Hi Everyone,
I have a Keller pressure transmitter (Non Calibratable) having output 4-20mA. When there is zero pressure in line then its output is 3.96mA, Analog channel is configured as 4-20mA channel. So when there is a zero pressure in line, it gives zero count.
I am running a system when pressure is below the certain limit to built a pressure in line. So if there there is a case of failure of tx, the system will run continuously and may damage the line.
Is there any method to detect failure of transmitter through PLC. Or Is there any problem if i configured particular channel to 0-20mA and rest are configured as 4-20mA.
I have a Keller pressure transmitter (Non Calibratable) having output 4-20mA. When there is zero pressure in line then its output is 3.96mA, Analog channel is configured as 4-20mA channel. So when there is a zero pressure in line, it gives zero count.
I am running a system when pressure is below the certain limit to built a pressure in line. So if there there is a case of failure of tx, the system will run continuously and may damage the line.
Is there any method to detect failure of transmitter through PLC. Or Is there any problem if i configured particular channel to 0-20mA and rest are configured as 4-20mA.