sparky64

Member
Join Date
May 2003
Location
Newcastle upon Tyne
Posts
127
I want to collect some data from an S7 - 400 using RSView32, I'm using KEPware.KEPServerEnterprise.V4, on my office PC, and have set Kepware up, so i can see the information i want when i launch OPC Quick client, because i can see the values i want in Kepware this means that the kepware is communicating with the PLC ok.

I've tried to configure a node in rsview, using the following settings:

DATA SOURCE - OPC SERVER

NAME - SIEMENS

SERVER NAME - KEPware.KEPServerEnterprise.V4

TYPE - LOCAL

ACCESS PATH - ?????????????? I don't know what this should be, i've entered the channel name and device name - Channel1.IgnitorLine

This is all accepted ok, but when i create a tag and monitor the tag, the state is ERROR.

Appologies if i haven't supplied enough info.

Any help appreciated thanks

Sparky
 
I managed to work out that you do not need to state a path, and then it allows you to use the opc browser to assign addresses.

If anyone wants any help doing this, let me know.



Cheers
Sparky :D
 

Similar Topics

Hello fellow wirenuts, I am looking to find the P.B. touch indicator option on version 13.00 and failing. It has been a year or so since I last...
Replies
9
Views
283
Hello, I have converted RSView 32 to FTView SE 14 (I have tested FTView 12 before as well and there were some difficulties so I moved on to...
Replies
4
Views
245
Okay, something I have not seen before.. RSView SE. I am working on an existing project. There is a value the customer wants trended and it is...
Replies
4
Views
801
I have a request to integrate a pause button in RSlogix to be able to start/stop a video. Video format is not defined at the moment, so it could...
Replies
2
Views
791
Hello everyone, I am having a problem with conversion from RSView32 to FT View SE Local project on version 12.00 (CPR 9 SR 12). Firstly, I have...
Replies
6
Views
1,403
Back
Top Bottom