Best way to upgrade a SCADA system

Right.. imagine the scenario.. an old PC running a SCADA system connected to seven S5 PLC's. The system needs upgrading but you have no documentation and no software to open the SCADA project (again, an old SCADA system thats been in for years).

How do you go about upgrading the system to a shiny new Mitsi SCADA front end and S7 PLC's in place of the S5's.

I can upgrade the S5 PLC's without any problems but I have no idea how you can upgrade the SCADA system. I'm very new to SCADA and imagine it works just like an HMI in that you set up an interface area and various 'tags' and then address those tags in the software.

How do I work out what 'tags' are being used when I can't get at the SCADA stuff that's on the system.

Basically what I'm saying, is that most, if not all the people on these forums are far more experienced than me.. so I was wondering how you would go about this.

What I was originally thinking was that if I could upgrade the SCADA system first (and get it to talk to the S5's) and then I could upgrade each PLC in turn.

If I upgrade the PLC's first then the existing SCADA system won't be able to communicate with them.

However, if I upgrade the SCADA system first then how do I go about ascertaining which 'tag' does what..? Or even what info I've got coming back?

Sorry if its a badly worded question and I'll happily expand on it if needed.

Thanks for your advice..

JT
__________________
I'm beta testing life...
  Reply With Quote
Old May 2nd, 2005, 01:29 PM   #2
krk
Lifetime Supporting Member
England

krk is offline
 
Join Date: Aug 2004
Location: Kent
Posts: 795
Johnny,

Just curious...what is the old SCADA system?

Kevin H

EDIT:
Don't worry...just saw your other post....
__________________
www.krkautomation.com

Last edited by krk; May 2nd, 2005 at 01:33 PM.
  Reply With Quote
Old May 2nd, 2005, 01:34 PM   #3
Johnny T
Member
United Kingdom

Johnny T is offline
 
Johnny T's Avatar
 
Join Date: Jul 2003
Location: Fife, Scotland
Posts: 642
krk

Its an old OCME proprietary system called Albatross. I mentioned it in another thread. The system is no longer supported by OCME as they have a new system out but the customer doesn't want a system that isn't futureproof. I think they would rather have a Siemens or Mitsi installed. Hence the change.

Plus, all their engineers are up to speed on S7 but there's only one or two of them that can do anything with S5.

__________________
I'm beta testing life...
  Reply With Quote
Old May 2nd, 2005, 04:18 PM   #4
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,325
Quote:
However, if I upgrade the SCADA system first then how do I go about ascertaining which 'tag' does what..? Or even what info I've got coming back?
I think you're going to have to do it the old fashioned way. Call up each screen on the old system and analize it, what does it display, what does it control, make a lot of notes. Depending on how well the PLC code is documented, that may help also.
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams

  Reply With Quote
Old May 2nd, 2005, 04:32 PM   #5
Johnny T
Member
United Kingdom

Johnny T is offline
 
Johnny T's Avatar
 
Join Date: Jul 2003
Location: Fife, Scotland
Posts: 642
Ken

I was fearing that!.. thought there might be something like a 'tag' file somewhere that systems use to store the info or something like that...

As you say.. I'm going to have to develop the new system in parallel with the old until I get all the tags sorted etc.

Sheesh.. boil the coffee, its gonna be a long night!!

__________________
I'm beta testing life...
  Reply With Quote
Old May 2nd, 2005, 05:39 PM   #6
DaveW
Member
United States

DaveW is offline
 
Join Date: Apr 2005
Location: SoCal
Posts: 351
I agree with Ken. Maybe you can set up a new SCADA that runs concurrent with the old SCADA. You can add/test/verify until you are confortable with new system, then cut the old SCADA's umbilical cord.
  Reply With Quote
Old May 2nd, 2005, 06:05 PM   #7
Johnny T
Member
United Kingdom

Johnny T is offline
 
Johnny T's Avatar
 
Join Date: Jul 2003
Location: Fife, Scotland
Posts: 642
Dave

Yep, will have to do this it seems. Oh well... at least it means I can develop the new system without the pressure of a timeframe.

Thanks for all your help..

JT
__________________
I'm beta testing life...
  Reply With Quote
Old May 3rd, 2005, 02:23 AM   #8
Unregistered
Guest
 
Posts: n/a
At the time S5 was used with SCADA systems, the data going to and comming from the scada where nearly allways routed trough communication DB's. If you can find these, you will know exactly what data is exchanged between the two, then you only have to find out where the data is used in the SCADA system.
  Reply With Quote
Old May 3rd, 2005, 02:38 AM   #9
Johnny T
Member
United Kingdom

Johnny T is offline
 
Johnny T's Avatar
 
Join Date: Jul 2003
Location: Fife, Scotland
Posts: 642
Thanks for the response.

When you say "communications DB's", do you mean via FB51 or some other Siemens FB?

If so, any idea what to be looking for?

I know that FB51 does comms to an OP, would it be the same comms FB for communicating to a SCADA system?

Cheers

JT
__________________
I'm beta testing life...
  Reply With Quote
Old May 3rd, 2005, 03:26 AM   #10
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,071
From the old OCME system you will need at least the following:

The tag list. Each tag must have an address in the S5. You will have to follow each tag (!) to find out what it does exactly. You can then replicate the same tag in the new system.

User settings (buttons, switches, setpoints) in screens in the OCME system must be identified. You will have to replicate these in the new system.

The functionality of the alarm system. Each SCADA has its own peculiar way of doing alarms. You will have to understand how the OCME alarms gets triggered and how alarms are acknowledged.

The alarm list. Each alarm has an alarm text that must be replicated in the new system.

Is there anything "advanced" in the OCME system ?
(Scripts, batches, recipes, datalogging, other ...)
You may not have to do the same thing again in the same way. But you should at least identify the existence of such things, and make a note if it has to be solved again, maybe in another way.

When you have finished the conversion of the OCME system to the new system of your choice, you can then start thinking about how you can convert the S5 system to S7.

OR .... how about ditching the old S5 AND the OCME SCADA system at the same time ? If you dont, then you are just postponing what must be done it the not so distant future anyway.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old May 3rd, 2005, 03:38 AM   #11
Johnny T
Member
United Kingdom

Johnny T is offline
 
Johnny T's Avatar
 
Join Date: Jul 2003
Location: Fife, Scotland
Posts: 642
Jesper

Thanks for your post mate.

The whole system is going to get ditched eventually but as its a production critical system I can't do it all in one go. I'm going to do it in stages, starting with the SCADA.

Once that's done, I'm going to do a PLC every weekend, or maybe two, (when the plant is shut down) until I've upgraded them all.
Thanks for the info on alarms etc. I'll look into that.

Cheers

JT
__________________
I'm beta testing life...
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Manual/Auto jthornton LIVE PLC Questions And Answers 9 October 5th, 2006 12:40 PM
OCME Albatross system Upgrade to Siemens Johnny T LIVE PLC Questions And Answers 0 April 30th, 2005 08:56 AM
SCADA system with RS232 to a MPI connection in S7-300 Andoni LIVE PLC Questions And Answers 2 January 15th, 2005 05:27 AM
SCADA System Security... Eric Nelson LIVE PLC Questions And Answers 2 April 26th, 2003 09:03 AM
Big SCADA system jimtech67 LIVE PLC Questions And Answers 6 November 25th, 2002 04:58 AM


All times are GMT -5. The time now is 02:38 PM.


.