Old May 20th, 2010, 03:49 AM   #1
Iner
Member
France

Iner is offline
 
Join Date: Mar 2010
Location: France
Posts: 100
WinCC Flexible and refreshing the values of variables

Hi,

I would like to know if there is a way to refresh the variables of only the current screen instead of refreshing all the variables ? The connection I use is a 9600/s and it can't take the more than one thousand variable I have.

I have seen there is a event associed with the buttons allowing to refresh a selected variable. But it would mean I would give a very long time of refresh to all other variables, and I would need to associate the variables of all a screen by one button, the button who will make the screen come. But after it would not refresh.... Is there a way to press a button automatically?

I don't like this solution so if an option allowed just to refresh the current screen, I would like to know it and it would help me a lot. Thanks in advance.
  Reply With Quote
Old May 20th, 2010, 03:52 AM   #2
Jeebs
Member
Belgium

Jeebs is offline
 
Join Date: Feb 2007
Location: Leuven
Posts: 1,010
In WinCC Flex > Tags > Select tags in groups of 500 or less > General options > Acquisition Mode > Change to: Cyclic on use.

Now they'll be updating cyclicly only when they are used in the current active picture.
  Reply With Quote
Old May 20th, 2010, 04:16 AM   #3
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,241
The normal is that the tags are to update "Cyclic on use", which means they will update only if they are displayed on a screen.
Some tags must be updated "cyclic continously", such as alarm tags.

Which PLC is this ?
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old May 20th, 2010, 04:27 AM   #4
Iner
Member
France

Iner is offline
 
Join Date: Mar 2010
Location: France
Posts: 100
Thanks for the answers.

Apparently yes, it was the option by default of the majority of the tags when made appear the option.

It is a TSX premium 57. I am using the Unitelway connection and I made a cable to connect the MP377 and the PLC.

My problem is that the connection works perfectly when I try to extchanges 15-20 tags.

But when I put all my application, I see in the alarm window that the connection is enabled, then interrupted, then enabled, then interrupted, and a part of the tags on the screen are refreshed, then disappear replaced by somes errors signs, then there are other tags who are refreshed etc... etc... And even on screens where there is nog a lot of tags.
  Reply With Quote
Old May 20th, 2010, 04:39 AM   #5
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,241
How about switching to Modbus TCP ? Both the TSX and the MP377 can do that.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 04:39 PM.


.