Interact PS10 HMI SLC5 Driver 8H Error Request Timeout [2]

JLDrescher

Member
Join Date
Jul 2009
Location
Georgia
Posts
13
Not Sure What I Have Missed Or Need To Check Next,
SLC5 Driver Request Timming Out On Node-2 [HMI]


Listed Below Are The Findings/Results: 07.16.2009

PLC Processor AB SLC5/03
Interact Power Station PS10 HMI

SLC5 Driver Error Codes [Offline/Online/Program/Run Modes]
Interact Shell Was Set@ Com-1/Now Com-2, Interupt&Irq Default

Recheck CH-1 Cat To CTC Com-2 9-Pin D-Shell Cable. /Ohm'd-OK
[No CTC Driver Code 10 Generated/Cable Is Open:]

Note: Previous Comm Cabling For PLC CH-1 Works w/
AB 1747-PIC [DH485] To Laptop Com-1
Currently Using PLC CH-0 9-Pin D-Shell RS232/DF1
For Laptop Comm/Working

LISTED DRIVER ERROR's [Interact]
1st Time:
00:10:41 Driver 4H Write Overflow [2]
[FIXED, Buffer From 10-20]
00:08:13 Driver 8H Request Timeout [2]
00:07:09 Driver 5H Node Inactive [1]
[PLC Processor CH-1 DH485 To CTC PS10]
00:06:42 Driver 5H Node Inactive [0]
[PC To PLC Processor [Working Communications]]

2nd Time:
Driver 8H Request Timeout [2] [CTC Station ID=2 / Node-2]
Driver 5H Node Inactive [1]
[PLC Processor CH-1 DH485 To CTC PS10]
Driver 5H Node Inactive [0]
[PC To PLC Processor [Working Communications]]

RSLOGIX-500 S:9&10 Not Set [0's] [Interact HMI Comm Active]
PLC Processor DH485 LED Status=Blinking Green

CTC Station ID=2 [Node-2] Max Nodes=2
COM-2 RS485 [Jumpers Verified] 9600 Baud
SLC5/03 CH-1 DH485 9600 Baud, Node-1
[CH-1 Works w/1747-PIC Converter To Laptop]

CTC AM [Application Mgr/Supervisor
SLC5 Driver Listed
SLC5 Driver File's Info:
SLC5.DLL 49KB Application 10/29/1997 3:05 PM
SLC5.EXP 78KB EXP FILE 4/23/1999 1:08 PM
SLC5.FIL 1KB FIL FILE 2/17/1996 11:29 AM
SLC5.TXT 4KB Text Doc 4/23/1999 1:07 PM

CTC Tag Editor Addressing Description Formats: SLC5\2$B3:0,0

Thank's
 
When I used CTC HMIs with SLC-5/03 and SLC-5/04, I used the ABDH driver with the following settings:
COM Port
-Port Number: COM2
-Baud Rate: 19200 (although I did go up to 38400)
-Parity: NONE
-Data Bits: 8
-Stop Bits: 1
Protocol
-Acquisition Rate: Constant
-Data Highway Timeout: 2
-ASCII Terminator Character: 0
-Maximum ASCII Length: 82
PLC Stations
-PLC Type: SLC-5
-Startup: Active
Watchdog
-Watchdog Reference: "blank"
Write Buffering
-Write Mode: No Wait
-Write Buffer Size: 128

As for the SLC-5/03:
Chan. 0 - System
-Driver: DHF1 Full Duplex
-Baud: 19200
-Parity: None
-Stop Bits: 1
-Source ID: 9
-Control Line: No Handshaking
-Error Detection: BCC
-Embedded Responses: Enabled
-Duplicate Packet Detect: checked
-ACK Timeout: 50
-NAK Retries: 3
-ENQ Retries: 3

I did use the CTC SLC5 driver once with a SLC-5/02. The baud rate was set to 19200, the SLC address was 1, and the CTC address was 2.

Your tag addressing looks fine.

I do not know if any of this is useful to you.
 
Thank's,
I'am Going To Assume On CTC Com-2 Was Jumpered To RS232 and Not RS485
or RS422 ?
Will Do Interact Tag Editor To ABDH And Try Again,
Thank's For Your Time/Research Mike, We Let You Know.
 
Thank's Mike,
Everything Went Excellent, Up And Communicating,
Going Back/Trying RS485 Again, If All Goes Well, Will
Post All Info Back Here For Other's.
Once Again Thank You Very Much, Just What The Doc Order!.
 

Similar Topics

I am taking over a CTC Interact project. All I have to start with is the LRP file. I do not know what version it was written in. It was done...
Replies
0
Views
1,765
Greetings! (First timer here) I've got a machine (b&r ipc 2001), and in its CompactFlash theres DOS and Interact (Version 5.2) My contractor...
Replies
0
Views
1,142
Hello Mr PLC Experts, I am working with a Parker CTC application on XP in VMWare. I am trying to modify and existing project and now it is not...
Replies
1
Views
1,842
Has anyone had any experience with this? I know how to setup users and user levels in the software and such but cannot seem to find where to...
Replies
0
Views
1,364
I am working on a conversion project, upgrading some old CTCs to Panelview 1000s, and have run into several buttons with addresses I don't know...
Replies
0
Views
1,321
Back
Top Bottom