Hi Friends,
Two Question here please:

1. Is it possible for someone to assign his own chosen IP address to a Panel View Plus6 1000?

2. At simulation stage, I intended using Tag address say N7:10 in Factory Talk studio ME instead of Tag Name (say start). but I can't see it via connection Tab. How can I Tag with Tag address like N7:10 at simulation stage not via PLC Node?
Thanks in advance for help
 
Hello,

1. Yes it is possible to assign unique IP address to a PVP6 1000. It is done under Network Settings as far as I remember. When you shut down your application you should get to panel setting window where you can navigate to Network Settings.

2.What version of FT View you are using?
 
Hello,

1. Yes it is possible to assign unique IP address to a PVP6 1000. It is done under Network Settings as far as I remember. When you shut down your application you should get to panel setting window where you can navigate to Network Settings.

2.What version of FT View you are using?
Version 9.00, so any IP address can work? No default IP address?
 
PanelView Plus terminals, like virtually all computers, are configured for DHCP network address assignment by default.

To configure a static IP address, you use the Configuration mode menus, in the Network Settings category.

There is no static default IP address.

For your second question, I think you are describing Offline Tag Browsing, in which an RSLinx Enterprise Shortcut is associated with a *.ACD file for a ControlLogix family controller.

This feature is not available with *.RSS files for SLC/MicroLogix controllers. You must manually type in the data table address.
 

Similar Topics

I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
173
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
Replies
8
Views
355
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
Replies
0
Views
77
Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
275
I copied a panel in factory talk HMI for an identical system. The label names are still the same as the original panel but I am trying to change...
Replies
1
Views
126
Back
Top Bottom