Siemens AG_RECV Buffer Issue

Rusty_K

Member
Join Date
Mar 2004
Location
Norway
Posts
73
Hey Guys!

I've run into a rather annoying little problem with the Siemens AG_RECV block (using a CP343-1) when trying to read data back from an RFID Reader.

It seems as though the NDR bit stays low until the entire buffer is full. At this point my received data will be in variable lengths so I cant really lock down my buffer size. Also, for some reason, if I try and set my buffer size to anything less than 130 Bytes if get a 80B1H error code meaning "Destination" area invalid.

Does anyone happend to have a work-around for this silly silly issue?

Ya just got to love those crazy cats at Siemens...

Cheers!

R.K.
 
Hi R.K.

I've run into similar problems also. I think this might help:

Link to Siemens forum

We solved the problems by always sending a same length message, from a server in this case.

Maitomies
 

Similar Topics

Can you please help me to choice the “best” solution for communication between CPU:s. I have following kind of system: I already have created S7...
Replies
6
Views
8,107
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
22
Views
235
Hi everyone, I am an omron plc tec , lately I came across a siemens s7 200 cn plc . Can someone help me regarding the software required and...
Replies
26
Views
465
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
117
Hi, I have PLC S7-1200 and switch XC-208 and Iam trying to implement this SNMP library: SIOS I am not sure, what I am doing wrong, but there is...
Replies
3
Views
122
Back
Top Bottom