Old July 3rd, 2008, 07:37 AM   #1
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
Question PanelView Plus ---> SLC L551 Ethernet Communication Issues

Hello fellow techies,

I am using a BSN modules to switch RIO on a redundant SLC500 project (I didn't spec the hardware). The design has one pair of the Ethernet wires going through the 232/485 A and B terminals on the BSN so that the primary PLC would have connectivity to the Ethernet HMIs. For the most part, this works. However, during a failover, I am experiencing communication loss for approximately 7 minutes and 30 seconds. I started to isolate the network, and I am down to the switch, one PLC and the PV Plus. I have disconnected the ME Station, the Secondary PLC and my laptop



Network Configuration

Linksys Switch SRW2008 (10.12.1.1).

PanelView Plus 1000 (10.12.1.13).

Two SLC 500ís 1747-L551 Ethernet. They both have the same IP address, only one is connected to the network at any given time (10.12.1.10).

Dell workstation running RSView ME Station (10.12.1.2).

Programming Laptop is configured as 10.12.1.250

PanelView, Station and PLCs have 10.12.1.1 configured as gateway, and 255.255.255.0 for mask.



Testing

With the PanelView Plus communicating to PLC #1, I can unplug either the PV or the PLC, reconnect, and communication is restored in seconds.



With the PanelView Plus communicating to PLC #1, I can unplug either the PV or the PLC, reconnect to a different port, and communication is restored in seconds.



With the PanelView Plus communicating to PLC #1, I manually unplug PLC #1 and plug in PLC #2 (same IP and program as #1). Communication is dropped and I have 7 minutes and 30 seconds before communication is reestablished.



Everytime I test this, it is around 7 minutes and 30 seconds (+/- 15 seconds).



I have tried different ports, and same ports with the same end result.

I tried forcing PLCs and ports to 100/Full with the same result.I tried using an unmanaged switch/hub with the same result.



If during the PLC swap, I reboot the PanelView (reset switch on the back), communication is restored after the reboot is complete (under 7 minutes).



Best regards,
  Reply With Quote
Old July 3rd, 2008, 08:54 AM   #2
ghettofreeryder
Member
Canada

ghettofreeryder is offline
 
Join Date: Aug 2005
Location: Alberta
Posts: 237
I presume the IP addresses are statically assigned. I wonder if it has something to do with Spanning Tree, Do you know if your switches support STP?. If it is enabled, this could be why
  Reply With Quote
Old July 3rd, 2008, 09:11 AM   #3
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
Yes, all IPs are static.

This SRW2008 does have spanning tree, and it is disabled.



Thanks for your reply, hoping someone else has seen this. Release notes for the F/W upgrade to PVP700-1500_50002.exe on the PV does not cover this problem.

Distributor and AB are stumped.

Best regards,

Paul
  Reply With Quote
Old July 3rd, 2008, 02:40 PM   #4
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
Looks like an ARP table problem in the PV+..stay tuned.
  Reply With Quote
Old July 4th, 2008, 10:30 AM   #5
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
On the PC running ME Station.



I switch PLCs, comms are disrupted.



I open a command prompt, type arp -d, then ping, and communication is established in seconds.



Need to be able to trigger this on comm. Loss and also perform this on PVP 8-).
  Reply With Quote
Old July 4th, 2008, 02:09 PM   #6
Eddie Willers
Member
United States

Eddie Willers is offline
 
Eddie Willers's Avatar
 
Join Date: May 2002
Location: Grand Central Station
Posts: 615
Don't be surprised when the local A-B office doesn't have an answer for you; none of the components your predecessor assembled are intended to work in that fashion. Using the relays on the 1747-BSN to switch between Ethernet cables is... inventive. You should definitely monitor the Station Diagnostics for the Channel 1 port of the SLC to be sure you're not introducing noise and failed packets into the Ethernet channel with this very nonstandard wiring method.

I think that you're right on about the PV+ ARP table requiring a rebuild when you swap devices that have a different MACID and the same IP address. It's just the way that IP works.

You might consider using THREE small switches to do this; one per SLC and one for the PanelView Plus. Manually switch on the power for the switch attached to the Primary SLC controller, and investigate if there's a Windows CE registry entry to cause an ARP flush any time the Ethernet link changes state.
  Reply With Quote
Old July 4th, 2008, 03:17 PM   #7
Eddie Willers
Member
United States

Eddie Willers is offline
 
Eddie Willers's Avatar
 
Join Date: May 2002
Location: Grand Central Station
Posts: 615
I wonder if you can cause an ARP refresh by manually resetting the SLC-5/05 Ethernet port using a CIP Generic Message to itself ?

Just unplugging it and replugging it probably does not cause it to send out new ARP announcements.

It would be useful and interesting to install a network traffic sniffer in this system (does your switch support port mirroring ?) to see if there is traffic that triggers the ARP refresh inside the PV+, or if the occurence is entirely within the OS.
  Reply With Quote
Old July 7th, 2008, 07:58 AM   #8
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
Great idea Eddie, and it is working now. I am sending out a "dummy" message on the network from the PLC after a switch over. This is updating the ARP tables and restoring communication in seconds!!

Thanks group (especially Eddie) for the assistance!!
  Reply With Quote
Old August 27th, 2008, 02:26 AM   #9
champion
Member
China

champion is offline
 
Join Date: Aug 2008
Location: Earth
Posts: 2
Hi Celichi, I predict i may encounter your problem for coming project but my hmi is GE's QuickPanel.

Could you elaborate on the last point how to "triggers the ARP refresh"? Is it done on Windows side and network switch side? Thank you in advance.
  Reply With Quote
Old August 27th, 2008, 07:11 AM   #10
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
Hi CHampion,

The PLC triggers a dummy message (using the MSG instruction), which "alerts" the HMI of the new IP/MAC relationship.

It works perfectly!

I hope this helps.
  Reply With Quote
Old August 27th, 2008, 10:02 PM   #11
champion
Member
China

champion is offline
 
Join Date: Aug 2008
Location: Earth
Posts: 2
Yes it's simple but a perfect solution with very short switching time. Thank you for your sharing.
  Reply With Quote
Old August 28th, 2008, 06:59 AM   #12
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
No Problem...Thank Eddie, he planted the seed 8-).
  Reply With Quote
Old April 11th, 2016, 03:28 PM   #13
JasonPei
Member
Canada

JasonPei is offline
 
Join Date: Apr 2016
Location: Kitchener, ON
Posts: 3
Hi Celichi,

I am having the same issue with my SLC switch-over. Could you please give more info on the "dummy" MSG instruction? is the MSG type peer-to-peer? the target device is PLC5 read, right? Since the commissioning time is very short, any additional info would be greatly appreciated.
  Reply With Quote
Old April 12th, 2016, 08:22 AM   #14
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
Because I was using this card to switch Ethernet (the MAC address changes).

Just send any messages, doesn't matter what it is, just fire anything out, and this will update the ARP tables.

http://postimg.org/image/baoghkc4h/

Last edited by celichi; April 12th, 2016 at 08:28 AM.
  Reply With Quote
Old April 12th, 2016, 08:33 AM   #15
celichi
Member
Canada

celichi is offline
 
celichi's Avatar
 
Join Date: Apr 2008
Location: Dundas
Posts: 59
SLC Export

dummymsg.zip
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Panelview 1000 communication trouble Spartan10 LIVE PLC Questions And Answers 2 June 25th, 2008 07:09 AM
Profibus --> Ethernet --> LabView Help! pmurray LIVE PLC Questions And Answers 0 November 13th, 2007 04:53 PM
connecting SLC 5/04 to Panelview through rs232 Bcon1006 LIVE PLC Questions And Answers 3 March 4th, 2007 09:24 AM
SLC 500 to Panelview 1000e Jody alford LIVE PLC Questions And Answers 6 March 2nd, 2007 10:55 AM
SLC 5/05 Ethernet hardware fault (A2h) Znatok LIVE PLC Questions And Answers 2 October 11th, 2005 11:26 AM


All times are GMT -5. The time now is 03:02 AM.


.