Allen-Bradley 1352 VFD Start time delay

Chris335577

Member
Join Date
May 2006
Location
Buffalo,NY
Posts
12
I have a AC drive that has a time delay of 17 seconds before the Motors start to hum and the VFD delivers voltage.

Does the drive have a time delay paramater after sending it a start and reference signal.

The Drive is 20 years old.
 
Last edited:
What network are you using to communicate with the drive? A 17-second communications delay seems very long, but it's not out of the realm of possibility.

Are there other delays for other machines on this network?

Rick
 
It could be RS-232 network. Whatever the main network that was in use at the time. Also their are two drives and they both have to start at the same time. The 17 seconds is a total for both drives.
The PLC has to communicate with both drives.

Thanks,
Chris
 
Last edited:
The Drive uses a 20 milliamp current loop at 4800 baud with SAMI digital drive communication protocol. It communicates with the PLC by using a Allen-Bradley 3500-NA2 PLC Interface Module.

PLC2/30----------1772 SD2------------3500 NA2--------------1352C




I guess there is a lot of room for communication delay?
 
Last edited:
Is that a delay from Initial Power On until it can spin a motor? Or is it already powered up, and it takes that long after giving it a reference and a run command?

If the first, the bus capacitors may be going south (if the unit has them), if the second, perhaps it's just an accel setting problem.

Has this always happenned? Or did it just start to happen?
 
I know essentially nothing about communications of that period but, if the drives are configured with motor Premagnetization you could be seeing the effect of having the Premag period set too long. usually 1 or 2 seconds is more than enough.
 

Similar Topics

Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
2
Views
142
Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
Replies
5
Views
326
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
124
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
Replies
14
Views
241
I have a client who periodically experiences network communication issues. Sometimes when I VPN into the site, their SCADA systems will flash comm...
Replies
2
Views
158
Back
Top Bottom