Micrologix 1500 Modbus Chan 1 not able to connect

vin7102

Lifetime Supporting Member
Join Date
Feb 2012
Location
Ohio
Posts
30
Hi Folks,


I have a Micrologix 1500 Series C rev 9 with a 1761-net-AIC connected to a weight transmitter. Communicating via Modbus RTU as Master.


Everything is working perfectly when connected to Channel 0 (I can use either PM02 or AM00 and both work fine). For hookup and HMI reasons, I need to get the Modbus connected to Channel 1, and I simply cannot figure out why it will not connect.


On the Logix500 side for CH1, I have the baud rate set matching the device (19200), The Driver set for Modbus RTU Master, No Handshaking, and I have only one simple MSG instruction running (on a 2 second timer) and it has the proper controller (Channel 1 Integral) and slave node address(2) set on both ends.
When trying to connect to the Micrologix, I've tried both a PM02 and a serial cable. I get one bleep on the TX of the AIC and thats it.


Anyone see anything missing?
 
Sure, Here are a couple pics.


As far as node address on both ends, set on the weight module params as well as in the MSG setting.

RL-1.PNG RL-2.PNG
 
Can you show us the whole rung with the timer used for the message instruction? And the whole rung of the message instruction?

It looks like you are getting data.
 
Mickey, the data in the screenshot was from when I was connected via chan 0...



*** UPDATE*** I hooked up the AIC to CH1 with a NULL cable and everything started working... Tough lesson learned on my end( Cant use a standard 232 for this).



I figured the PM02 would work from the round 8 pin on the AIC to CH0... Not the case! WTH



Hope this thread helps someone else out there!


Thanks Mickey.
 

Similar Topics

Does anyone have an example program using control techniques EN drives?RSLogix 500 ver 6.3, to be put in the upload section on here. I’m wanting...
Replies
2
Views
1,353
Hi, Need to communicate Allen Bradley Micrologix 1764 LRP with my Laptop to read data (coil & holding registers) via modbus rtu protocol using...
Replies
5
Views
5,401
Can anyone give me an easy explanation on how to use modbus/rtu with 1761-net-aic module, for micrologix 1500. If it isn't very easy then maybe...
Replies
7
Views
3,307
Does the Micrologix 1500 can communicate with the device with MODBUS RTU? The device is a temperature transmitter. The processor is Ser. C Rev. D...
Replies
0
Views
2,658
Hi, I am trying to connect a micrologix 1500 (1764-LRP) to a Hitachi SJ700-2 inverter. To connect them i am using ch1 in the PLC (RS-232), a...
Replies
1
Views
2,993
Back
Top Bottom