinet controller (i.e. the S7-1500 CPU) that communicates, not the ET200SP station.

I think you are mixing things up. You probably mean that you need an Modbus RTU connection to the Schneider SCADA system, and you intend to use a Modbus RTU module (CM PtP) in the Siemens PLC to achieve that.
If that is the case it is certainly possible, but it would be an arcaic and cumbersome design; definitely not the 'best way'.
If the Schneider SCADA do not have a Siemens S7 driver, then at the very least it should be possible to be an OPC DA or OPC UA Client.
So the 'best way' in my opinion is to get an OPC DA or OPC UA Server (can be Siemens Simatic Net, or it can be a 3rd party vendor) to provide the OPC Connection to the Schneider SCADA as OCP Client.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old November 24th, 2021, 07:20 AM   #3
hagos
Member
Sudan

hagos is offline
 
Join Date: Oct 2004
Location: Africa
Posts: 229
+1

Agree with what Jesper said.
  Reply With Quote
Old November 24th, 2021, 11:45 AM   #4
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,772
Also agree with everything Jesper said.



Quote:
Originally Posted by JesperMP View Post
It is as far as I know not possible to setup ET200SP as Modbus RTU slaves. There is an Interface Module for Modbus TCP though.
You can install an CM PtP which will can communicate via Modbus RTU. But it will be the Profinet controller (i.e. the S7-1500 CPU) that communicates, not the ET200SP station.
Possibly it's an et200sp PLC, in an RTU kind of setup? ALSO possible it's just unfounded optimisim, someone selecting parts without knowing how the system actually works.



Quote:
Originally Posted by JesperMP View Post
So the 'best way' in my opinion is to get an OPC DA or OPC UA Server (can be Siemens Simatic Net, or it can be a 3rd party vendor) to provide the OPC Connection to the Schneider SCADA as OCP Client.
Another option would be to use the built in OPC UA server on the 1500s, although I think something like Simatic Net becomes more cost efficient with many PLCs.
  Reply With Quote
Old November 24th, 2021, 12:11 PM   #5
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 15,044
Quote:
Originally Posted by mk42 View Post
Another option would be to use the built in OPC UA server on the 1500s, although I think something like Simatic Net becomes more cost efficient with many PLCs.
Also one must consider that on the lower-end S7-1500 PLCs, incl. 1511SP and 1512SP, the integrated OPC UA Server is really lame.
__________________
Jesper
See my profile interests for Q&A
  Reply With Quote
Old November 24th, 2021, 05:50 PM   #6
the_msp
Lifetime Supporting Member
United Kingdom

the_msp is offline
 
the_msp's Avatar
 
Join Date: May 2008
Location: Northern Ireland
Posts: 1,018
Quote:
Originally Posted by JesperMP View Post
Also one must consider that on the lower-end S7-1500 PLCs, incl. 1511SP and 1512SP, the integrated OPC UA Server is really lame.
What's the lowest model 1500 you'd recommend with an integrated OPC UA Server?
__________________
Regards,

Patrick G. B.Eng MIET

Making the flashy lights flash since the 90's

SCADA - Inductive Automation Gold Integrator | PLC | Control Panels | Robotics | Training

Connect with Matrix Engineering
  Reply With Quote
Old November 25th, 2021, 04:53 AM   #7
DigiWaste
Member
Norway

DigiWaste is offline
 
Join Date: Apr 2021
Location: City of Bergen
Posts: 5
Yes it is a new system in a new building.
And as you correctly mentioning, I'm mixing things up here. As you put it, we need an Modbus RTU connection to the Schneider SCADA system, and my client intend to use a Modbus RTU module (CM PtP) in the Siemens PLC to achieve that.

You probably understand I'm a pretty new in this field, but I also waswondering about the choice of my client, and I will discuss this further with him. As I understand the PLC1500 have OPC UA Server included (licens), in which can serve an OPC UA client on the Schneider side.
Thanks a lot JespepMP for your quick replay.

By the way, this is a greate place for novices like myself
  Reply With Quote
Old November 25th, 2021, 05:12 AM   #8
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 15,044
Quote:
Originally Posted by the_msp View Post
What's the lowest model 1500 you'd recommend with an integrated OPC UA Server?
This may give you a hint of what is possible:
https://support.industry.siemens.com...view/109755846
And you can play around with this:
https://perfdata.public.siemens.com/...ion=34&lang=en
My estimate is that what is possible via an S7 connection on an 1511 CPU will need a 1517 CPU to achieve the same via OPC UA.
edit: If the data volume is very low, OPC UA will be OK even on a small CPU. So it depends on what is required in the actual case.
edit: Even on a high-end CPU, it seems that you will reach transfer times of approx 250 ms unless the data volume is very low. I use down to 100 ms for data that is used to visualize movements, and I want a smooth animation on the screen. This is not a problem for an S7 connection, even on smaller CPUs.

Quote:
Originally Posted by DigiWaste
we need an Modbus RTU connection to the Schneider SCADA system, and my client intend to use a Modbus RTU module (CM PtP) in the Siemens PLC to achieve that.
Who says that you 'need' that ?
If the Schneider SCADA is not completely outdated, then it should support some other protocols than Modbus RTU.
Today, Modbus RTU is very rarely used, mostly as the last option when nothing else is possible. I.e. to connect a modern PLC to a legacy device.
Modbus RTU is never used as the main data connection between a SCADA and a PLC.
It is like sending an important document by fax.
I would challenge the clients decision, and ask if either OPC DA or OPC UA are possible. What exactly is the Schneider SCADA ? Name, and version ?

edit: Do not be confused by the above discussion about the OPC UA server integrated into the S7 CPU.
The OPC UA server can be installed on a PC, either the SCADA PC or another PC, and then there will not be any performance issues.
__________________
Jesper
See my profile interests for Q&A

Last edited by JesperMP; November 25th, 2021 at 05:52 AM.
  Reply With Quote
Old November 25th, 2021, 05:57 AM   #9
DigiWaste
Member
Norway

DigiWaste is offline
 
Join Date: Apr 2021
Location: City of Bergen
Posts: 5
Thanks again JesperMP.

I have a meeting with my client next week and come back to you on "What exactly is the Schneider SCADA ? Name, and version ?" and other stuff.
  Reply With Quote
Old November 25th, 2021, 02:58 PM   #10
Lare
Member
Finland

Lare is offline
 
Join Date: Jan 2006
Location: Finland
Posts: 1,727
Even that it would be modbus comms from scada there is no need to use that for ET200SP Remote IO from 1500CPU.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Problem with communication Siemsns S7 - HMI bm1209 LIVE PLC Questions And Answers 6 April 9th, 2015 04:09 PM
s7 1500 cant connect to wincc scada Blue Fox LIVE PLC Questions And Answers 1 October 3rd, 2013 08:32 AM
S7 - What is in the System Data Block? Jack Schit LIVE PLC Questions And Answers 3 May 16th, 2012 10:27 AM
s7 1200 to scada rQx LIVE PLC Questions And Answers 9 October 26th, 2011 01:07 PM
Ethernet communication S7 S300 / S7 400 obi wan LIVE PLC Questions And Answers 2 May 20th, 2010 08:26 AM


All times are GMT -4. The time now is 07:19 PM.


.