1762-OF4 AB Analog output

GACrichmond

Member
Join Date
Feb 2010
Location
Richmond
Posts
3
The Allen Bradley Analog Output module 1762-OF4 with a ML1200 processor, when using old version of RSLogix 500 (5.5) no window comes up to configure the module to 4-20mA from 0-20mA, use to be able to do it through bits, the module is listed as "other-product id 66" in the configuration window, vendor recommends upgrading software, but we are going to buy RSLogix 5000 for another project, is the MicroLogix 1200 programmable with 5000? Our old 500 is version 5.5. Any suggestions??:D
 
Last edited:
1762-of4

Well, updated the RSLogix 500 and got the config. window, but the module will only allow either -10 to +10V or 4-20 but when you enter in 0 in Engineering units, it should give a 4mA signal, but gives 0 so it seems to work as a 0-20mA not 4-20, in order to get 4mA need to enter around 6500 (0-32767)I am confused...
 

Similar Topics

Hello, I'm new to analog signals as far as scaling them and what the useable output voltage will be. I need to utilize the 0-10vdc output. I...
Replies
6
Views
5,446
Hey guys I 'm having problems getting a valve to move that has a DVC6200 actuator connected to it via a MicroLogix 1762-OF4 PLC card. I can move...
Replies
18
Views
5,400
Hi, I have a 1762-OF4 A/O Module connected to my ML 1400. The module is configured through RSLogix 500 and wired properly per the UM. The problem...
Replies
17
Views
4,068
Hello, i have a 1762-of4 connected to a ml1100. i setup an scp instruction with n7:0 min 0 max 32760 scaled min 0 scaled max 10 output...
Replies
4
Views
2,124
I have and OF4 configured for 4-20mA. How can I test the current output from a 1762-OF4 on the lab bench. i.e. the OF4 does not have a load...
Replies
15
Views
4,611
Back
Top Bottom